after my rather vague thread Friday about finding the 30 mtrs of 10mm 2 core swa In the back of me van.....after some views on earthing to the shed, 3 options as far as I’m aware are
1. Run a single 10mm from main met upto the shed and use that
2. Use the armour of the swa, adiabatic permitting..
3. Connect the swa to the main met at source end and TT the shed
Each option is appruthe same cost wise and it’s my own house so Labour is not a big issue, as per title just after others views and preferences....
 
Oh god! Here goes......

If = 230x0.95 (c min) / 0.36 (Zs) = 606 a

t = 0.1s (40a 60898 mcb)

K = 115 (copper line conductor) / 51 (steel armour) x 10 size of line conductor = 22.54

Sooooooo......

S = (sq root symbol ?) 606a 2 x 0.1/22.54 = 8.5mm

CSA of 2 core 10mm2 swa is 41mm2 so all is good?

Kill me now!
 
Last edited:
Why does t = 0.1s?
It’s a distribution circuit, so t = 5s.
Actually t is the actual disconnection time. So in this instance it won't be anything like 5 seconds, but probably between 0.01 and 0.1 seconds.
 
Yeah, 0.1s is as low as BS7671 goes for your calcs, any Zs =/< max Zs for that 60898 would achieve that (as needs at least that fault current). As Zs drops, fault current increases and disconnection will get quicker. Would require manufacturer's data if you needed to go lower than 0.1s to satisfy thermal constraints but you definitely don't need to in the case of this job.
 

Reply to Pros...cons...preferences.. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top