No earth on his DNO TN-S supply, No earthing from an earth rod, No earthing from either the Water and Gas bonding connections to service pipes, ... And the OP can't even say this situation was present before he started any work.
Something is very wrong here. Have to wonder if the OP even checked bonding was in place, before starting this CU change!!

I have yet to see a broken down TN-S earthing supply with 0 ohms, that is almost an impossible scenario. Add to that, the bonding of service pipes (if not both plastic) not having any potential either, the chances then become astronomical of a L-E test being 0!! lol!!

If and it's a very big IF, the incoming TN-S had a really high or an impossible Ze value 0. then the very first thing you would do is call in the DNO as an emergency situation, not go ahead and do a CU change, ...find you have a problem, then start fluffing around installing an earth rod!!

I'll take some of that Oxygen now if there's any left!! lol!!
 
Hello all. Went to a property to give an certificate, it was an old ccu so. I recommended to install a new 17th edition board. All installed but when it came to testing tried to take a zs on sockets using my fluke tester it was coming out to be error 5, which means 1 of the conductors is not connected. So done a ze on the main income still got error 5. The supply is a TN-S and is soldered on. The earth looks good well soldered on. So decided to convert it to a TT by putting an earth electrode. which we did today but however doing the ze on the main still showing error 4/5. thought it might be my test instrument but tested on different property and reading coming fine. i have been told it could be an neutral fault at the main incomon or with in the house. But however everything seems to be working fine. Unless its using the earth as a neutral but if that was the case the extraneous conductive parts would have become live. its a tricky and hard one anyone got any ideas thank you in advance

Dont quite get this....if you went to give a certificate..(EICR?)....how come the first thing you decided to do was replace the CU before even carrying out any tests?
 
Strikes me, after re-reading some of this thread, that an EICR was truned into a DB change without ANY tests being done and this has bitten the OP in the xrse.
 
I'm hoping he's at least been and proved/made the installation safe, the L-E test giving 0 volts was somewhat worrying and possibly dangerous for the occupants.

In the interests of safety I'd rather it were that the OP could return here without fear of abrasive comments if he's got any questions or uncertainty.
 
I'm hoping he's at least been and proved/made the installation safe, the L-E test giving 0 volts was somewhat worrying and possibly dangerous for the occupants.

In the interests of safety I'd rather it were that the OP could return here without fear of abrasive comments if he's got any questions or uncertainty.
I agree with you to a point mate but this guy is out of his depth and needs to realise it.
 
The electrical supply company came out and tested it but said seems to be a fault down earth thats all they said and said we are running late on job so without further test converted it to a PME system and took reading came as 0.09ohms. Another happy client thank you for all your replies
 
Was the DNO operative dressed as spiderman and as he left,did he say "everybody gets one!" :devil:
 
The electrical supply company came out and tested it but said seems to be a fault down earth thats all they said and said we are running late on job so without further test converted it to a PME system and took reading came as 0.09ohms. Another happy client thank you for all your replies

I bet they didn't get a Zero reading when testing the Ze off the cable sheath before they converted though!!! ....lol!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
No earth reading!
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
59

Thread Tags

Advert

Thread statistics

Created
Khan,
Last reply from
Engineer54,
Replies
59
Views
7,498

Advert

Back
Top