just thought i would update this since i spoke to hager technical dept ant the IET.Also so the ESC switched on issue 18
Hi Jamie
Please see the reply from Hager technical manager I received earlier. I recall a megger engineer on the national committee mentioned something similar about the meters being affected by this when loads were in circuit
Hi Richard,
Quick reply as I am in and out of company meetings!!
I hope the following answers the questions. Out of interest, please can you tell me the type of connected load.
I am assuming thatyour comment "it fails to trip at 150ma (x5) within 40 mS" means ittrips, but appears to exceed the maximum time?
This is a known phenomenon attributed to the load (capacitance) influencing the RCD tester.
This is why the correct RCD test procedure prescribed in GNs states:"The load supplied should be disconnected during the test".
The ESC are currently investigating this, please see attached, page 15 "Influence of connected loads".
Richard Townsend
Senior Engineer
Standards and Compliance
The IET