hi .customer complained that her off peak water wasn't heating.its a ex b7 controler .boost worked fine on 24 supply.there is just 1 cable going to tank [1 elememnt] but off peak trips old wylex 15a push button mcb
sorry dont no the bs number.changed the b7 controller because it was 25 years old anyway.the off peak came on to give her a full tank of hot water and then next day trips.never tested element or cable because the boost works fine on a mem 16 a mcb.i am going to put in a 2 way consumer unit tomorrow for off peak.
surely it has to be that pop mcb that is faulty.has anyone else came across similar scenarios .thanks
 
Is a dual element immersion heater?

Why do you want to fit a new CU when you could just replace the mcb which you seem to think is faulty?

And why did you replace the controller just because it was old?
 
its a single element.timer plugs were brittle inside and discoulered around double pole switch for timer.the wylex mcb will hold for an hour or so and then pop.its a rented flat so land lord agreed to change timer.can you still get that type of mcb apart from ebay.trouble is tennent is complaining on cost of using boost
 
The replacement for that mcb is a current item yes, I'd expect any wholesaler to have them on the shelf.
You may have to change the base too but that comes with the mcb so shouldn't be a problem.

Even screwfix sell them! http://m.NoLinkingToThis/p/wylex-16a-sp-type-b-curve-mcb/34544

Why didn't you test the element?
 
didnt test element because the 16amp type b 60898 works fine on the boost.its the same element for both mcb

How do you know that mcb is working correctly?

I can't see the logic in not doing a couple of tests which would take a couple of minutes to confirm the element is ok in favour of randomly changing parts and expecting a bunch of strangers online to help.
 
Is it me or am I being thick.

There's 1 cable going to a single element, which works OK on boost but not off peak?

Puzzled!

It sounds like it. With a boost controller to swap it onto the 24hr supply for the boost.

So it has a 24hr supply from a 60898 16A and an off peak supply from a 3871 15A
The 24hr works but the off peak trips after ~1hr
The element is untested.
So we could have a worn out 3871, or a faulty 60898, or an element just starting to break down. Or any combination of the above

Plus we have an OP who has fitted a new boost controller and now wants to rip the customer off for a new CU just in case that fixed it. Oh yeah, he hasn't tested the element either for unspecified reasons.

I'm only assuming he has actually looked inside the cap of the I/H and confirmed it's a single element. It may yet turn out to be dual element and a 4 core cable!
 

Reply to off peak immersion problems in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K
  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
169

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top