Has anyone ever encountered a fault with a RCD which causes a potential on earth in respect to neutral?



I am a trainee electrician, working with an experienced electrician. We encountered a fault today, earth had a potential of 238V in respect to Neutral and a 0 V potential in respect to line.



We did an insulation resistance test at 500V on all circuits from line to neutral, line to earth and neutral to earth. All circuits gave a resistance of >999M ohm. So there is no way line and earth can be crossed anywhere.



The fault didn't trip the RCD or the MCB, yet there was a potential difference between neutral and earth.



We got really strange voltage readings while probing around, differences between earth and neutral ranging from 100v to over 300v, how can this be as nominal voltage was 238V.



The potential difference between neutral and earth was greater when the RCD was in the closed position.



All I can possibly think of is the somehow the line windings around the iron core in the RCD have made contact with the Neutral windings. Could a fault like this possibly create a voltage on Neutral, and cos it is a TN-C-S system, Neutral is connected to earth at the incoming supply, so is it possible this voltage could be seen on the earth bar in the consumer unit?
 
Hi dude,no guess would be possible,without knowing where you were measuring this voltage,and what position all the various switches/breakers,etc were in.

Start from a position upstream,where all measurements are as expected,or if not,somebody has a bigger problem :)
 
I just would like to know if anyone thinks it is remotely possible a fault inside the RCD could cause this issue?
 
You've posted this on another forum.

Why didn't you test Ze?

Yes I got a temp ban on this forum, so I joined another one. You use two forums too, else how would you know?

We didnt suspect the issue to be with the distributor.
 
Sounds like a floating neutral to me.

With the earth connected to the DNO's incoming earth, what resistance are you getting between N > E
 
So Gigsy..... are you going to update this forum with your findings reported on the other forum?

Is that necessary? I don't think anyone would be interested? Is it frowned upon to use two forums? If so why do you use more than on forum? Which forum do you like the best? Why are you making an issue with me using two forums?
 

Reply to Potential difference between Earth and Neutral in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
740
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top