Turning off normal single-pole (SP) MCBs won't narrow it down, as they don't switch the neutrals. Hence Brian's comment that over time, with the increasing use of RCBOs with double-pole switching that do isolate the neutrals, troubleshooting will get easier.
 
Thank you.
So can this be caused by an appliance that is plugged in and has a fault?
And turned off at the socket, in most cases. Some sockets have double pole switching, but they are rare.
This is something I've spent hours on the 'phone, trying to explain customers, while trying to avoid being dragged out on 'emergency' calls.
 
Thank you - but what if it hasn't been pressed for say 3 years - I am just buying a socket tester with a "RCD test button" I will try this on a circuit to see if that trips the MCB (I assume that "safely" shorts the live and earth) I will explain the "3 Years later!"
 
If a RCD isn't tested regularly, the hair trip mechanism can become stuck in place and the contacts of the test button can tarnish. If you can get it to trip, and then 'exercise' the mechanism, by tripping and resetting it several times, they can usually be brought back to life.
Note that anon working test button is a fail when an electrical condition report (EICR) is undertaken, and will result in the installation being declared 'unsatisfactory'.
 
Thanks for all your advice I really appreciate it - so trying to trip the MCB via a socket tester would show if the problem was with the test button and if the RCD was working or not?
Now I will explain the three years - The Consumer unit is in Thailand! and was installed by a "professional" electrician (at least as professional as you will get in Thailand when we built the house - EICR in Thailand -non existent) 8 years ago.
I tested the RCD at least twice a year until - Covid struck and I was in the UK and my Thai partner was in Thailand we were apart for just over 2 years and asking her to check it would have been a useless exercise and I must admit when I got back in January I forgot to check it until now!
 
Your socket tester is better than nothing, in that it will confirm that the RCD is kaput, if it is, but a full test involves checking that it trips within a certain range of leakage current, and measuring the time it takes to disconnect the power, which has an upper limit.
 
Your socket tester is better than nothing, in that it will confirm that the RCD is kaput, if it is, but a full test involves checking that it trips within a certain range of leakage current, and measuring the time it takes to disconnect the power, which has an upper limit.
I understand what you are telling me and of course if I find I need to replace it I will get a "professional" to do that.
This is the tester I am buying - I'll let you know and thanks again
 

Attachments

  • [ElectriciansForums.net] RCD test button not working
    Screenshot 2022-12-17 105612.png
    389.3 KB · Views: 12
Your socket tester is better than nothing, in that it will confirm that the RCD is kaput, if it is, but a full test involves checking that it trips within a certain range of leakage current, and measuring the time it takes to disconnect the power, which has an upper limit.
 
Sorry to bother you again but I have just noticed that the RCD in my consumer unit has a variable trip can be set to 5, 10, 20, 30 (currently 20) and the socket tester is available in 30 Ma or 5 Ma RCD tester should I buy the 5 Ma socket tester not the 30 Ma tester as being more sensitive?
 
That is the first time I have seen an adjustable RCBO!

Generally if you get a 30mA tester it will show if any RCD/RCBO that is rated from 5-30mA is working OK or not. It is not as precise a test as an electrician can do with the appropriate test equipment to verify the trip-time (usual test at fixed 'fault' current at device's specification, e.g. 30mA) and the trip current (done by slowly ramping up the 'fault' current to see at what point it fires). Any external tester would confirm if it is the RCD that has failed/stuck stuck, or if it is the self-test button that has failed.

The use of 30mA is normal in the UK/Europe for most applications as that is the threshold for 'reversible effects' (i.e. it hurts but you are OK immediately afterwards):

What RCD/RCBO don't do is limit the shock current, what they do is limit the exposure time above a certain current which limits the physiological impact but it still depends on how conductive the event was (e.g. if dry skin contact or wet, etc ,etc). So RCDs are very useful in the prevention of death/injury but are always "additional protection" along with the basic protection of suitable insulation and earthing of metalwork, etc.
 
That is the first time I have seen an adjustable RCBO!

Generally if you get a 30mA tester it will show if any RCD/RCBO that is rated from 5-30mA is working OK or not. It is not as precise a test as an electrician can do with the appropriate test equipment to verify the trip-time (usual test at fixed 'fault' current at device's specification, e.g. 30mA) and the trip current (done by slowly ramping up the 'fault' current to see at what point it fires). Any external tester would confirm if it is the RCD that has failed/stuck stuck, or if it is the self-test button that has failed.

