hi i have the following problem, im open to ideas:cool:

16th ed board. 100ma old wylex stand alone rcd installed on the tails protecting all circuits , 30ma split in the board covering sockets shower etc as you would expect.
i had to connect a replacement shower cable from 6mm to 10mm afetr a bathroom refurb.

i arrive esstablish tt system 133 ohms possible to convert to pme (.31ohms) if required, carry out zs at shower unit along with ins res test, all good.
I then carry out rcd test and nothing trips.
i walk to board and re test NOTHING.
I decide it must be 30ma rcd and return with a new unit, install it and .. NOTHING.

I am unable to get either rcd to trip even in i apply test current at the 100ma wylex unit, i have checked my testers and they work.

i think i read somwhere that these old wylex rcd units work in a different way to modern ones, could they cancel each other out?? (magnetic operation)

my next visit will be my third and im open to solutions to save another trip.

any ideas?? :cool:
 

Reply to rcd will not trip in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
590
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
771
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

M
  • Question
I believe you're in Australia? Could you clarify the distribution arrangements - is this RCD for one particular circuit, or is it protecting a...
Replies
1
Views
291
Glad you got it sorted.
Replies
9
Views
803

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top