I wonder how this was comunicated? and to who?
i actually had no idea they was going to run the cable when we wasn't on site , i just gave them the list to get on site , other than that the removed and replaced a large section of the block paving and slabs
they did well considering how busy that part of the job , just a shame they didn't get it completely right lol
i actually had no idea they was going to run the cable when we wasn't on site , i just gave them the list to get on site , other than that the removed and replaced a large section of the block paving and slabs
they did well considering how busy that part of the job , just a shame they didn't get it completely right lol
So its not their fault then..................
so if i tell you that we need a 35mm swa and a 16mm earth run in for the mains , and you only run a 35mm swa and forget the earth even though theres an email trail then I'm guessing its your fault ...... or is it just me
so if i tell you that we need a 35mm swa and a 16mm earth run in for the mains , and you only run a 35mm swa and forget the earth even though theres an email trail then I'm guessing its your fault ...... or is it just me
So what exactly did the email say?
You previously said you gave them a list of what to get onsite ....
My experience of builders leaves me in no doubt, spell it out AND check they understand - and sometimes it'll still go wrong - the only way to avoid issues like this is to supervise/help on the day.
i think i started my original question by stating that the builder forgot to run the earth cable , trying to gage a easy result in solving the issue, be it by earth rod or if the builder needs to dig up the road/ earth again.
the builder him-self was the one on my last site visit to show me that his men forgot to run the earth , i confirmed to him ill do some homework and see if its a big issue or if theres an easier route
didn't realise idd have to remember word for word of emails (i do a few ) to provide as evidence ????
and the fact they undertook the works between us on site (1st fix that took 3 to 4 weeks) and our planed return to site to start 2nd fix is just unlucky but i guess worked with there plans
moving on , its now proven that the swa braid is correct for the required bonding earth size so all and all no issues
no blame needed, was about solving an issue , which has been sorted
Staff member
Admin
Esteemed
Supporter
I disagree, the armour is not adequate.
whys that ?
I'm only quoting what the NICEIC told me via phone conversation
Staff member
Admin
Esteemed
Supporter
If they told you the armour of that cable is adequate to support bonding they are incorrect.
-
Mentor
Arms
V.Nearly Esteemed
If your protective bonding conductors require to be sized 10mm copper minimum then if you intend to utilise the armouring of the swa then the sizing must be equivalent of 10mm copper as an example an 85mm steel conductor would meet this requirement as the copper to steel ratio would be 8.5 as referenced in GN8
Staff member
Admin
Esteemed
Supporter
I would like to know where the NICEIC got 84mm from as this goes against GN8 which quotes 79mm and from manufacturers spec I have looked at none are quoted at 84mm.
Have you got it in writing from the NICEIC Helpline that the SWA is adequate for bonding?
Are they also prepared to stand over their calcs if the s**t hits the fan?
I'm hopping your wrong , but would be great to be sure either way
I've got a few days before I'm back on site , so time to make sure I'm clear on how to proceed
Reply to PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...