B

BlueToBits

Hi
Has anyone else found that about 10% of RCBOs appear to fail the 5I test but pass at the rated (30mA) current?

(Telaris 0100 plus)
 
several times on RCDs. even took my mft for checking. apparently some wylex units are suspect. they have recalled MCBs recently
 
Thanks
I have recently tested about 100 of these and I found 11 with rated trip times of around 20ms but 5I trip times of over 50ms. My tester is probably due for re-calibration but I find it surprising they pass at 30mA but fail at 150mA where others of the same type, rating and manufacturer are OK.
 
thanks
i have recently tested about 100 of these and i found 11 with rated trip times of around 20ms but 5i trip times of over 50ms. My tester is probably due for re-calibration but i find it surprising they pass at 30ma but fail at 150ma where others of the same type, rating and manufacturer are ok.
in the select certs that i use it only asks for x5 test times on 30ma r.c.d,s not r.c.b.o,s. So i only test them on x1
 
Cant say I have, I test about 150 RCD's of all different types, makes and sizes every 6 months and they seem to either pass on all tests or fail on all tests.

tester calibrated annually too.
 
All but one were in the same installation and were Crabtree Loadstars in TP distribution boards, the other I found yesterday (whilst on my annual NICEIC assessment) was a Denman's "Basic"

I found that taking an rcbo out of the board and shaking it around hitting it almost to the point of causing physical damage would sometimes give a satisfactory test but not consistently. I did suggest to the NICEIC that I could change the wording on the quaterly test label...
 
in the select certs that i use it only asks for x5 test times on 30ma r.c.d,s not r.c.b.o,s. So i only test them on x1

Really???

So when a 32A 30mA RCBO is used to give additional earth fault protection to a socket outlet circuit for instance, you would not test a 5x because it isn't an RCD???
 
ive always found square D on x 1 always close to or over the 40ms mark ,other makes crabtree wylex hagar prolec niglon to name a few test below 30ma
 
I found that taking an rcbo out of the board and shaking it around hitting it almost to the point of causing physical damage would sometimes give a satisfactory test but not consistently..

You need a technical adjustment tool

But on a serious note, I have not come across any failures lately, mainly Hager, Wylex and a load of Zehler I have fitted from Meteor Electrical, all I have fitted recently had exactly the same results and I started to wonder if my tester was playing up, tried with another tester and all the same.
 
in the select certs that i use it only asks for x5 test times on 30ma r.c.d,s not r.c.b.o,s. So i only test them on x1

Can I ask you please if you are serious about your statement? Or if it is a wind up?

I'm not attempting to humiliate anybody. I'm trying to gain an understanding on the what areas are commonly misunderstood, what with all these express train training companies and courses.
 

Reply to RCBOs fails 5I test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
7K
suffolkspark
S
  • Question
I don't think it will work with only one stake unless some meters have different operating parameters. It doesn't necessarily have to be a stake...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top