View the thread, titled "Power to shed." which is posted in UK Electrical Forum on Electricians Forums.

I was changing an extractor fan today and while I was there noticed the set-up he had for his shed: 2 x s/o + 1 fluorescent light via a junction box in the shed, what looks like 2.5mm SWA down the small garden into a box on the outside of the house then through into the living room to a 13A RCD plug plugged into a living room socket.

I wanted to tell him that it all seemed a bit of a bodge but couldn't think of what was actually unsafe about it. Any ideas what I could say to him next time I see him (assuming that 'it doesn't seem right' won't make the grade)?

Thanks.
 
may not be ok for the big green book, its protected by a 13a fuse in the plug, rcd in the plug, possibly another rcd and a fuse in consumer unit. small job of adding a fused spur instead of a plug, and another 6a fused spur for the ligting in the shed will do, if someone insists and pays for fixing it.
 
It might be a bit rough, but nowhere in the BGB does it talk about aesthetics and what you describe would meet all the applicable regs. In fact, I would go so far as to suggest it doesn't even qualify as fixed wiring therefore not even of interest for Part P.
 
When i've got a little bit more time i'll search the regs for you, but im not sure what it actually doesn't comply with - Effectivley he's plugging the garage in, regardless of whats on the end of it. I don't like the fact the lighting and sockets are off the same plug without a FCU though.

- What sort of box does he outside? isit ip44?
- Lighting and socket together without a FCU is a no-no
- forget the light, hes got 2 sockets spurred off one without FCU.
- Has he terminated the SWA properly into the outside box?

Theres nothing wrong with spurring the garage off a socket providing the load is adequate. The socket he has got the SWA connected to in the living room needs a FCU chased in next to it, i'd probably even suggest using T+E in this case aslong as its buried and placed in flexible conduit (or something similar) from there to the 2 sockets and another FCU put in for the light inside the garage fused down accordingly.
 
When i've got a little bit more time i'll search the regs for you, but im not sure what it actually doesn't comply with - Effectivley he's plugging the garage in, regardless of whats on the end of it. I don't like the fact the lighting and sockets are off the same plug without a FCU though.

- What sort of box does he outside? isit ip44?
- Lighting and socket together without a FCU is a no-no
- forget the light, hes got 2 sockets spurred off one without FCU.
- Has he terminated the SWA properly into the outside box?

Theres nothing wrong with spurring the garage off a socket providing the load is adequate. The socket he has got the SWA connected to in the living room needs a FCU chased in next to it, i'd probably even suggest using T+E in this case aslong as its buried and placed in flexible conduit (or something similar) from there to the 2 sockets and another FCU put in for the light inside the garage fused down accordingly.

Go on.... I'm looking forward to this......
 
I was changing an extractor fan today and while I was there noticed the set-up he had for his shed: 2 x s/o + 1 fluorescent light via a junction box in the shed, what looks like 2.5mm SWA down the small garden into a box on the outside of the house then through into the living room to a 13A RCD plug plugged into a living room socket.

I wanted to tell him that it all seemed a bit of a bodge but couldn't think of what was actually unsafe about it. Any ideas what I could say to him next time I see him (assuming that 'it doesn't seem right' won't make the grade)?

Thanks.

Supplied via a RCD socket. OK IMHO but as asthetics go it stinks.
 
As said although a bit rough it does seem to comply, the circuits protected by the 13A plug top fuse and an RCD.

When i've got a little bit more time i'll search the regs for you, but im not sure what it actually doesn't comply with - Effectivley he's plugging the garage in, regardless of whats on the end of it. I don't like the fact the lighting and sockets are off the same plug without a FCU though.

- What sort of box does he outside? isit ip44?
- Lighting and socket together without a FCU is a no-no
- forget the light, hes got 2 sockets spurred off one without FCU.
- Has he terminated the SWA properly into the outside box?

Theres nothing wrong with spurring the garage off a socket providing the load is adequate. The socket he has got the SWA connected to in the living room needs a FCU chased in next to it, i'd probably even suggest using T+E in this case aslong as its buried and placed in flexible conduit (or something similar) from there to the 2 sockets and another FCU put in for the light inside the garage fused down accordingly.

2 sockets spurred off one?...it's on a 13A plug...that only applies to unfused spurs from ring finals, this has 13A protection squire.

SWA is a lot better than T+E in flexible conduit too, it's not adequate protection for burial...
 
Probably safer than most shed feeds. It's got isolation facility, rcd, suitable cable for an outdoor run. Daz
 
Well look's like im going to have to bite the bullet on this occasion and quite simply eat humble-pie. Reading back my last post, literally no idea what i was thinking...

As said although a bit rough it does seem to comply, the circuits protected by the 13A plug top fuse and an RCD.



2 sockets spurred off one?...it's on a 13A plug...that only applies to unfused spurs from ring finals, this has 13A protection squire.

SWA is a lot better than T+E in flexible conduit too, it's not adequate protection for burial...

First point, appologies - honestly no idea what i was thinking, like you say its just rough-arse work. Apologies also for the burial quote, however do i have time to change the word burial to clipped lol?

Go on.... I'm looking forward to this......

What do you mean by that exactly? I said, that i don't think it contravenes any regs. But i will check at some point.
 
i have a job in the pipeline. a feed to a wooden shed/garage. client wants just a couple of sockets and a florry. to come from the CU is a no go as it would involve a 40m trench. however, there is a double socket on the RFC handy, RCD protected, so as to require only a 2m trench in easy dig ground. i have 3 options..


1. using 4 core 2.5mm SWA, extend RFC to garage sockets.

2. using 4mm 2 core SWA, spur off RFC. sort of reverse lollipop circuit.

3. fit FCU at 13A in house to spur to garage.

each option would, of course entail a 3A or 5A FCU in the garage for the light/s.

be nice to hear thoughts on the above. which option would you go for?
 
i have a job in the pipeline. a feed to a wooden shed/garage. client wants just a couple of sockets and a florry. to come from the CU is a no go as it would involve a 40m trench. however, there is a double socket on the RFC handy, RCD protected, so as to require only a 2m trench in easy dig ground. i have 3 options..


1. using 4 core 2.5mm SWA, extend RFC to garage sockets.

2. using 4mm 2 core SWA, spur off RFC. sort of reverse lollipop circuit.

3. fit FCU at 13A in house to spur to garage.

each option would, of course entail a 3A or 5A FCU in the garage for the light/s.

be nice to hear thoughts on the above. which option would you go for?

Option 4. 20A isolation switch off existing RFC, 3 core 2.5mm SWA to garage, 1 x 13A FCU (or put this at house) 2 x 2G sockets and FCU for lights. Defo not keen oin extending RFC into garage without any way of isolating it!
 
Option 4. 20A isolation switch off existing RFC, 3 core 2.5mm SWA to garage, 1 x 13A FCU (or put this at house) 2 x 2G sockets and FCU for lights. Defo not keen oin extending RFC into garage without any way of isolating it!

so what about fusing down for the 2.5mm spur? i am thinking a 13A D/P FCU, but that gives him a very small capacity in the garage.
 

Reply to the thread, titled "Power to shed." which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top