Hello everybody

Ive got my niceic inspection soon. On my recent fuse board change and test i completed Zs tests for each circuit but only calculated R1 + R2 (apart from the ring mains) IS THIS OK? Also if anyone has had the niceic guy come out, any words of warning?

Thanks
 
At every point on every circuit? are you sure it's not just the furthest point on every circuit?

If its a board change only
No requirement for Zs throughout the circuits,a reading at the extremity of the circuits is ok
I would also do a loop test at all the sockets if possible as well as continuity of the ring
 
i usually calculate R1+R2 on existing circuits too (except on ring circuits) and only measure it if its a new circuit. I also am looking into NICEIC enrolement soon and would like to know the assessors views on this so plz post the outcome,
cheers,
wayne
 
i usually calculate R1+R2 on existing circuits too (except on ring circuits) and only measure it if its a new circuit. I also am looking into NICEIC enrolement soon and would like to know the assessors views on this so plz post the outcome,
cheers,
wayne

If he's any good, he'll ask you what possible use a 'calculated' R1 + R2 measurement was to anyone.
 
Must admit chaps, there is no reason not to measure R1+R2 on a CU change.

This would then go towards ensuring the cpc is continuous throughout the circuit, which a Zs measurement would not.
 
Must admit chaps, there is no reason not to measure R1+R2 on a CU change.

This would then go towards ensuring the cpc is continuous throughout the circuit, which a Zs measurement would not.

I agree, Jason - measure it. Your cables are already disconnected etc etc. so why not.

A calculated R1 + R2 is as much use as a chocolate teapot - what does it tell you? Nothing.:)
 
good post Lenny, but would be ok IMO to measure R1+R2 , and calculate Zs?
 
Last edited:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
NIEIC inspection
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
40
Unsolved
--

Advert

Thread statistics

Created
tom-the-sparky,
Last reply from
Guest123,
Replies
40
Views
5,932

Advert

Back
Top