im talking definitions see post 26
ok wayne,
exposed conductive part:
"a conductive part of equipment which can be touched and which is not a live part but which may become live under fault conditions"
(i know you know it Wayne, this is so everyone else can see straight off what we are discussing
)
looking at equipment (electrical equipment) are you saying it will come under 'accessory'
?
Is it an item for "distribution or utilisation of electrical energy"?
lets say i have a metal beam in the ceiling in the roof an factory. It is not connected to the structural steelwork so is not extraneous
If there is no cables near it, then it would not be an exposed conductive part
But if a lay a cable along it, would it then be an exposed conductive part????
And heres another thing
we are discussing BONDING the tray
but we also agree that it is not extraneous, so if it is an exposed conductive part, then connecting it to the MET would be via a CPC (ie earthing) by the regs defenition
if you were coneecting it an extraneous conductive part, (or another exposed conductive part) then that would be SUPPLEMENTARY bonding
You could not BOND it to the MET
so where is he connecting it to?
hmmmm, interesting one this
i have heard this argument before about back boxes as well