New sub board for shed swa advice. | Page 9 | on ElectriciansForums

Discuss New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 15, 2018
Messages
3
Reaction score
1
Location
Essex
Hi guys new to the forum after bit of advice. My family are installing a new shed in the garden and require a lot of power ie few sockets, lights. I am planning of running a swa fed from 32a mcb from the main board to a sub board.
Have a question-
Shall I install the new 32a mcb in the main board on the RCD side or main switch side?
Thanks
 
Not sure that the difference between a MET and an EMT has any significance?
Regulation 8 of the EAWR is not particularly complicated, though it is a bit contradictory.
Tells us to earth all conductors not intended to be live, which obviously contradicts Regulation 9.
 
yes consult the DNO. It is their Earth not yours. It’s their TX not yours. It is their engineers that calculate where and when a neutral can be used as CNE.

No if you ask them for permission and they say ‘yes’ then you can. Obviously.


With TT systems, the consumer must provide his or her own connection to Earth, i.e. by installing a suitable earth electrode local to the installation. The circumstances in which a distributor will not provide a means of earthing for the consumer are usually where the distributor cannot guarantee the earth connection back to the source, (IET)

IET. Guidance Note 5: Protection Against Electric Shock, 7th Edition.

That means you are guaranteeing it! But it’s not yours! ESQCR 24 you will be in jail.

installations supplied from TN-C-S (PME) systems, in view of the risk of danger in the event of an open circuit neutral fault on the distributor's low voltage network. ESQCR Regulation 25(2) prevents a distributor from providing a PME supply to premises (IET)
IET. Guidance Note 5: Protection Against Electric Shock, 7th Edition.

ESQCR 25 (2). Taking a DNO supply and provided earthing arrangement out of their specified equipotential zone. Jail.

You do understand that out of all the documents electricians ‘use’ BS7671 is the last one! And it starts with EAWR 89 and ends with ESQCR....with HASAWA and CDM regulations in between...
 
I’ll let you in on a little known secret....

While the publisher and contributors believe that the information and guidance given in this work is correct, all parties must rely upon their own skill and judgement when making use of it. The publisher and contributors do not assume any liability to anyone for any loss or damage caused by any error or omission in the work, whether such error or omission is the result of negligence or any other cause. Any and all such liability is disclaimed. (IET)

IET. BS 7671:2018 Requirements for Electrical Installations, IET Wiring Regulations, 18th Edition.
 
Are you EVER going to quote a BS 7671 reg that states clearly that SWA must be earthed at the supply end ?
Are you going to ignore ‘manufacturers instructions’? And are you going to let us all know what ‘SWA glands’ are produced for if not to go on SWA cable?
SWA is an extraneous conductive part......go back to college.
134.1.1
 
It is a requirement of ESQCR (Reg 24 I believe) for the DNO to provide consumers a connection point to either the network neutral or protective conductor, for connection of the installation earth.
Regulation 25 allows the DNO to refuse this connection only if the installation fails to comply with BS7671, or could pose a danger or cause an interruption of supply.
 

Reply to New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
723

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top