2394:Basics .
BS-7671:2011: States - Three-fundamental-requirements. for fault-protection by ( ADS ) in a TN - system . ( Exams )
- Protective-Earthing. - Regulation - 411.3.1.1.
- Protective-equipotential-bonding - 411.3.1.2.
-Automatic-disconnection in case of afault - Regulation-Group - 411.3.2.
• Protective-Earthing . - ( All Protective-conductor)
Earthing-arrangements consisting of the ( Means ) of earthing . the ( Earthing-conductor ) & the circuit-protective-conductor(s) connecting the . exposed-conductive-parts tothe ( MET ) must be present . adequately-sized & properly-connected such that their contribution to the . Earth-fault-loop-impedance ( Zs ) is sufficiently-low . ( Circuit-loop-impedance)
• Protective-equipotential-bonding
Main-protective-bonding-conductor(s) . complying with Section - 544 . are required to connect all . Extraneous-conductive-parts . to the ( MET )
• Automatic-disconnection .under-earth-fault-condition(s) isrequired . to provide fault-protection .Automatic-disconnection . can be provided by a suitable . Overcurrent-protective-device . under earth-fault-loop-impedance . is sufficiently-low to satisfy the disconnection-time requirements of BS-2011: or alternatively . by a RCD - residual-current-device. provided the appropriate requirements are Met .
Protective-devices. ( Genetic-Name )
For. fault-protection - Regulation - 411.4.4. . requires one or more . of the following types of protective-devices to be used.
• An Overcurrent-protective-device such as a . Fuse or Circuit-breaker .
• An RCD .
The operating-characteristics of overcurrent-protective-devices . complying with the relevant product-standards are given in p.295. Appendix - 3 .
- The purposeof ( Earthing ) where used for the .protective-purposes . within an installation. ( is to limit the Duration of the voltages )
- In ( Contrast ) the purpose of ( Bonding) is to limit the ( Magnitude of the voltages )
Whenan . Earthing-Conductor - isre-moved . What’s in a Regulation . !!!!!
Main-Earthing-Terminal - ( MET ) disconnectionof .
542.4.2. “ let’sget this out the Way “
To facilitate-measurement of the résistance of the . earthing ( Arrangements) means shall be provided in an accessible-position . for disconnecting the earthing-conductor . such means may conveniently be combined with the . ( MET ) or bar . Any joint shall be capable ofdisconnection only be means of a tool .
Regulation- 542.4.2. does not stipulate aparticular-arrangement . for the means of disconnection . ( Any suitable- arrangement may be used which meets all the requirementsstated in the Regulation )
2394:- So what is suitable-arrangements. in which case the ( Earthing-conductor ) iswithdrawn for its ( Terminal ) atthe main-earthing-terminal . by the useof a Tool - Screwdriver . 2394 inorder to facilitate the résistance-measurement . ofmeans of earthing .
Forthe sake of -&-s here . “ Safety “ ( Earthing-conductor ) thenreplaced & re-secured into the terminal after the measurement hasbeen made .
(MET ) incorporating a ( Bolted-link ) which isopened or re-moved by the use of a Toll ( Spanner ) in order to disconnect the ( Earthing-conductor ) & then replaced & re-secured after the résistance-measurement to the means of earthing has been carried-out.
TheRegulation are telling us - whatever ( Arrangement ) is provided as the means fordisconnection . of theEarthing-conductor .
Inaddition to the requirements of Regulation - 542.4.2. Thisrequirements of the . Electricity atWork Regulations & these of Section- 522 - BS-7671:2011: must be Met .
Regulation - 9 . of the Electricityat Work Regulations . requires that .
“ if acircuit-conductor is connected toearth or to any other reference-point . nothing which might reasonably be expected to ( give rise to Danger ) by breaking theelectrical-continuity or introducing . high-impedance shall be placed in that ( Conductor ) unless suitable-precautions are taken toprevent that - “ Danger “
Wherea . joint or bolted-link is provided . it must be arranged to ensurethe ( Integrity ofthe conductor ) theconnection or link . must not be able to be re-moved insuch a way as . would give rise to “ Danger “ ( Ways of achieving this )
□ Disconnection requires a deliberate-act using a Tool .
