RCD trips a few minutes after lights turned on | Page 2 | on ElectriciansForums

Discuss RCD trips a few minutes after lights turned on in the UK Electrical Forum area at ElectriciansForums.net

H

harpoon

Hi all,

I am trying to diagnose the following problem.

After coming back from holiday, we noticed that our RCD keeps tripping a few minutes after our kitchen lights have been turned on. If the kitchen lights are kept switched off, then everything is ok.

The lights were GU10 spotlights connected to a dimmer switch. Replaced the dimmer switch with a trailing edge dimmer and replaced the GU10 with dimmable LEDs ... and the problem is still present.

Any ideas what this could be and how to test the fault ?

Could there be water somewhere in the ceiling cavity ?

Any advice is appreciated !

Many thanks !

Harpoon
 
Has anyone come across this before ? ... i.e. RCD only trips after the circuit has been switched on for a while ... does it make sense ?
Yes as conductors gently begin to heat up from draw of current (even low temperature)a low insulation problem in the wiring can operate the protective device or rcd
 
Yep, I agree with Will, the reason I asked if low voltage or mains voltage was because if they had been low voltage, the transformer would have come into play and may have been faulty, but as they are mains this does not apply.
How old is your wiring?

It's the RCD tripping, as transformers are generally class 11 how are they going to trip the RCD?
 
Its been a fairly wet week across Britain so damp on that part of the lighting circuit might be an issue. Seeing as you have changed the switch and lamps its pointing towards the wiring instead. Basic Insulation Resistance testing would find the fault but remember to disconnect your brand new accessories. This is simple fault finding for any decent Electrician, call one.
Why disconnect the accessories?
If the RCD is tripping there is no point in L-N tests, therefore no point in disconnecting accessories and potentially removing causes of the tripping during testing resulting in wrong conclusions.
 
It's the RCD tripping, as transformers are generally class 11 how are they going to trip the RCD?
I agree under normal circumstances a class II device should not trip an RCD but we have a fault situation and possible dampness, if a transformer is sitting in a puddle of water in the ceiling void would this not cause the RCD to trip?
As the OP had changed the lights and the fault still existed, I was thinking what else could there be, it has been eliminated anyway as they are mains powered.
 
Why disconnect the accessories?
If the RCD is tripping there is no point in L-N tests, therefore no point in disconnecting accessories and potentially removing causes of the tripping during testing resulting in wrong conclusions.

The point would be to separate L and N so that you can establish whether the fault is L-E or N-E, which may (or may not) assist in the fault finding process.
 
I agree under normal circumstances a class II device should not trip an RCD but we have a fault situation and possible dampness, if a transformer is sitting in a puddle of water in the ceiling void would this not cause the RCD to trip?
As the OP had changed the lights and the fault still existed, I was thinking what else could there be, it has been eliminated anyway as they are mains powered.

It would hopefully cause something to trip if it's sitting in a puddle of water but then you'd expect the ceiling to be noticeably wet and discoloured. This wouldn't be unique to transformers though as that much water would likely have got in to joint boxes etc.
Also I wouldn't expect connections sitting in water to present such a delayed tripping action.
 
Why disconnect the accessories?
If the RCD is tripping there is no point in L-N tests, therefore no point in disconnecting accessories and potentially removing causes of the tripping during testing resulting in wrong conclusions.

OP said he had already swapped the dimmer and lamps and the fault is still occurring. He has then ruled out that the aceesories are not at fault. He should remove them anyway to properly carry out insulation resistance testing.
 

Reply to RCD trips a few minutes after lights turned on in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

Have you notified Building Control of these works?
2
Replies
19
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top