Hi. Testing an old lighting circuit today after a c/u change. First few readings were all fine. Then on one rose I got a reading of 0.5 ohms switch closed (fine) and 186 ohms switch open.

Is this indicative of an insulation problem or something else? I did an IR test and got 0.75 ohms but it was a bit rushed and couldn't be sure it wasn't just an error. That is very low surely? I'll do that again tomorrow.

I'd be grateful for suggestions!
 
If you're not taking the neutral of the circuit you are testing out of the neutral bar at the CU, then you are effectively IR testing every circuit connected to that neutral bar. If any one of those circuits has a low IR then this will bring down your reading. Surge protectors plugged into a ring main will also show a low IR to earth. I think Powerbreakers show this too??? Also a combination of circuits with acceptable but low IR can combine to give an overall low IR that fails.

Always best to take both live conductors out at CU before IR testing. And I tend to test at 250v first to make sure there's nothing still plugged in or wired in before giving it full 500v. If L-N still shows continuity and I cannot find the thing wired into the circuit then I will just IR test st 250v with L and N tied, to avoid frying the thing. Chances are it's a TV amp or smoke detector or PIR or something equally sensitive to meggering.
 

Reply to R1+R2 continuity both ways in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top