Hi, as I've said I'm not an electrician but studying C&G in my own time and have worked as a mate.
I've just had a qualified sparky upgrade my CU to a split board 10 way dual RCD. He has run a 4mm2 cable (from a 40A MCB protected by one of the RCDs) to my hut and will be coming back to wire up a sub main for a radial with a couple of double sockets and a light circuit. He says he is fitting a sub board whose main switch will have no RCD (since the circuit is already protected by the RCD form the main board?) I don't understand that. Can someone help? BTW, I couldn't find the DIY section to post this.
 
If any circuit has an rcd at its origin, it doesn’t need another one.
2 rcd’s in-line like that can cause a lot of head scratching if there’s a fault....

4mm to a hut? What’s in there? Sounds like a lot of power for a potting shed
 
If you're studying then performing a cable calculation for the hut feed could be a useful and enlightening experience.
A said, the RCD affords it's protection for all circuits downstream of it, it will detect imbalances in the hut distribution circuit and all the associated final circuits so another RCD in the hut is not necessary.
 
If any circuit has an rcd at its origin, it doesn’t need another one.
2 rcd’s in-line like that can cause a lot of head scratching if there’s a fault....

4mm to a hut? What’s in there? Sounds like a lot of power for a potting shed
Thanks for the prompt reply. Potting shed......I have great plans :)
[automerge]1573169528[/automerge]
Wow, that was quick and thanks for the prompt responses. I agree that the 4mm cable (rated at 37A) is overkill. By my calculations on a load of say 4KW gives approx 18A and since there is little need to allow for derating factors (wooden framed man cave) then 2.5 mm (rated at 27A) would be enough, but if this is wrong please let me know.
 
Last edited:
Thanks for the prompt reply. Potting shed......I have great plans :)
[automerge]1573169528[/automerge]
Wow, that was quick and thanks for the prompt responses. I agree that the 4mm cable (rated at 37A) is overkill. By my calculations on a load of say 4KW gives approx 18A and since there is little need to allow for derating factors (wooden framed man cave) then 2.5 mm (rated at 27A) would be enough, but if this is wrong please let me know.

The problem is that if the cables maximum rating is 37A then the largest standard size ocpd it could be connected to is 32A, it is not suitable for a 40A ocpd unless overload protection can be omitted, which it can't for a submain.

I think you have some terminology confused in your OP, 'submain' is the common term for a distribution circuit. So a submain generally refers to the cable and associated ocpd which forms the circuit feeding a distribution board.
 
The problem is that if the cables maximum rating is 37A then the largest standard size ocpd it could be connected to is 32A, it is not suitable for a 40A ocpd unless overload protection can be omitted, which it can't for a submain.

I think you have some terminology confused in your OP, 'submain' is the common term for a distribution circuit. So a submain generally refers to the cable and associated ocpd which forms the circuit feeding a distribution board.
Thanks for taking the time to reply. After studying a bit more I can see what you mean. We have Ib = 18A, In = 40A and Iz = 37A. We need to have Ib<=In<=Iz so these numbers fail. Should have used 32A MCB - am I correct?
 

Reply to No RCD in sub main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
808
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top