Apologies for the length of this post but I'd like to provide as much information as possible

We moved house last October knowing that the property would require a full rewire. Our electrician completed the rewire (including new consumer unit) in December last year and although we were unhappy about his reliability at points during the process, we were pleased that the job had been completed and that he had issued a certificate detailing the work done. The rewire didn't include any work in the bathroom or kitchen as our intention was to completely refurbish these rooms at a later date.

That time has now come and we decided against using the previous electrician due to the reliability issues mentioned above A local electrician came to the house last night to discuss our requirements. He had a few questions about the exisiting electrical set up so I dug out the 3 page certificate that the previous electrician had issued. Upon viewing the certificate the electrician commented that the certificate didn't show which body the issuing electrician belonged to. He said that without the registration body information and registration number the certificate would not be acceptable to building control. He also said that the previous work should have been notified to building control either prior to work commencing by an unregistered person or afterwards by the registered 'competent person'.

This set off alarm bells. I've spent this morning online trying to find him listed with one of the registered bodies but he doesn't appear on any of the sites I've been to. I've looked at NICEIC, ELECSA, NAPIT,BSI, Kitemark and Benchmark Certification Ltd (CORGI Membership). Are there any others he could be registered with that would allow him to certify his work?

We had used this electrician on a smaller job (wiring an ensuite shower room) at our old home 3 or 4 years ago and had been really pleased with his work. He had issued a certificate for this work too and also came heavily recommended on a local community website, so we had no reason to think he shouldn't be certifying his own work. Although no rewiring took place in the bathroom, kitchen and garden areas I'm assuming that this is notifiable work because he installed a new consumer unit?

I'm not sure what to do next. I haven't spoken with the electrician yet because I want to get my facts straight first. I'm worried about contacting the council because I've read that they can fine the householder upto £5000 if work that should have been notified in advance hasn't been. I also need to understand what we might be forced to do if the certificate is invalid. Are we likely to have to lift all our floorboards again and reexpose all the cables within the walls ?

This is so frustrating because we would never have had the electrician undertake the job if there'd been any suggestion that he could not certify his own work.

Apart from berating us for being so foolish as to take him at his word without checking him out further at the time, can anyone offer any constructive advice on how we should deal with this situation. Although we've lived at our current address less than a year we want to ensure that we don't have any problems when we come to sell in the future.

Many thanks for taking the time to read this and for any useful advice you may be able to provide.
 
Eiluj68. There are certain certificates that anyone can buy over the counter, or download for free. Anyone can get them. Can you scan them, with name address etc blanked out, and Im sure me and the guys will suss out whats what
 
Well I could always post a warning on the local forum where he is currently highly recommended. He gets a lot of business via that route. :biggrin5:

I'd have to be careful though. Probably wouldn't be allowed to name names but I could warn everyone to check registration details of any electricians they use.

One more question - does the fact that the he issued a certificate prove that he was trying to pass himself off as a 'competent person' or is it common for these certificates to be issued regardless. I'm just trying to pre-empt his response when I contact him. I'm just wondering if he might claim that the certificate is purely a list of all the individual jobs/tests that he's done, rather than an attempt to officially "certify" his work.

The fact he issued a certificate, at the very least is some form of acknowledgement that certificates are required.

I guess it would come down to what his written, emailed estimate said - did he refer to LABC (local area building control) notification in any way? When I provide estimates for notifiable work, this is confirmed on my estimate.
 
Last edited by a moderator:
Eiluj68. There are certain certificates that anyone can buy over the counter, or download for free. Anyone can get them. Can you scan them, with name address etc blanked out, and Im sure me and the guys will suss out whats what

Thanks. I'll scan them in when I get home.

You guys are great :smiley2: Thanks so much for all your replies so far.
 
Before going off on one, maybe you should ask him if he is Registered for Self-certification.
I know the paperwork and test results I give out do not show any membership number etc., and as a Sole Trader, it can be easy to confuse the Trading name, and my own name, so a search may not bring up the details of my business.
To be honest, if you are happy with the work he did, then there is little reason to take things further, as it appears he knew what he was doing by thorough testing, and he did issue test results and Install Cert., so if these tally up, then there is no safety problem if he has followed the current regulations.

This ncould all be down to a lost in the post certificate from the Governing body, or he may have forgotten to register it with the body. i know I have come close to not notifying as I have forgotten about some jobs. A rewire I did was spread over 6 weeks, and that was nearly not notified, I only remebered as I had to go back and fit a new light.

