new supply needed for granny annex? | on ElectriciansForums
Discuss new supply needed for granny annex? in the UK Electrical Forum area at ElectriciansForums.net
S
sparks1664
I've been asked to quote for wiring a granny annex and i'm in two minds whether it needs a second supply or not, i know the on site guide is only a guide and you have to do whats practical but because there's a real possibility of cookers, kettles dishwashers etc.. being used at the same time i'm thinking it would be better on a separate supply, wiring as follows
x2 - 32A cookers
x3 - 32 rings
45A garage/shower (used daily)
15A immersion
6A lights
6A lights
I get about 153A after diversity
what would you do?
Out of interest what is the heating system? If you could swap that shower to a mixer it would help improve the loading situation.
I'd weigh up the cost of an extra supply to that of changing the plumbing.
I still reckon the single supply will more than cope with that demand anyway. How did you calculate the shower and cooker? Seems high
heating's on a combi , one cooker is 4.5kw the other 10.5kw. first 10A plus %30 of rest. i calculated shower as 100% with a few sockets/lights in garage, i have suggested changing shower, how did you get 60A?
NO property would EVER draw 163 a...
The diversity calcs in the OSG are so old hat and take absolutely no account of the reality these days....
Even multiplying by 0.25 will give you 58A but that is too high.... IMHO
6 bed holiday cottage, 3 electric showers, cooker etc. First I was suprised when the seals fell off, second I was suprised when the fuse fell out, third I was really suprised to find that it had all been running quite happily for over 10 years on a 60A fuse. I worry a lot less about maximum demand these days and would agree with all the others
There is a 12 bedroom guesthouse local to me with an electric shower in each room. The property is fed with a standard single phase supply and the client assured us he had never had an issue! Was tempted to pull the fuse carrier and see if there was actually a fuse in there!
They serve breakfast by room numbers at ten minute intervals so only a couple of showers at most can ever be on simultaneously. :D
Possibly! They take a lot of these minibus tours so most, if not all rooms being filled at the same time of evening. Can only be luck that they've managed so far.
x2 - 32A cookers
x3 - 32 rings
15A immersion
6A lights
6A lights
what would you do?
As mentioned if new shower was mixer type then you can cross off the shower and immersion, then you're sorted.
Reply to new supply needed for granny annex? in the UK Electrical Forum area at ElectriciansForums.net
Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...