The more I read, the more i find out the more I think with 15th edition equipment then possibly the whole house could do with attention to bring it up to the same standard as the new addition and incorporate it into one installation
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss RCD splitting question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
So i have to install a new board to create a new way rather than tap off the tails and put in an extra 17th CU that can feed the extension board because there is no supplied main isolator and because the house is only 4 bedrooms?Isn't this just like tapping off a busbar chamber with a new board and labeling it DB2 then making the extension DB2/1 at both ends?
.....If the property is as you describe I absolutely agree with you,final circuits should be run to a single DB...but as this info was not provided your all encompassing statement concerning additional DB's in a single property is misleading and incorrect.......you dont have to agree,but you are wrong.First off .... It wouldn't then be a ''Single Dwelling'' house if the extension was to be an annexe or separate flat, would it?? Then you would be correct...That info wasnt available in the OP,therefore your general statement about having 2 DB's in one propety was misleading
If this was a large house to start with, it would be very doubtful the owner would be adding a two storey extension, ....not impossible, but doubtful!! I would suggest that the now present size of house is in all probability a 4 bed-roomed house converted from a 2 or maybe even a 3 bed-roomed house. ....So how many 4 bed-roomed houses have you seen with 2 completly separate CUs supplying it's electrical needs??? That info was not in the OP either....you appear to have an uncanny ability to decipher imformation that is not provided
I stand firmly behind my statement, ...it's certainly not misleading and it's not incorrect either. If we were talking about a very substantial 3 or 4 storey house, or of the like you could possibly have a valid point.
Well no mate....if it's a TT an RCD with be necessary at the origin to provide fault protection to the distribution circuit...ideally a 100ma time delayed with a split rcd board in the extension.....if it's a TT and thats how the OP is going to do it
Absolutely loath submains run in twin nad earth. Its the skin flint way IMO!
Though we now know it's a TN-S system the sole use of RCD protection for a SWA distribution cable is not totally correct. Reg 411.5.2 does state the prefered method of fault protection should be an RCD, but providing that the Zs allows disconnection time then another type of protection device can be utilised such as a BS 88-3 ( 1361) fuse.
I know that in design you may not be able to achieve the required Zs by calculation, but in reality with earth paths and bonding it may be achievable.
Absolutely loath submains run in twin nad earth. Its the skin flint way IMO!
Technically correct.yes...but in practice the chances of getting a low enough Zs for a 60a bs 88 fuse with a rod are around zilch.