Chill a little!
Alan.
 
Hi,

I'm at work at the moment so don't have the certificate to hand. It had 3 pages and was green and white as I recall. Each room was listed and there were boxes for testing results which had all been completed.
Sounds like an EIC, whch he should have issued anyway, registered or not.

Issuing one, detailing the testing etc that he did, is not only not an attempt to pass himself off as registered, it is required by the Wiring Regulations.

Unless it's a complete fabrication, the fact that he did one is encouraging - try vernam's first suggestion. (But not his 3rd - it's not worth risking a prosecution for fraud, no matter how small the risk.)
 
How are they going to prove that you had that rewire carried out? you cant specifically tell when cable/accs where installed

There will only ever be a problem if something go's wrong, get a registered electrician out to carry out a full inspection
 
Not sure if this has already been mentioned (as I only flicked through posts, so sorry if it has), but if you mention it to the LABC they may just ask you to fill in a regularisation application. Normally costs price of building notice (between £200-£300) + 10%. I had an issue with this for my NIC assessment when I completed the job but hadnt notified building control (dont ask). In the end they had a winge and then done it as a building notice. Cost me £210, bloke came out tested and inspected, wrote certificate out, job done. I wouldnt worry too much. As already mentioned its down to him and not you. I would phone him and verify all this first as it maybe he has already notified them. Certificates from building control took 2 1/2 weeks to come through on my jobs.

Happy hunting,

Rob
 
Where does it say you can't use generic forms which you've bought from the wholesaler or even downloaded from the IET website? Provided the work has been done to an acceptable standard, all the inspection and testing done and the appropriate certificates filled in correctly I don't see the problem; as already mentioned anyone can join a scheme after a couple of weeks - having a fancy pad of forms with logos on them and sending them to the right people doesn't make someone a good or (in my eyes) even competent electrician.
For all we know this guy could have been doing sterling work for 20 years, have more qualifications than you can shake a stick at, and just disagree with having to pay through the nose for some scheme provider - if he was a scammer or a cowboy or both I doubt he would have issued any paperwork at all.

As mentioned if there are no apparent problems I see no cause for concern, although I'll happily cast my eye over the certs which have been issued.
 
Thanks for your patience guys. I've scanned the certificate as you can see below, having removed all names and addresses first.

Pg1.jpgPg2.jpgPg3.jpg

It all looks kosher to a non-electrically trained person as myself. I wouldn't have thought to question this if the electrician I saw yesterday hadn't queried the certificate when he saw it. I've had another electrician round to quote tonight and he didn't think we should be too worried, although we definitely didn't get a certificate from building control. He also said that registration with all the various bodies such as NICEIC etc is voluntary and that you can still issue certificates provided you're fully qualified and deemed competent (how do you do that?). This electrician is registered with ELECSA.
 
It all looks kosher to a non-electrically trained person as myself. I wouldn't have thought to question this if the electrician I saw yesterday hadn't queried the certificate when he saw it. I've had another electrician round to quote tonight and he didn't think we should be too worried, although we definitely didn't get a certificate from building control. He also said that registration with all the various bodies such as NICEIC etc is voluntary and that you can still issue certificates provided you're fully qualified and deemed competent (how do you do that?). This electrician is registered with ELECSA.

He's right in saying registration with a governing body is optional, but if you still have to notify building control for major works in this case rewire and consumer unit replacement. If the electrician is not part of a scheme, you have to notify building control what work will be carried out before work starts.
 
Last edited:
Installation is new? (more like alteration if he isnt rewiring all the circuits)
TNs Ze 0.85 ohms?
80amp T2 1361 = 11ka?
Max demand 120 ?
(Main switch circuit breaker) 80947-3?
16mm tails ok so long as service fuse is indeed no higher than 80amp (would normaly be upgraded to 25mm on a board change.
No selv or double insulation anywhere in the property?
No barriers or enclosures?

R1+R2 on the lighting circuits, I would have thought they would be higher readings.
No meter serial number

Gave up
But as he has changed the cu & I assume connected all the properties circuits to the new cu, then he has to test & cert all the circuits including the kitchen & boiler.
 

Reply to Not sure what our options are. Advice required for homeowner please. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
166
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Article
This is an RSS feed of thread: ADVICE for young plumber required please staffs/midlands Content of the thread: hi all, posting on behalf of my...
Replies
0
Views
318
The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top