New sub board for shed swa advice. | Page 7 | on ElectriciansForums

Discuss New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 15, 2018
Messages
3
Reaction score
1
Location
Essex
Hi guys new to the forum after bit of advice. My family are installing a new shed in the garden and require a lot of power ie few sockets, lights. I am planning of running a swa fed from 32a mcb from the main board to a sub board.
Have a question-
Shall I install the new 32a mcb in the main board on the RCD side or main switch side?
Thanks
 
Ok, how about a supply to an outside socket or shed where you're coming from an existing socket on a RFC, plasterboard walls so you put in a single dry lining box for a DP switch or SFCU and drill through to outside behind the box, how do you earth the armour at that termination ? Yes I know you could terminate into a box outside but why create another unnecessary connection when you can earth the armour at the other end ? Or you could have an insulated CU to take your SWA from with no space around it for an additional connection box and no way of drilling a 20mm hole into it.
I don't understand your argument here to be honest. You have got to gland the SWA to something have you not?? So just earth it at that point. I often use a Wiska box on the outside wall, not forgetting the danger 230V label :)
 
Ok, how about a supply to an outside socket or shed where you're coming from an existing socket on a RFC, plasterboard walls so you put in a single dry lining box for a DP switch or SFCU and drill through to outside behind the box, how do you earth the armour at that termination ? Yes I know you could terminate into a box outside but why create another unnecessary connection when you can earth the armour at the other end ? Or you could have an insulated CU to take your SWA from with no space around it for an additional connection box and no way of drilling a 20mm hole into it.
I don't understand your argument here to be honest. You have got to gland the SWA to something have you not?? So just earth it at that point. I often use a Wiska box on the outside wall, not forgetting the danger 230V label :)
 
Going back to basics is needed here so that the requirements can be understood.
I can assure you that I am NOT wrong, (this is NOT just my opinion), if you listen to, read and understand the posts I have made then this can be understood.
Firstly it must be understood that HASAWA applies to all persons when at work, employed or self-employed if people can't understand that then they are beyond help.
Is this understood by all, or are many of you going to disagree and state that you are beyond the law of the land when you are at work, and thus the law does not apply to you because you are some sort of special being?
 
I think your problem is that you are confusing a ‘task of work’ with a ‘domestic installation’.
If no task of work is being conducted, neither the HASAWA or the EAWR applies.
If a task of work is being conducted the HASAWA and EAWR would apply to that task, not to the domestic installation.
It may be that the task of work is to make safe a dangerous condition in the domestic installation.
How would such a task be able to be conducted if the domestic installation must first comply with HASWA and the EAWR?
 
No you wouldn’t, you can’t have exposed metal connected to two different earthing systems like that. You insulate the armour at the load end of the submain so that it does not introduce another potential.

Also leaving a TT system with such a high Ra is unacceptable.

That's what I thought, so instead of the scenario I suggested you'd use a plastic enclosure for the swa instead of metal, and boot over the swa gland so no exposed metal is left? (lets leave the 1667 ohm TT topic for another day, sometimes it's impossible to achieve below 200 when your installation is on a cliff edge, or on a sandy beach for example ;-))
 
I think your problem is that you are confusing a ‘task of work’ with a ‘domestic installation’.
If no task of work is being conducted, neither the HASAWA or the EAWR applies.
If a task of work is being conducted the HASAWA and EAWR would apply to that task, not to the domestic installation.
It may be that the task of work is to make safe a dangerous condition in the domestic installation.
How would such a task be able to be conducted if the domestic installation must first comply with HASWA and the EAWR?
I am fully understanding the situation, and this is not just my opinion it is that of many others, and other organisations.
The task of work is being done when the domestic electrical installation is being designed, constructed, inspected and tested, or do you not charge for the domestic installations you do Spin?
Do the rest of you do all your domestic installations works as DIY, therefore no money changes hands and nobody gets paid for any domestic installations works?
I know that the domestic installation industry is a race to the bottom, but I don't believe that no one gets paid for domestic installations works.
How do all these domestic electricians and those working for builders doing new builds pay for their food and mortgages of they are not at work and being paid when they are doing the electrical works?

Thus the law does apply to people doing electrical installations works, whether employed or self employed when they are at work doing the work.
Therefore the Health and Safety At Work etc. Act 1974 applies to these people when they are at work, if it doesn't why to all these house building companies make such a bloody massive thing about Health and Safety on their construction sites.

So is every house building company in the country wrong then Spin? Because that is what you are saying. You are saying that HASAWA & EAWR do not apply to domestic works.
 
RCD in house, so you are protecting the cable and can see if your freezer has tripped out.
RCD in shed for circuits also. Nuisance tripping means they are working! If the shed or house RCD go then good that’s what they are meant to do! Find the fault!
Do not export the TNCS earth! Your equipotential zone stops 1.5m away from the footprint of the building containing the supply!
TT the shed like you would with any external buildings and portacabins etc
 
... The task of work is being done when the domestic electrical installation is being designed, constructed, inspected and tested ... Thus the law does apply to people doing electrical installations works, whether employed or self employed when they are at work doing the work...
Hi - this has got a little complicated for my brain, but it seems @spinlondon (#96) post and yours agree ... That's me running for cover :) .
 

Reply to New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top