Opinion on Supply System Type Wanted: TN-S or TN-C-S | on ElectriciansForums

Discuss Opinion on Supply System Type Wanted: TN-S or TN-C-S in the The Welcome Forum area at ElectriciansForums.net

J

jlrb

Hi - My first post to this forum.

I am having a disagreement with another electrician on the type of the supply characteristics for a domestic installation, i.e. whether it is TN-S or TN-C-S. I have uploaded a photo of the cutout/supply head. To resolve the disagreement I suggested we ask for a 3rd, 4th, 5th .... opinion from the forum.

The building is in a suburban area and is over 100 years old , not that I am suggesting that the supply head is that old. There are no PME labels/markings. The measured Ze is 0.11 ohms.

Thanks for your views in advance.

jlrb

Supply Type.jpg
 
Did you test L-N fault loop?

measure both pefc and pscc. if they are the same, i'd opt for TNC-S.

As Murdoch and telectrix suggested:

Measured PEFC = 2.10 kA (0.11 ohms)
Measured PSSC = 1.30 kA (0.18 ohms)

This indicates to me that it is TN-S rather than TN-C-S, but I was expecting the relative values to be the other way around - but on reflection I am not sure why I should expect that.
 

Reply to Opinion on Supply System Type Wanted: TN-S or TN-C-S in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top