Give the customer the choice , the prices and the pros and cons and let them decide
 
I also ran 6mm radials whilst working in Canada @110Volts using MK 110V socket outlets, had nil trouble with connecting them up either. Just saying.

I cannot understand how someone can be working on electrics in Canada and not know the voltage is 120v plus or minus 5%. 110v is a myth and outside the permitted tolerance.
 
I cannot understand how someone can be working on electrics in Canada and not know the voltage is 120v plus or minus 5%. 110v is a myth and outside the permitted tolerance.
Hi check regulations , can use radial 2.5 mm serves 50 square meters 20 amp cb& 4mm at 75 square meters 32 amp cb
 
If you think about it, if you take an RFC wired in 2.5 and supplied by a 32A MCB and: remove one section of cable, and split the tails across two 20 or 25A MCBs then you have :
  • Increased the total available current from 32A to 40 or 50A
  • Reduced the amount of cable used
So the two radials (assuming a new install or a rewire) will need less cable and provide a higher total load capacity than the same outlets wired as an RFC. You've also (assuming RCBOs) reduced the amount of stuff that goes off when a breaker trips.
However, you've also increased the volt drops. So if the alternative RFC was on (or near) the limits, the two radials would most likely be over the limits for volt drops.
 
Increased the total available current from 32A to 40 or 50A

However, you have also restricted where the current can be used. With a 32A circuit, regardless of whether it is radial or an RFC, you could spread 32A around half of it, or all of it, and nothing will be overloaded. With two 20A radials, to get even 32A let alone 40A it has to be correctly split between the circuits, which the customer knows nothing about and may not be convenient. E.g. if a room gets flooded and needs drying out, they will plug two heaters and a dehumidifer in there and the 32A circuit would be OK with that, whereas a 20A might trip. I know that's an unusual situation but there are lots of similar scenarios.

This is one of the advantages of the 32A socket outlet circuit that is often overlooked - a larger circuit with more points makes better use of diversity and is less likely to get overloaded if the loads are not in the anticipated places. A typical family home with GCH will run quite happily on a single 32A circuit. Not ideal in the event of a fault etc. but it works fine for loading. Our entire living area used to run fine on one 30A Wylex MCB with lounge, dining room and kitchen including washing machine, tumble dryer, dishwasher, fridge, freezer, microwave etc. Theoretically you can't put just the washer and dryer together on a 20A.

But, importantly, the distinction between 32A circuits and 20A circuits is a different one to the difference between RFC's and radials. The current rating dictates how many circuits are needed, the RFC / radial aspect dictates cable size, testing method etc. A 32A radial provides the same functionality as a 32A RFC.
 
I agree with all of that. But of course, a 32A radial needs more copper than a 32A RFC.

On overloading radials, at a local church the boiler broke down so they had to use electric heaters - which could barely take the chill off. Of course, someone got over ambitious - and after blowing a fuse (radial on 15A rewirable fuse), told me he'd been careful and plugged them into different sockets :rolleyes: He was also amazed that I was able to find the blown fuse :astonished:
 
I rarely do final ring circuits now, generally radial in 4mm but watch the cable length.
 

Reply to Radials V Ring mains in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
785
https://www.amazon.co.uk/gp/product/B08CJ3VC79/ref=ppx_yo_dt_b_asin_title_o05_s00?ie=UTF8&psc=1 I use this, current clamps go round each outgoing...
Replies
3
Views
755

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top