I think we have ended up slightly at cross purposes. I have no issue with anyone using OSG, BS7671, Pro Certs, or any other reliable reference of the resistance of copper in order to work out expected R1+R2 values.Okay, if i had a radial circuit wired in 6mm/6mm swa and the measured R1/R2 was 0.16ohms. What table or resistance value would you personally use to calculate the length of that circuit as a reference point, and what length would you calculate?
Since you disagree with using the onsite tables and the procert one, im curious what you would use?
Two things concern me about this thread:
1. The OP is conducting EICRs but not doing any live testing.
2. The OP is conducting EICRs without knowing basic things like how to calculate R1 and R2 values.
3. Sorry there is no third thing
Two things concern me about this thread:
1. The OP is conducting EICRs but not doing any live testing.
2. The OP is conducting EICRs without knowing basic things like how to calculate R1 and R2 values.
3. Sorry there is no third thing
For EICR purposes, the two things that come to mind are how close the calculated Zs is to the limit for the device, and a sense of how big the property you are in is and whether a reading seems plausible. The more you do the easier that gets.All I was wondering is if they was a table about I could use as a guide for r1 r2 readings so I know my readings are correct or slightly high and I need to do abit of further investigation on circuits
Surely a bad connection is going to make BOTH readings off.Previously I’d do dead and live testing and I’d be able to check check the r1 r2 results by the zs readings
Yea I generat know what I’m looking at what seems high and things but I just wanted something to work towards incase I was been slightly generous and over cautious chasing faults that didn’t really need further investigation.For EICR purposes, the two things that come to mind are how close the calculated Zs is to the limit for the device, and a sense of how big the property you are in is and whether a reading seems plausible. The more you do the easier that gets.
e.g. if you're re in 2 up 2 down and you get 1.5 ohms for an immersion heater circuit then a bit of head scratching is due.
The other thing you can do is try RN+R2 or use a wander lead to obtain a 2nd frame of reference, and whether it's R1, R2 or both that have a loose connection.
I'm assuming that you are allowed to do Ze, Zs@DB and RCD tests, and your company only prohibits live Zs readings?
I do know the methods for carrying them and things,This is so basic for someone qualified. Whether dead or live testing, you should know the methods of carrying them out (and working them out) without thinking.
Yea we carry out ze and rcd testsThis is a 'modern' take on Zs testing that you don't do it live except for socket outlets where there is no risk of exposed live parts but as @timhoward asks do you carry out Ze and rcd tests.