No earth electrode visible? | on ElectriciansForums
Discuss No earth electrode visible? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Cork
Hi all,
Carrying out a periodic inspection at a domestic installation. Semi- detached house on a row of houses. I cannot for the life of me locate any sign of the earth electrode inspection chamber. Just wondering how you would number this? A 1,2,3 or a 4?
You need to establish the property has a reliable and safe means of earthing. Can you visually trace the earth? What size is the main earth at CU?
Is Irish EICR coding different to mainland uk?
Hi Richy.
Thanks for the reply. I can't trace that cable as it disappears down behind the wall the DB is mounted on.
The main earth coming from suppliers cut out is 10sq.
Yes the coding is different, as we number it 1-4 in terms of the risk involved
Hi Richy.
you say there is a main earth from the supply cut-out. does that mean it's been upgraded to PME? what's the Ze?
have you tested this unknown earth cable? (earth loop)
Hi James,
No I haven't tested the cable. I'm going to have to return there on Monday. Incidentally, I checked the front of the houses next door and all along that row of houses and there's no sign of an earth rod. Couldn't see any in front or rear of the house I was inspecting either. Very odd
Assuming the installation is neutralised, I would give a 2 to an Earth electrode which could not be located as it is impossible to verify that it is correct (or even present). A simple test doesn't prove this.
Thanks Risteard. I had put it down as a 2, even though I wasn't sure if I was right in doing so. Good to hear you'd have done the same. Thanks for the reply
Reply to No earth electrode visible? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
I don't think it will work with only one stake unless some meters have different operating parameters. It doesn't necessarily have to be a stake...
