Hi, as I've said I'm not an electrician but studying C&G in my own time and have worked as a mate.
I've just had a qualified sparky upgrade my CU to a split board 10 way dual RCD. He has run a 4mm2 cable (from a 40A MCB protected by one of the RCDs) to my hut and will be coming back to wire up a sub main for a radial with a couple of double sockets and a light circuit. He says he is fitting a sub board whose main switch will have no RCD (since the circuit is already protected by the RCD form the main board?) I don't understand that. Can someone help? BTW, I couldn't find the DIY section to post this.
 
Thanks for taking the time to reply. After studying a bit more I can see what you mean. We have Ib = 18A, In = 40A and Iz = 37A. We need to have Ib<=In<=Iz so these numbers fail. Should have used 32A MCB - am I correct?

The cable should have been sized correctly for the selected OCPD.
A soloution now could be to use a 32A OCPD, but I wouldn't use an MCB if it can be helped.
 
Wow, I am surprised, not many of us out there that know how to gland off micc cable now days. Seems a surprising choice of cable for a domestic setting.
 
The cable should have been sized correctly for the selected OCPD.
A soloution now could be to use a 32A OCPD, but I wouldn't use an MCB if it can be helped.
Thanks again. As I've said, I'm not qualified so what alternative to an MCB would there be bearing in mind a 10 way dual RCD Hager board has just been fitted by my electrician
 
Thanks again. As I've said, I'm not qualified so what alternative to an MCB would there be bearing in mind a 10 way dual RCD Hager board has just been fitted by my electrician

A switchfuse seperate from the main CU then an RCD CU in the outbuilding would be a better choice from the point of view of selectivity and minimising disruption in the event of a fault.
 
Are you sure? That is a very odd cable to use for a domestic installation these days considering it costs around ÂŁ10/m
I'm not sure whether its MICC but I attach an image of what they've run to my hut. None of the cable is exposed to the elements.
[ElectriciansForums.net] No RCD in sub main
 
I'm not sure whether its MICC but I attach an image of what they've run to my hut. None of the cable is exposed to the elements.
View attachment 53750
Not MICC then, was this cable circular before you split it to show it's construction? or was it flat?
 

Reply to No RCD in sub main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
783
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top