Hi,

Our breaker box is located in the cellar. We experience random socket trips throughout the year. Summertime seems to be the best when we can go months without an issue.

Autumn/winter time is awful. We have had 3 trips within the last 24 hours. No new appliance has been switched on when the trips occur.

Could it be a faulty RCD? Is it the location of the breaker box? Please help.
 
Is there any signs of condensation on the consumer unit or in the cellar?
 
If you have a dehumidifier you could try putting that near the consumer unit and see if that helps.
 
Hi Fuz and welcome to the Forum:) .
Repeating trips don't happen for no reason and aside from the inconvenience to you it could be a fault that's getting worse and so may become dangerous at some point. If it's not related to an appliance then as Buzz has advised, I think you'll be best served by getting your local friendly Electrician around to have a look. Most do "attend and work for an hour" callouts. Someone here may be nearby (?).
 
Fuz, what actually trips, is it the RCD for a set of mcb’s, or is it an individual mcb that keeps tripping?

If it’s the mcb, is there a label below it that says what circuit it’s protecting and what is plugged in to the sockets of this circuit?
 

Reply to Random socket tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
671
  • Question
The RCB was only just put in. The board was last week and yes we have the cert already. The new board was not only because of the tripping but...
2 3
Replies
32
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top