□ The Joint or Link should be ( Accessible-only ) .when the installation is ( Isolated )
□ The Joint or Link should be ( Accessible ) toSkilled-persons - Only .
Section- 522 . requires that the means fordisconnection must be protected . where necessary against . External-influences.
What- External-influences !! . Vandalism . Unauthorized-interference . Damp . Corrosion . Dust . Vibration or mechanical-impact .
2394: What Implications’ - 132.16. . this one will work its way into Exams .
Additions& Alterations to an installation .
We’llgo by the book . BS-7671:2011:
“ No addition or alteration . temporary or permanent. shall be made to an . existing-installation . unless it has been ascertained that the. rating & the condition of any existing-equipment . including that of the distributor . willbe adequate for the . altered-circumstances . furthermore . the ( Earthing& Bonding-arrangements ) if necessary for the protective-measure applied for the safety of the addition or alteration . shall be adequate .
Adequacy of the Existing-installation . is therefore required to be assessed in three-areas .
- Existing-equipment . including that of the supply . which mayhave to carry - increased-load .
(T) - Earthing and Bonding-arrangements.
- Certain additional-considerations .
(T) - Existing . Earthing and Bonding-arrangements (Assessing the adequacy & suitability of the existing-earthing& bonding-arrangements ) Upgrading .10.0mm[SUP]2 [/SUP]
-Establishing the suitability of the meansof earthing in respect of its type - such as a PME-earthing-terminal or anEarth-rod . & condition .
asan Inspector your looking for . Corroded . damaged . inaccessible .
2394{- most-important-Test . “ Verification “ of the means of earthing by . determination of theexternal-earth-fault-loop-impedance - (Ze ) Regulation - 313.1.
If - ( Ze ) is determined by . ( theRegulations remind us - “ Methods of determining ( Ze ) at least one of the Three-methods ) must be used to determine ( Ze ) .
i). Enquiry .
ii). Calculation .
Itis necessary also to obtain a measured-value to “ Verify “ that the intended-means of earthing is both present andof the expected-value . ( by - measurement Ω )
2394{- in our case here . Only “ (iii) . Measurement “
Determination of external-earth-fault-loop-impedance -at the Origin of the installation . The importance of determining the normal-range of - ( Ze )
Theeffectiveness of the measures of ( Fault-protection ) against thermal-effects & protection against . earth-fault-current in each-circuit of an installation depends on the value of ( Ze ) this is because ( Ze ) contributes to the . total-earth-fault-loop-impedance - ( Zs ) of each-circuit . it is therefore essential that in the design of an installation . account is taken of anychanges that can reasonably be expectedto occur in the value of ( Ze during the life of the installation )
- With the possible ( Exception ) ofa supply from a privately-owned-generator.
Itmust generally be presumed that whateverthe source of supply to an installation . ( changes may occur in the value of Ze atsome time during the life of theinstallation )
- Ascertainingthat the ( Earth-conductor ) isof adequate . cross-sectional-area . mm[SUP]2[/SUP]
The ( Earthing-conductor ) ofan electrical-installation is the . ( Protective-conductor-connecting ) the Main-earthing-terminal - (MET )
(T) - . 2394 {- Means for disconnecting the -Earthing-conductor .
542.4.2. requires means for disconnecting of the . earthing-conductor. to be provided at or near the ( MET )of an installation to facilitate ( Measurement of the résistance ) of the earthing-arrangements.
Additional- Considerations . ◄ ( Wording )
Additional- considerations relating to the . ( Existing-installation ) or any effects that the ( Addition or Alteration ) may have upon it .
Point to Note : not specifically mentioned in Regulation - 131.16. are covered by . other - requirements of BS-7671:2011: making them . applicable .
Grouping-effects.
Rating of all cables . in the wiring-system ( both Existing & the Proposed-additional-cables ) must beassessed to take account of any .additional heat generated by the larger-grouping . & be de-rated as necessary . if theexisting-cables would not be adequate when de-rated . then one option would be to install the .new-cables separately from theexisting-group .
Isolation & Switching .
New-circuit(s) may place - additional-load . on theexisting-isolation &switching-devices . which have to be “ Verified “ as being adequate for the increased-load . New-equipment may have particular-requirements for isolation & switching that must be Met .
