R2 test on a ring main where the conduit is the earth | Page 2 | on ElectriciansForums
Discuss R2 test on a ring main where the conduit is the earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Low readings on a conduit system R2 reading is what you want and the reading you got was fine. remember its a big lump of metal and a high reading would indicate bad joints!! and a bad joint really aint what you want.. Telextrix pass round what ever that is :)
So it's still eligible to do the r1+r2 test on the ring main where the conduit is the CPC yea? Just link at board and test at each socket yea?
Reply to R2 test on a ring main where the conduit is the earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Often, but not always: 543.2.9 Except where the circuit protective conductor is formed by a metal covering or enclosure containing all of the...
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...