hi .customer complained that her off peak water wasn't heating.its a ex b7 controler .boost worked fine on 24 supply.there is just 1 cable going to tank [1 elememnt] but off peak trips old wylex 15a push button mcb
sorry dont no the bs number.changed the b7 controller because it was 25 years old anyway.the off peak came on to give her a full tank of hot water and then next day trips.never tested element or cable because the boost works fine on a mem 16 a mcb.i am going to put in a 2 way consumer unit tomorrow for off peak.
surely it has to be that pop mcb that is faulty.has anyone else came across similar scenarios .thanks
 
This sounds to me that you may have a problem with the off peak supply feeding the controller. If it works on boost supply but blows when it runs on the night supply the chances of the element being defective are minimal. I would firstly disconnect both supplies from the CU and controller and carry out proper i.r tests to clarify firstly your circuits feeding the unit are healthy.
 
[ElectriciansForums.net] off peak immersion problems
. this is the clock in question or similar
 
I am saying if the off peak is dedicated ie only live on off peak,one element, one flex, how is that going to work without linking both 24hrs and off peak cu's together.?
 
I am saying if the off peak is dedicated ie only live on off peak,one element, one flex, how is that going to work without linking both 24hrs and off peak cu's together.?

It's just a changeover switch with a timer.

It's normal position is with the element connected to the off peak supply.
When the timer is activated it changed over to the 24hr supply for the time period then drops back to the off peak supply.
 
I am saying if the off peak is dedicated ie only live on off peak,one element, one flex, how is that going to work without linking both 24hrs and off peak cu's together.?

The unit basically works as an either or switch. If the switch is in the off position the element draws no supply......
If you switch it to boost and turn the boost dial it uses the on peak circuit for the time you set the boost dial for......if you choose to switch to 'timed' supply the boost dial is rendered dead and the element becomes live when the off peak circuit becomes energised by the dno. All functions from one element, thats how it works matey.
 
The clock 'davesparks' mentioned is a similar method of operating the element the only difference being that the boost unit has only two switch positions instead of three. Same outcome with only one element. [emoji106][emoji106]
 
It's just a changeover switch with a timer.

It's normal position is with the element connected to the off peak supply.
When the timer is activated it changed over to the 24hr supply for the time period then drops back to the off peak supply.

That makes sense, but an easier way would be to have the IH circuit on 24hrs, with E7 tariff, when off peak kicks in the whole installation goes over anyway, so change over switch/ clock not needed.
 
That makes sense, but an easier way would be to have the IH circuit on 24hrs, with E7 tariff, when off peak kicks in the whole installation goes over anyway, so change over switch/ clock not needed.

Exactly Dave, but unless you want to stay up until midnight or 1 in the morning every night to switch it on you still need a timer.
 
That makes sense, but an easier way would be to have the IH circuit on 24hrs, with E7 tariff, when off peak kicks in the whole installation goes over anyway, so change over switch/ clock not needed.

One problem with that one matey. You'd have to have the switch on all the time which would send your bill through the roof and knacker your thermostat inside the tank in next to no time with it kicking in and out all day. Alternatively you'd have to manually switch it on at night when the E7 kicks in.
 
the E7 BX is the horstmann timer of choice for THTC installations .
It can be configured to either feed an off peak heater and boost heater or a single heater by putting links across 5+9 and 6+10.
make sure they are not mixed up as one is the live and the other the neutral!
I find them pretty reliable tbh as there is no moving parts to them unlike their E7 quartz cousins.
the off peak is switched by the radio telemeter at various parts of the day.
the boost is available 24 hr.
check the heater and thermostat first.look out for white powder in the bottom of the case a sure sign that the element is on its way out.
if ok check your controller is wired up correctly.the BX can get a bit congested with 10 terminals in it..
check your circuits after this.
these types of plug in mcb used to have a 3k rating if i mind right and if its had a short odds on its knacked.
 

Reply to off peak immersion problems in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K
  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
169

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top