E

eco-tech

The job im about to do is a extension and im going to extend the ring main and the lighting radial etc.

The client does not want me to chase his walls to the 50mm that regs states and he will not pay for a CU change and a full part P test as his board is not a split RCD Cu.

So i would like to know if i can use RCD Sockets on the ring main in the extension and bury the lighting cable in conduit to meet regs etc ?

Please Advise if i can do this ?

This way i can issue a Minor-Works Cert !
 
Hi

The requirement for RCD's is to protect the cables in the installation as well as whatever is plugged in to the sockets. RCD sockets offer no protection of your wiring between CU/ring and the new socket outlet so won't allow compliance with 17th edition. Running in conduit is fine if the conduit is earthed.

Can you fit RCBOs in place of the circuit MCBs or would the customer accept surface mounting of the cables in trunking?
 
using RCD sockets does not protect the cabling that is not buried more than 50mm. However, if you spur off the ring main using an RCD fused spur, this may comply for your extension.

And doing you lighting circuit in conduit would mean doing the switch drops in conduit and would have to be chased anyway and will make a major mess. Im pretty sure it will have to be earth metallic to??? unless you surface mount in mini-trunking on switch drops

cheers

D.

beat me to it ;)
 
Last edited by a moderator:
RCBOs look the best option on both lighting and Sockets if i can fit them in the board !

Would i still be able to cover the install with a Minor Works cert ?

Spur off the ring main Hmmm is this within the regs ?
 
Last edited by a moderator:
Yup, you're extending existing circuits, not adding new ones so Minor Works Cert. is OK

RCD protected fused spur is OK off the ring
 
Last edited by a moderator:
Thought so but needed to check it out.

Thanks for that.

Hmmm one more thing, im told they may want a extractor replacing in the bathroom so as its not a new circuit i could get away with the part p too yes ?
 
If you are doing a like for like swap of the extractor then no need to notify under Part P. No need to raise a cert. either if it is just a simple swap.
 

Reply to Rcd sockets in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
551
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
922

Similar threads

Many thanks. Very clear!
Replies
2
Views
288
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
465

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top