Hi guys,
Doing a periodic on a cabin which is to be used for buisness use.
Its a new install and the one thing i have seen which im not sure weather it warrants a code or
not is they have a chandelair type fitting where the bracket is screwed to the beam,
Meaning due to the size of the fitting its possible for someone to put there hand above the
fitting and go into the connection behind it.
The height from floor to the fitting is 2.25m
would you guys snag this.
thanks
 
The top surface of an enclosure needs to meet IP4x regardless of how high it is above FFL


Sent from my iPad using Tapatalk

416.2.2 - horizontal top surface of an enclosure which is readily accessible shall provide at least IP4X (I've not typed word for word)

2.25m above the floor is not readily accessible to my way of thinking!
 
If the connections are properly done within the 'cap' then it should still meet IP2X and not pose a hazard with regard to a finger touching a live terminal , who would be stupid enough to poke fingers in there anyway ?
 
416.2.2 - horizontal top surface of an enclosure which is readily accessible shall provide at least IP4X (I've not typed word for word)

2.25m above the floor is not readily accessible to my way of thinking!

2.25m is within arms reach when standing on the floor, hardly inaccessible is it?

Plus of course the fact that someone has to gain access to the light fitting to change the lamps means that it must be readily accessible.
 
2.25m is within arms reach when standing on the floor, hardly inaccessible is it?

Plus of course the fact that someone has to gain access to the light fitting to change the lamps means that it must be readily accessible.

Its not as if someone could accidently poke their fingers into something that high! This is similar to ensuring any cable connections are enclosed in an enclosure that requires a tool to gain access. If somebody wants to get a stepladder and don't know what they are doing then they deserve all they get!

The other reference I've seen with respect to 'readily accessible' is the top surface of a consumer unit that is situated immediately below the ceiling, does that need to be IP4X? Especially now when using metal enclosures that in some cases have larger cable knock-outs.
 
What's all this "above 2.25m" and "readily accessible" chat about ? As far as I am aware the regs make no allowance for these factors and just state that all enclosures shall be IP4X on their horizontal top surface.

I stand to be corrected though


EDIT: Just read the wording of the reg and corrected myself :D
 
Last edited:
What's all this "above 2.25m" and "readily accessible" chat about ? As far as I am aware the regs make no allowance for these factors and just state that all enclosures shall be IP4X on their horizontal top surface.

I stand to be corrected though


EDIT: Just read the wording of the reg and corrected myself :D
Yellow van man has the correct reg number to cover this but i would agree with others that it is readily accesable
 
Yellow van man has the correct reg number to cover this but i would agree with others that it is readily accesable

I was kind of meaning that I have always maintained IP4X on any enclosure regardless of accessibility. Glad to be corrected by me reading the reg properly though. Though without a definition of readily accessible.......... nah that's another debate.
 

Reply to PIR coding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
690
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
900

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top