I was changing the consumer unit today and look how the previous person has earthed the main water and gas!
[ElectriciansForums.net] One way of earthing the pipes.....


I will give them 10 out 10 for ingenuity:confused:

Here's how it looked after i had finished.
[ElectriciansForums.net] One way of earthing the pipes.....


On a totally different job i was called out to i came across this fitted by a so called electrician.
[ElectriciansForums.net] One way of earthing the pipes.....

The bottom of the rcd is feeding straight out to the RFC.
How he thought that a 63amp RCD on it's own would comply with regulations is beyond me.I had to removed the enclosure and fit a larger one so that i could fit a 32 amp mcb next to the RCD as it needed.
The guy even charged ÂŁ330 just to fit that unit!

It saddens me that cowboys like this get away with it and tarnish qualified electricians in the process.:mad:
 
Never been pulled before for tie wrapping the bonding wires and i've done it for numerous inspections before.What harm can it do.They aren't hot or don't move so i cannot see the problem?
The NIC did issue guidance on this very thing some time ago, I only have the BRB to hand so the reg number may have changed, but 528.3.3 (proximity to non-electrical services) basically states that where an electrical service is in close proximity to another service it shall be arranged that work on that service does not affect the electrical service. I suspect that is the reg that applies.
 
Not a criticism at all Bob but with the meter tails going in through the rear and not glanded I'd secure then with clips or small cleats.

Cheers mate.The tails are cleated at the back of the board before i fitted it so they aren't going anywhere;)

Is there a definite regulation about not tie wrapping bonding cables to the pipes anywhere?
I can understand not tie wrapping t&e cables but bonding cables?
 

Reply to One way of earthing the pipes..... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
884
  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top