I've been asked to quote for wiring a granny annex and i'm in two minds whether it needs a second supply or not, i know the on site guide is only a guide and you have to do whats practical but because there's a real possibility of cookers, kettles dishwashers etc.. being used at the same time i'm thinking it would be better on a separate supply, wiring as follows

x2 - 32A cookers
x3 - 32 rings
45A garage/shower (used daily)
15A immersion
6A lights
6A lights

I get about 153A after diversity

what would you do?
 
Out of interest what is the heating system? If you could swap that shower to a mixer it would help improve the loading situation.

I'd weigh up the cost of an extra supply to that of changing the plumbing.

I still reckon the single supply will more than cope with that demand anyway. How did you calculate the shower and cooker? Seems high
 
heating's on a combi , one cooker is 4.5kw the other 10.5kw. first 10A plus %30 of rest. i calculated shower as 100% with a few sockets/lights in garage, i have suggested changing shower, how did you get 60A?
 
NO property would EVER draw 163 a...

The diversity calcs in the OSG are so old hat and take absolutely no account of the reality these days....

Even multiplying by 0.25 will give you 58A but that is too high.... IMHO
 
6 bed holiday cottage, 3 electric showers, cooker etc. First I was suprised when the seals fell off, second I was suprised when the fuse fell out, third I was really suprised to find that it had all been running quite happily for over 10 years on a 60A fuse. I worry a lot less about maximum demand these days and would agree with all the others
 
There is a 12 bedroom guesthouse local to me with an electric shower in each room. The property is fed with a standard single phase supply and the client assured us he had never had an issue! Was tempted to pull the fuse carrier and see if there was actually a fuse in there!
 
There is a 12 bedroom guesthouse local to me with an electric shower in each room. The property is fed with a standard single phase supply and the client assured us he had never had an issue! Was tempted to pull the fuse carrier and see if there was actually a fuse in there!

They serve breakfast by room numbers at ten minute intervals so only a couple of showers at most can ever be on simultaneously. :D
 
They serve breakfast by room numbers at ten minute intervals so only a couple of showers at most can ever be on simultaneously. :D

Possibly! They take a lot of these minibus tours so most, if not all rooms being filled at the same time of evening. Can only be luck that they've managed so far.
 
I've been asked to quote for wiring a granny annex and i'm in two minds whether it needs a second supply or not, i know the on site guide is only a guide and you have to do whats practical but because there's a real possibility of cookers, kettles dishwashers etc.. being used at the same time i'm thinking it would be better on a separate supply, wiring as follows

x2 - 32A cookers
x3 - 32 rings
45A garage/shower (used daily)
15A immersion
6A lights
6A lights

I get about 153A after diversity

what would you do?

As mentioned if new shower was mixer type then you can cross off the shower and immersion, then you're sorted.
 

Reply to new supply needed for granny annex? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
1K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top