RCD CODEs
Code 1: The main RCD or voltage operated earth leakage circuit breaker on a TT system failes to operate when tested
Code 1: Absence of RCD protection for socket-outlets in bathrooms or shower rooms, other than SELV or shaver socket-outlets
Code 2: Absence of fault protection (protection against indirect contact) by RCD where required, such as for a socket-outlet circuit in an installation forming part of a TT system.
Code 2: Absence of RCD protection for portable or mobile equipment that may reasonably be expected to be used outdoors
Code 2: Neither local supplementary bonding nor RCD protection is present in a bathroom or shower room.
{Note the absence of any code for RCDs to protect cables in walls etc Rule 522.6.7}
SUMMERISING THE REPORT
It would not be reasonable to indicate a
‘satisfactory’ assessment if any observation in
the report had been given a Code 1 or Code 2
recommendation.
{I think thuis should read "It would be unreasonable to indicate a ‘satisfactory’ assessment if any observation in the report had been given a Code 1 or Code 2 recommendation. }
DEALING WITH CODE 1s
Where, during the course of inspection or testing, a
real and immediate danger is found to be present in
an installation (from an exposed live part, for
example), immediate action will be necessary to
make it safe before continuing.
Contractors should note that, even in domestic
premises, Section 3 of the Health and Safety at Work
etc Act 1974 and the Electricity at Work Regulations
1989 effectively require them to endeavour to make
safe, before leaving site and with the agreement of
the user or owner, any dangerous conditions found
in an installation.
From this we can only conclude that the final report can under no circumstance have any code 1 s !!!!!!!!
Apart from my conclusion in italics, all above are extracts from the BestPractice Guide published by the ESC.
*********************************************************************************************************
The above was my first post and was not originally displayed ! That below was my second post and has been joind to the first! What is happening?
***********************************************************************************************************
I'm wondering it its worth replying again. I've just spend 20mins getting quotes from the ESC Guide to best practice and it all got lost when I posted. Anyway the guide escentiall says:
If its a TT system the RCD failure or none existance is a Code 1
Lack of RCD protecting a bathroom is Code 2
Lack of RCd to protect cables in walls ect (Rule 522.6.7) dont even warrent a code!!!!
All items posing an immediate danger (ie Code 1s) must be fixed or made safe before leaving site. So I conclude you cant have any code 1 s left when you write out the report!!!
To answer the original question:
Both sparks mentioned need to re-consider their City and Guilds. BS7671 is NOT a legal document and nobody is required to comply. At best they can only be advised to upgrade. In any case (as mentioed by others) items which are not in accord with current standards (2008) are simply Code 4 unless they constitute an immediate or potential danger. This includes the lack of a cpc in a lighting circuit, even though the best practice guide on that subject recommends us to recomend a re-wire. Only the "lack of a cpc in a circuit feeding Class 1 equipment other than a lighting circuit" scores a code 2.