- if a . new-circuit is the supply a .discharge-lamp-operating at thevoltage exceeding ( LV) low-voltage . a fire-fighter’s switch would be required Regulation - 537.6.1.
Upgrading of an - Existing-installation . Where-necessary .
Whenan ( Existing-installation ) is not adequate to support aproposed-addition or alteration safely the work . must NOT - proceed.
- The ( Client ) must be . advised - Immediately . & preferably in writing .
- The necessary-upgrading-work . should be recommended to the . ( Client )
- When the . ( Client - consent ) has been given . the upgrading-work should be completed ( Before ) the additionor alteration is put into ( Service )
Upgrading - Work . necessary toenable an installation to . safety accommodate the . Addition or Alteration .
- replacementof any equipment or cabling having-defects . Omissions . Damage or minor-deterioration .
- replacement or upgrading of existing-equipment in theinstallation where its rating is notadequate .
- addition to . or upgrading of ( Main-protective-bonding-conductor ) inan installation relying on the ( Protective-measures - ADS ) for protectionagainst electric-shock . if the ( C.S.A. ) of the exciting bonding-conductor(s) is found to be less than that required - BS-7671: the installer . of the addition oralteration will need to make . a Judgement as to the suitability of those conductor(s) & whether the . new-work mayproceed .
If Exceptionally ) it isdecided that it is safe to proceed . with the new-work without upgrading the ( Equipotential-bonding )the client should be advised that the . ( Bonding ) should be upgraded to the current -standard at the earliest-opportunity .
- replacementof any . voltage-operated-earth-leakage-circuit-breakers . with residual-current-devices- RCDs . if fault-protection relies upon the successful operation of thecircuit-breaker(s) . this would be necessary to ensure compliance with theapplicable Regulations’ in BS-7671: that requires an RCD to be provided .
Whereprotection against electric-shock isprovided by ( ADS ) Regulation -411.3.3. Additional-protection .
411.4. - TN-system . 411.5. TT- systems . require an RCD to be used under . certain-conditions .
A voltage-operated-earth-leakage-circuit-breaker would not be considered to provide adequate protection in such conditions - it does not comply with the requirements of BS-7671:2011:
Chapter- 61 contains the requirements for . Initial-Verification . Inspection & testing must be performed to confirm the adequacy & suitability .
- The relevant-parts of the existing-installation . tosupport the changed-requirement .
- The upgrading of the existing-installation . necessary to support the addition or alteration .
-The addition or alteration itself .
Certification:
Regulation- 610.4 . requires that compliance with . BS-7671:2011: is Verified for every ( Addition or Alteration ) Chapter - 63 contains requirements for . Certification & Reporting . in respectof electrical-installation(s)
631.1. & 631.3. which requires an . ( EIC) or ( MEIWC ) given details of the extent of the . installation covered by the certificate . together with a ( Record ) -Schedule of the Inspection & the ( Results ) - Schedule of testing . be issued the . “ Verification“ of the installation . New or Changes to an existing-installation - required by Chapter - 61 . The ( DEIC ) may be used . under appropriate-conditions . as an alternative to the ( EIC )
Where minor-electrical-installation-work .does not include the provision of a new-circuit . Only for the purposes of BS-7671: a minor-electrical-installation-works-certificate may be issued for ( Each-circuit ) towhich an . alteration is made . insteadof an ( EIC ) of ( DEIC ) - 631.3
Facts. 2394: Itcannot be predicted - where in the range a . Circuit-breaker will Trip . Not -RCBOs
Fault-current:
Prospective.
Themeaning of “ everyrelevant point “ Regulation - 434.1.
Whatis meant by the word . “ Every relevant point “ in - 434.1. that is the regulation requiresthe ( PFC ) at every-relevant-point of the installation - to be determined
Quite-simply “ Everyrelevant point “ means
Every-point where . for reasons of confirming-compliancewith . One or More of the requirements of . BS-7671:2011: it is necessary to determine the ( PFC )
434.1. Determination of ( PFC )
The prospective-fault-current . shall bedetermined at every-relevant-point of the installation . this shall be done by .Calculation . Measurement . or Enquiry .
