looking for a fault on a caravan where the rcd trips when a main earth is added. with no main earth the rcd want trip. the caravan has only got an earth path via bonding from the earth rod to the db and no main earth from the earth rod to the db.

zs is 66.4 on sockets 67 on lights and 66 on the shower.

the board has been tested and no faults found. as soon as u add 4mm or a 10mm main earth the rcd trips when say the cooker or shower are turned on.
 
when an rcd trips it usually is because there is an ir fault, ie l-n l-e n-e. or high current in the earth from computers, 6 or more on one circuit ish, ITS A PROBLEM IN THE INSULATION. it might be as small as a fixing screw nicked a neutral, open everything and check.
 
when an rcd trips it usually is because there is an ir fault, ie l-n l-e n-e. or high current in the earth from computers, 6 or more on one circuit ish, ITS A PROBLEM IN THE INSULATION. it might be as small as a fixing screw nicked a neutral, open everything and check.

I think you might be right, myself I would bypass 1st RCD and the meter for a test and install a secondary RCD in the right place
 
some of you are are so good that I am afraid to say my opinion in case I am wrong and had few drinks now.

I don't think RCDs are designed to be installed before the meter, the interference could be the problem .
Just wade in mate, we're all trying to help. Even if it's wrong (I am frequently) it may jog someone else's memory and we find a solution.
 
Another afterthought. The meters at each van are often owned by the caravan site (not the DNO) and are used to work out what to charge each van. The main meter to the site is what the park gets charged for and they then apportion the costs to each van.
 

Reply to rcd not tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
800
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top