Guest viewing limit reached
Hi guys new to the forum after bit of advice. My family are installing a new shed in the garden and require a lot of power ie few sockets, lights. I am planning of running a swa fed from 32a mcb from the main board to a sub board.
Have a question-
Shall I install the new 32a mcb in the main board on the RCD side or main switch side?
Not sure that the difference between a MET and an EMT has any significance?
Regulation 8 of the EAWR is not particularly complicated, though it is a bit contradictory.
Tells us to earth all conductors not intended to be live, which obviously contradicts Regulation 9.
yes consult the DNO. It is their Earth not yours. It’s their TX not yours. It is their engineers that calculate where and when a neutral can be used as CNE.
No if you ask them for permission and they say ‘yes’ then you can. Obviously.
With TT systems, the consumer must provide his or her own connection to Earth, i.e. by installing a suitable earth electrode local to the installation. The circumstances in which a distributor will not provide a means of earthing for the consumer are usually where the distributor cannot guarantee the earth connection back to the source, (IET)
IET. Guidance Note 5: Protection Against Electric Shock, 7th Edition.
That means you are guaranteeing it! But it’s not yours! ESQCR 24 you will be in jail.
installations supplied from TN-C-S (PME) systems, in view of the risk of danger in the event of an open circuit neutral fault on the distributor's low voltage network. ESQCR Regulation 25(2) prevents a distributor from providing a PME supply to premises (IET)
ESQCR 25 (2). Taking a DNO supply and provided earthing arrangement out of their specified equipotential zone. Jail.
You do understand that out of all the documents electricians ‘use’ BS7671 is the last one! And it starts with EAWR 89 and ends with ESQCR....with HASAWA and CDM regulations in between...
I’ll let you in on a little known secret....
While the publisher and contributors believe that the information and guidance given in this work is correct, all parties must rely upon their own skill and judgement when making use of it. The publisher and contributors do not assume any liability to anyone for any loss or damage caused by any error or omission in the work, whether such error or omission is the result of negligence or any other cause. Any and all such liability is disclaimed. (IET)
IET. BS 7671:2018 Requirements for Electrical Installations, IET Wiring Regulations, 18th Edition.
It is a requirement of ESQCR (Reg 24 I believe) for the DNO to provide consumers a connection point to either the network neutral or protective conductor, for connection of the installation earth.
Regulation 25 allows the DNO to refuse this connection only if the installation fails to comply with BS7671, or could pose a danger or cause an interruption of supply.
Essex
New sub board for shed swa advice.
Jcamerz,
Pete999,