Forthe installation . suppose it is being checked whether the .rated-short-circuit-breaking-capacity of each . fault-current-protective-device . is at least-equal to the . prospective-short-circuit . or prospective-earth-fault-current at the point where the device is installed . Regulation - 434.5.1. requires each-device to have sucha breaking-capacity . except where appropriate back-up-protection is provided by another device or devices . on the supply-side .
Typesof fault-condition .
Thereare . two-basic types offault-conditions .
A- Short-circuit . this is any fault between live-conductors . that is Three-line . Line-to-Line. Line-to-neutral .
An- Earth-fault . this is a fault between a Line-conductor & an . exposed-conductive-part or the protective-conductor of the circuit .
Resistance & Inductive reactance-values for cable(s) ….. ( r ) & ( x )
Live-conductor(s)
Exceptfor fault-loop . where the impedance is manly due to largesingle-core-cables in flat-formation .values of résistance & inductive reactance for live conductors of most types of cables in common use can be obtained from voltage-drop-tables . in appendix 4 . Values of inductive reactance can also be calculated where . necessary.
Thevalues of ( r ) & ( x ) in tables in appendix - 4. correspond to résistance & inductive reactance . respectively in units of ( mV/A/m ) the equivalent of . milliohms-per-metre . for conductorssizes of up to 16mm[SUP]2[/SUP]. separate-values of ( r) & ( x ) are not given in the tables . because the . inductive-reactancefor such sizes of conductor is negligible compared with the . résistance & may beignored . the single-value of ( mV/A/m ) for conductor-size of up to 16mm[SUP]2 [/SUP] should be taken as the value of ( r )
Inorder to be used in . calculations of .prospective-fault-current . the tabulated-values of ( r) & ( x ) have to be divided by ( 2 ) inthe case of . two-core-cables . &for two-single-core-cables . used for single-phase . & by ( √3 ) in the case three-core . & four-core-cables . & for three or four-single-core-cables . usedfor three-phase .
Togive values of résistance & inductive reactance for a conductor . of a given-length the . ( r ) & ( x ) values - duly-divided by ( 2) or ( √3 ) as applicable . are divided by . 1000 . so as to give the .answer in Ohms rather than . milliohms .& multiplied by the conductor-length in metres .
Consider. a single-phase . circuit consisting of a . 30metre-run of two - 50mm[SUP]2[/SUP]. thermoplastic - ( PVC ) insulated-copper-cables . installed in trunking - reference - method . B
The- tabulated-value of ( r ) & ( x ) given in column . 3 of table -4D1B . appendix - 4
( r) = 0.95 . mV/A/m .
(x ) = 0.30. mV/A/m .
The value of résistance ( r ) foreither the line-conductor . orneutral-conductor is therefore given .by ( R = 0.95 x 30 ------- 2 x 1000 = 0.0143Ω )
Similarly. the value of . inductive reactance ( x ) foreither the . line-conductor . or neutral-conductor is given by . ( X = 0.3 x 30 ------ 2 x 1000 = 0.0045Ω )
I stop there .
2394:This is Only a Learning-curve . taken form - Old / Note . 16[SUP]th[/SUP] Edition / tweaked to 17[SUP]th[/SUP] Edition . [ Getting my way around - O.S.G. ] :svengo:
• Two- 25mm[SUP]2[/SUP] single-core ( PVC ) insulated-cables - copper-conductor(s) are drawninto . ( PVC - conduit ) along with a 10mm[SUP]2 [/SUP]protective-conductor to feed a 230V - industrial - heater .
Thefollowing details are RELEVANT .
Protective-device:- protection atthe Origin by - 80A BS-88 fuses .
Thetested-value of ( Ze ) at the cables-Origin is - 0.35Ω .
Thelength of cables-run is 55m .
(a) Establish the :
i) . value of . ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) of the cables .
ii). prospective-earth-fault-loop-impedance ( Ief )
iii). the disconnection-time of the fuse .
(b). does the clearance-time comply with - BS-7671:
(a) - (i) Using the - O.S.G.
FromTable - 11 . ( R[SUP]1[/SUP] + R[SUP]2[/SUP]) for 25mm[SUP]2[/SUP] / 10mm[SUP]2 [/SUP]cables ( Colum -8 ) = 2.557 .
