shovelhead

Hi
can anyone help.

I have just done an extension to an annexe, using 3 core 1.5mm swa for the lighting and 4 core 2.5mm for the ring into a 2 way CED Garage Consumer Unit with a 63A 30mA RCD, 32A and 6A MCBs.

Ze, Insulation resistance and continuity test came out fine testing with a Megger MFT 1553 but the RCD will only trip at 5x.

Any advice please?
 
Ill have a guess, remove bus bar and do a three lead test on the load side terminal screws and see if it trips. This means your rule out any possibility of it being down to the circuit(s) your testing. Coreect me if im wrong though :D
 
Ill have a guess, remove bus bar and do a three lead test on the load side terminal screws and see if it trips. This means your rule out any possibility of it being down to the circuit(s) your testing. Coreect me if im wrong though :D
No need to remove busbar. Switching off circuit breakers will do.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD won't trip
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
35
Unsolved
--

Advert

Thread statistics

Created
shovelhead,
Last reply from
telectrix,
Replies
35
Views
4,915

Advert

Back
Top