I am a new member to the forum and a relatively new spark. When I went through my training I became very familiar with the layout of the rig in the training centre and felt very confident. But when I went out into the real world I quickly realised that every installation is different and it can be a little confusing. I take my time, refer to my notes and publications and occasionally check out the forums for advice. Today I was a little confused about Ze and sub boards and this thread has jogged my memory. Thanks guys, I really appreciate the advice.
 
Well you would take a reading at the sub board in a similar way to taking a Zs and people refer to it as Zdb. Ze is the external reading and should be taken with the Earth bond disconnected to ensure no parallel paths. At a sub board this is not the case.
 

Reply to Questions regarding testing for Main/Sub Distributor board. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
514
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
915

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
503
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top