looking for a fault on a caravan where the rcd trips when a main earth is added. with no main earth the rcd want trip. the caravan has only got an earth path via bonding from the earth rod to the db and no main earth from the earth rod to the db.
zs is 66.4 on sockets 67 on lights and 66 on the shower.
the board has been tested and no faults found. as soon as u add 4mm or a 10mm main earth the rcd trips when say the cooker or shower are turned on.
Are you saying that there is a connection, earth cable, between the db and earth rod?
When you then say main earth what do you mean?
Sounds like a right bloody mess ;)
What is the supply earth at the meter (assuming the van is individually metered) ... often TNS, then SWA to the CU.
I'd be tempted to sort out the earth first before looking for errant equipment.
this is an old set up. swa in coming to rcd, rcd to card meter, then meter to db. there is currently no earth from the earth rod to the db. only from the caravan frame to the db. with this as it is the rcd doesnt trip. when u add an earth straight from the rod to the db the rcd will trip when ever the cooker or shower is turned on. all other caravans have the same set up and same earthing arrangement. its just this single caravan
Then it sounds like you have a fault either in the wiring (or an appliance(s)), or possibly a faulty RCD. Do a ramp test and see at what current the RCD is actually tripping ... typically 20 odd milliamps (20-29) for one rated at 0.030 amps. If it's substantially less than that then replace it.
all circuits have been tested, no faults found, rcd has been replaced twice with ones i know that work. appliances work fine when theres no main earth tho. rcd trips at 26.6 and 14.9 before appliances are turned on with main earth in place
How can there be two different trip currents for the RCD?
The only thing that leaves, if all tests are ok, is leaky appliances. The reason that it won't trip before the "main earth" is connected is that there is no where for the current imbalance to go (so line/neutral are in balance).
Reply to rcd not tripping in the Australia area at ElectriciansForums.net
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...