K
keith@kbw
can any help me, i need to install 200amp three phase supply at 135m long, i wish to run two smaller cable insted of one large size cable, so can any one tell how to calculate for parallel cables supply.:confused:
we are supplying a water teatment plant, which needs 120amps 3 phase+N and we have to run parallel cable plus earth cable, what i am looking for is formulas to calaculate cables sizes.
Max demand and diversity along with possibly power factor correction to be considered, The link below could prove usefull to you hope it helps. :)
cablecalculation
Also appendix 4 of the big red book will give you all you need with regards to calcs rating factors ect.
I would think a 185mm is a bit over and without checking would have thought a 4c 120mm
would be ok or 2x 4c 70mm in parallel also i believe cables in a trench underground benifit from the natural cooling of the soil
yours benji
Do you have all the details of equipment you are connecting? Supply over 100A really should take into account Xl and Xc so a bit of j notation might be required. As for the two cables thing if your calcs ask for a 400mm2 cable for example and you want to use two for ease of installation just use 2 x 200mm2.
Reply to parallel cables in the Australia area at ElectriciansForums.net
https://sravivarman.com/technical-articles/parallel-operation-of-thyristors/ Series resistor, or bigger series resistor, needed?