Kev2632

What readings would expect for the wandering lead method whilst testing from the consumer unit to the sockets, would you expect in the region of less than 0.10 ohm?
 
yea its a ring final but the conduit is the CPC and once ive deducted the resistance of the "wandering lead" im getting less than 0.10 ohm for the resistance of the conduit, does that sound right?
 
What cable is used? Is it a RFC or a radial? whereabouts are you expecting to get this <0.1 ohm reading and why mate?

see his thread from yesterday for the whole story and this will all become clear.

He needs to find a fault in a circuit with high loop impedance where conduit is the earth.
 
yea its a ring final but the conduit is the CPC and once ive deducted the resistance of the "wandering lead" im getting less than 0.10 ohm for the resistance of the conduit, does that sound right?
so from yesterday, we can deduce that the fault is on the live or R1 part of the circuit giving you greater than 200 ohms overall.
 
yea when i moved onto the Ringmain im getting less than 0.10ohm for the R2 reading on the ringmain circuit does that seem to be right ?yea
 
you didn't mention yesterday it was a ring final. Have you taken all the socket fronts off?

im on a different circuit than yesterday and all im wanting to do is get my R2 reading for the ringmain and im getting less than 0.10ohm for the ringmain does that sound right? its a 1 storey 1 bedroom house really small.
 
i'l chance it and say yeah, sounds about right. You're spending some time testing this house!

yea thats what i was thinking ye, you always expect really low readings like that yea, with a small house and when testing for the R2 reading yea??? nahh ive been busy with other jobs and that this last two days, only got a wee while here and there at it like.
 
yea, well let me take a pull of this here spliff while i think, nahh, bad weed, poor joint somewhere.
 

Reply to R2 test on a ring main where the conduit is the earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top