R1+R2 continuity both ways | Page 2 | on ElectriciansForums

Discuss R1+R2 continuity both ways in the UK Electrical Forum area at ElectriciansForums.net

S

shinypen

Hi. Testing an old lighting circuit today after a c/u change. First few readings were all fine. Then on one rose I got a reading of 0.5 ohms switch closed (fine) and 186 ohms switch open.

Is this indicative of an insulation problem or something else? I did an IR test and got 0.75 ohms but it was a bit rushed and couldn't be sure it wasn't just an error. That is very low surely? I'll do that again tomorrow.

I'd be grateful for suggestions!
 
could there be a switch with built in ilumination ?

[ElectriciansForums.net] R1+R2 continuity both ways
 
It always mystifies me when an (alleged) low IR is encountered that a neon always seems to get the blame. This would only happen on a L-N test, the OP has not specified what IR test has been carried out but I doubt it's L-N. Or is it OP?
 
Tested polarity of incoming supply, ze@ board, direct zs and pfc of several points on system and bonding before hand. All were fine. The board was a mess and a real tangle of too short cables.

I freely admit to being new to this so as an aside is it really common practice to do a full set of tests on every part of every circuit before a board change?

In this instance it's my board and any problems that arise need to be fixed by me anyway. Surely safer and easier once a new board in place.
 
No damp areas? Almost like there is something else in the circuit? Or when you IR'd did you have cpc on the bar still with neutral connected?
Thanks anthony. This is helpful. I did indeed have the cpc still connected to the bar. Hadn't realised this could introduce problems. I'll update this post at the end of the day with the results! Hopefully just that and an incorrect ir test...
 
Yes it's always best to IR test before CU change why? because you are adding RCDs to the system, and any IR N-E L-E will trip the RCD, nothing more frustrating than changing CU all nice and neat, then do your testing, no bonding IR faults file:///C:/Users/Pete/Downloads/Best-Practice-Guide-1-Issue-3-(1).pdf
 

Reply to R1+R2 continuity both ways in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top