FromTable - 13 . apply the factor . 1.20. 70°C
Thus- ( R[SUP]1[/SUP] + R[SUP]2[/SUP]) = 55m x 2.557 x 1.20 ÷ 1000 = 1.68762 . rounded up to = 0.169Ω .
So- ( Zs ) at distribution-board = 0.35Ω + 0.169Ω = 0.519Ω .
ii). Prospective-earth-fault-current - ( Ief ) = 230 ÷ 0.519Ω = 443A .
iii). & (b) amleaving out .
O.S.G.- Table - 11 / 12 / 13 .
Multipliersto be applied to Table 11 . to calculate conductors-résistance at maximum-operating-temperature ( note - 3 ) for standard-devices ( note - 4 )
Table- 12 . Ambient-temperature .multiplier to Table - 11 .
O.S.G.- simplifies . “ Genetic “ Protective-devices . Fuses . Circuit-breaker - BS-EN-60898 . BS-3871-1 . part/ 1 ◄ . Wording
► Point to Note : Incorporated in acable or bunched - note - 2 . ( Cf 1.20 ) see Table - 54.3 . BS-7671:2011: which applies where the .protective-conductor is a . core in a cable or is bunched with cables .
(note - 3 ) The multipliers given in Table - 13 . for bothcopper & aluminium-conductors arebased on a [ simplification of the formula given in . BS-EN-60228 . namely that the . résistance- temperature - coefficient is . 0.004per °C at 20°C ]
(note - 4 ) Standard-devices are these described in appendix - 3 . of BS-7671:2011:
2394:simplified : O.S.G. - Table - A2
A2- from the O.S.G. to apply-diversity-factors . we can find the . Assumed-current.
“ Shower “ No-diversity .row - (5) 10.000 : 10000 ÷ 230V = 43.47A . rounded up to . 45A -circuit-breaker .
Because it does not say “ Shower “ people do get confused .
Settingthe record / Straight . A2 / (5) Water-heater. ( Instantaneous - type . “ Shower “ ) power-circuit .
Cooker- (3) of table .
12.000 - 12000W ÷ 230V = 52A. ( fL ) full-load . you are going to applying diversity
First 10A off . 52A is 42A
Table- A2 . Colum - (3) Cooking-appliances .
O.S.G.simplifies . Individual-household-installation .
First - 10A & 30% of remainder . [ 42 x 30% = 12.6A ] for your calculator . 42 x 0.3 = 12.6A.
First - 10A
30% ofremainder = 12.6A .
Total of : 10A + 12.6 = 22.6A .
10A + 30% ( fl ) full-load . ofconnected-cooking-appliances inexcess of . 10A + ( 5A ) ◄► if a socket-outlet is incorporated in the control-unit .
Total of : 10A + 12 = 22A . 22A + 5A = 27A.
2394:simplified : O.S.G. - Table - A2
A2- from the O.S.G. to apply-diversity-factors . we can find the . Assumed-current.
“ Shower “ No-diversity .row - (5) 10.000 : 10000 ÷ 230V = 43.47A . rounded up to . 45A -circuit-breaker .
Because it does not say “ Shower “ people do get confused .
Settingthe record / Straight . A2 / (5) Water-heater. ( Instantaneous - type . “ Shower “ ) power-circuit .
Hi there Amberleaf,
Your posts are very helpful and good reminders, thanks.
I imagine you must be a lecturer yourself.
BUT, please use a spell checker and for clarity I would recommend "Times Roman" font.
Also when using words have a space between them, spell checker will show them up.
ie, such as above (
Settingthe).
Then, as I have seen earlier an opportunity to download your complete synopsis would be gratefully received, no doubt by all your readers.
Thanks once again.
Table- A2 . Lighting : row (1) Individual-household .
2000W ÷ 230V = 8.69 x 66% = 5.73A . [ for your calculator 8.69 x 0.66 = 5.73A ]
66% oftotal-current-demand .
Rugbyspark . Thank you .
When I send anything down into the forum . its normal from my computer . sorry about theclosing up of words . its sincethe forum changed over . ??
Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
thanks for the confirmation this is what i thought.
i cant think of what use this device is .
i have seen David Saverys Arc Fault Detection Device...
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...