Just been looking at the new regs book cant find any change for the need for rcd protection on minor works i.e extra socket to existing circuit
Was this recommendation dropped
 
First off, only circuits of special locations require RCD protection.
As such unless the RFC includes a socket-outlet in a bath or shower room, or the installation is TT or agricultural/horticultural, there is no requirment to provide RCD protection to a RFC.
If you are extending the circuit and concealing cables in walls, you are required to provide additional protection for those cables.
If you are adding socket-outlets for general use by ordinary persons, or to supply mobile equipment outdoors, then those socket-outlets must be provided with additional protection by means of a 30mA RCD.
As for the best method, that is something for you and your client to determine.
You could provide the whole RFC with 30mA RCD protection with a separate RCD in an enclosure.
You could run earthed sheathed cables and use RCD sockets.
You could install the cables in earthed conduit or trunking and again use RCD sockets.
If all you are doing is spuring off a RFC, you could use an RCD FCU.
 

Reply to Rcd protection new regs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
800

Similar threads

  • Question
I will go over and get some photos, the CU is well labelled and very long with many breakers. I never seen one that big in a small flat but then I...
Replies
8
Views
802
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top