There is one fundamental thing I don't understand about PME supplies.

If the line conductor comes into a system and the neutral goes out, then in a balanced system the current should be the same in both conductors right?

So in a PME system the earthing conductor is connected to the live neutral conductor.

Why then is the earthing conductor not live as well and hence all othel conductors connected to it?

Thanks for your time.

Regards
Harry
 
The neutral conductor carries the same current level as the Phase conductor in a balanced system

The phase conductor is at 230 volts with regard to true earth,because the neutral of the supply transformer is earthed at the star point of the transformer

Because the neutral is earthed at the star point,then its potential difference to true earth may be just a couple of volts
So yes the earth system in an installation and everything connected to it are at that low potential

The suppliers spike the neutral conductor at various points to make sure that it maintains that low potential
Hence the protective multiple earthing

Because of the possibility of that neutral/true earth potential rising due to external problems
PME should be assessed with regard to exporting it to garages and sheds etc
 
As described by Des, the neutral conductor in PME is spiked (connected to the ground) at multiple points on it's route to consumers, therefore you cannot get a shock off it in theory as it is at the same potential as you stood on the ground.
 

Reply to Query regarding PME in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top