Doing a PIR lately and found no continuity on one of the ring final neutral circuits. I am not familiar with fault finding and would appreciate any help and hints. IR test on the circuit passed.
 
There would seem to be a break in the neutral somewhere, hopfully at a socket and not a in-accessible junction box.

Split the ring at it's geographical centre, or as near as you can. Do an R1 +RN test on both sides of the ring, with luck you will get one side showing an open circuit and just keep spliting that side of the ring until until you find it.
 
As malcome has said there is also another possability if its concrete floors the cables normally drop check to see if there and any pictures above sockets ,see this a few times if there is do a long lead test between the neutral and the nail i know it sounds daft but you,d be suprised how many live nails stick out of walls , yes i know it the neutral same scinario
 
Or new skirting? - had one yesterday. Old cables (not in zones to be fair to the Chippy) so nail rignt through neutral - good shot!

surprised the chippy didn't nail directly below socket otlet. he'd have missed it then ! :death:
 
Doing a PIR lately and found no continuity on one of the ring final neutral circuits. I am not familiar with fault finding and would appreciate any help and hints. IR test on the circuit passed.

Some good help given already. When fault finding start with the basics, keep it simple and methodical. It is all too easy to get in too deep when you don't need to.

Your IR test will give a good result because the circuit is broken, so you are only testing up to the point of the break, and it wont help you in anyway to find the open circuit problem.

As you say that you have little experience fault finding, then getting and reading Guidance note 3 is a must, even more so if you are doing PIR's. This book shows you how to test properly all the circuits you will come across. Once you have grasped a good understanding of testing, fault finding will fall into place for you, because the test procedures are designed to show up faults, but it is too much to write in a forum post.

Cheers..........Howard
 
Instead of going round takeing all the socket facias off he needs to do a proper fault finding tests.

THE HALF TEST METHOD!


Afterall it might not just be a loose connection inside a socket!
 
Doing a PIR lately and found no continuity on one of the ring final neutral circuits. I am not familiar with fault finding and would appreciate any help and hints. IR test on the circuit passed.

Some good advice as usual here but it really worries me that someone without the competence to find a broken ring conductor is carrying out a Periodic Inspection, it doesn't get much more basic than this!
 
I had removed all the covers on the circuit to check all connections and found them to be secure. I had then also tried to follow the ring; slightly awkward as 2 of the sockets are in the upstairs bedroom and the rest below in the kitchen/diner. It appeared to be down to a couple of points but is proving difficult to pin down. The cables are buried in the walls and won't pull through and the upstairs floor is sheet board. I was wondering if there was a non-invasive way of locating or is it a case of rip everything up and take the newly tiled kitchen apart.?
 
remove tails from board (for that circuit that is not the main tails lol ) do a r2rn test link out the neutral and earth lever wagos are brill for this thne use you meter and do a continuity test at each socket across the cpc and neutral , if you have a tester that has a plug lead for Zs testing install the neutral to the live terminal on you meter and then the earth lead to the earth terminal then test at each socket till you locate the fault it could well be below the floor in a junction box doing this method saves taking all the fronts off again
 
if you find that it's not viable to locate the fault due to it being inaccessible without major damage, you could split the ring into 2 radials and replace the 32A MCB with 2 16A MCBs, 1 for each radial.
 

Reply to no continuity on ring final neutrals in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
525
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
758
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Not sure what you mean by pre-IP? as IP guidance was introduced long before 12v halogen downlights became 'fashionable'. That aside I would ditch...
Replies
2
Views
240
My guess would be damp and corrosion somewhere is the cause. But same result as what James has said.
Replies
3
Views
279

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top