The regs are not rectrospective,if an install complied with the regs when it was installed,but does not meet the current requirements of bs 7671,in most cases the code would be 4.
A lighting circuit in a commercial property surface wired and on a TN system would not require RCD protection.
A lighting circuit in a domestic property surface wired would not require RCD protection.If that circuit included a bath/shower room,that would be a code 4.
A lighting circuit with buried cables wired prior to the 17th edition (2008)did not require RCD protection,it was safe then and it's safe now...therefore code 4.
RCD protection cannot be a substitute for lack of adequate earthing....if a lighting system with class 1 fittings does not incorporate an earth that would be a code 2 or even a code 1 if there was evidence of a low IR or failing insulation....Lack of RCD to such a circuit ( even if it is required) is a different issue altogether.