The use of 30mA is normal in the UK/Europe for most applications as that is the threshold for 'reversible effects' (i.e. it hurts but you are OK immediately afterwards):

What RCD/RCBO don't do is limit the shock current, what they do is limit the exposure time above a certain current which limits the physiological impact but it still depends on how conductive the event was (e.g. if dry skin contact or wet, etc ,etc). So RCDs are very useful in the prevention of death/injury but are always "additional protection" along with the basic protection of suitable insulation and earthing of metalwork, etc.
 
As promised feedack on this thread - socket tester with RCB test button fails to trip MCB on any circuit.
So I guess that means a new RCB.
Once again thanks to all those who gave me advice - and the seasons greetings.
 
Just noticed a little switch, labelled on/off on the pic of this RCBO. Is this to switch off the RCD part, just leaving the MCB?
Before giving up on this device, I'd give it a good 'exercise', by switching it off and on again several times..
 
Just noticed a little switch, labelled on/off on the pic of this RCBO. Is this to switch off the RCD part, just leaving the MCB?
Before giving up on this device, I'd give it a good 'exercise', by switching it off and on again several times..
Thank you for that - this is what happened - I switched of the little black switch and inserted the socket tester in a socket and pressed the test RCD button - One of the main switches tripped and the black button (which is labelled earth leakage indicator) came out (see pic) resetting the earth leakage black button allowed me to reset the the switch that had tripped.
Not really sure what that is telling me except that isolating the RCDO appears to provide some degree of protection (and maybe that the RCDO is Defunct).
Until I get an electrician to look at it do you think it would be better to leave the RCDO isolated?
 

Attachments

  • [ElectriciansForums.net] RCD test button not working
    Complete consumer unit 1.jpg
    405.7 KB · Views: 9
The switch that you have the red arrow pointing at IS the RCD, as far as I can make out from the pic, and tripping to the downwards position is exactly what it is supposed to do when earth leakage is detected. You introduced an imbalance between the live and neutral currents going through it, by using your socket tester, and the RCBO indicated earth leakage to be present (a feature not found on UK RCBOs) and then the big red switch turned itself off.
This is exactly what it should do, as far as I can tell from here.
 
The switch that you have the red arrow pointing at IS the RCD, as far as I can make out from the pic, and tripping to the downwards position is exactly what it is supposed to do when earth leakage is detected. You introduced an imbalance between the live and neutral currents going through it, by using your socket tester, and the RCBO indicated earth leakage to be present (a feature not found on UK RCBOs) and then the big red switch turned itself off.
This is exactly what it should do, as far as I can tell from here.
Once again thank you Brian.

I must admit to being somewhat confused. The black switch that you told me to exercise was ON when the test button on the consumer unit would not work – after you told me to exercise the switch, I switched it OFF and then tried the socket tester and the trip worked!

I have now tried the test button on the consumer unit and it works correctly – this is with that little black switch set to the OFF position! So I’m unsure what that switch is switching ON and OFF.

Very confusing for me (but maybe not for you!).

Another thing I have now noticed is this: the picture I sent you was taken in May this year just before we came to the UK for 5 months (I added the arrows just before I sent it to you). In that picture you can see the little black switch is OFF and the trip value was set to the minimum 6mA.

I haven’t changed any of the settings since my return but the mA is now set to 30 and as I said above the little black switch was ON.

A Thai neighbour “took care” of the house whilst we were away and I am wondering if some “tinkering” took place for some reason.

Anyway, these are my problems and getting an admission from a Thai is impossible – I am happy that the RCBO protection is working. (not sure about the MCBs for tripping although all circuits appear to be working).

Finally, I worked in IT for 40 years (I’m 78) and I know how difficult it can be for a professional dealing with people who already have some knowledge, but limited, on a subject, so I say again I really do appreciate that you were prepared to offer your assistance with this issue.
 

Reply to RCD test button not working in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
327
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
Thanks everyone for your help on this one, I've bookmarked the other thread. Turns out on this one it was a faulty RCD, I went back with a new...
Replies
22
Views
2K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
626
  • Question
I misread it.
    • Like
Replies
13
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks