Basics . 2394:
411.3.1.2. - Equipotential-bonding : (Making me Equal ) - “ Protective “
In each installation . main-protective-equipotential-bonding-conductor should be connected to themain-earthing-terminal for all .Extraneous-conductive-parts to create an( Equipotential-Zone ) being Metal - can make me a Conductive-part. under a fault-condition ( If ) it’s aProtective-Measure
- Water-installation-pipes . copper
- Gas-installation-pipes . copper
542.4. - ( MET ) main-earthing-terminals or ( bars )
542.4.1. - in every installation a ( MET ) shall be provided to connect the following to the (Earthing-conductor )
- Circuit-protective-conductor
( CPC - T&E) 2394: ( PE ) protective-earth . making me an . protective-conductor
- Protective-bonding-conductor(s)
Main-protective-bonding-conductor. Supplementary-protective-bonding-conductor . when required .
- Functional-earthing-conductor- if required . RCBO .
2394: the one you need is . Regulation - 544.1.2. Main-equipotential-bonding-connection to any Gas . & Water . or other services
Do not mix up Circuit-breaker-side & RCD-side - to BS-EN-61009-1
Maximum-earth-fault-loop-impedance : Table - 41.3.
The Circuit-breakerside . BS-EN-61009-1 Overcurrent .32A - 1.44Ω .
Maximum-demand is one of the . general-characteristics of aninstallation . that part - 3 of BS-7671:2008:2011: requires to be Assessed .
2394: from your point . Your assessing the .Maximum-demand for an installation of an - Individual-domestic-dwelling .
Maximum-demand - Regulation- 311.1.
Basics: To assess . maximum-demand - sufficient information is needed about the connected-load .
- Howthe Installation is likely to be used . &any allowance for . diversity that maybe applied .
( † ) it isimportant to ensure that your . consumer-unit are of sufficient-rating to take the total-load-connected to them without the application of any diversity .
Table- A2 ( * & † ) ◄ pointto note .
p..111 . O.S.G. - Allowance for diversity . Only be a guide . nominal-voltage 230V - rated-current-capacity 100A . Single-phase .
Question. you Maximum-demand of the installation is to be calculated . O.S.G. A2 . is tell us your - demand-factors
Allowance for diversity to be applied to an:
- Individual-household-installation . including Individual-dwellings of ablock . 2394 : - 100A .
- Small-shops. stores . offices & business-premises .
-Small-hotels . boarding-houses . guest-houses . etc .
(5)- Water-heater (( Instantaneous-type )) turn to . p.112 . ( * & † )
( * ) in contextan Instantaneous-water-heater . is considered to be a water-heater of anyloading which . heats-water-only while the tap is turned on & thereforeuses-electricity-intermittently .
- Individual-household-installation .
(9)- standard-arrangement of final-circuits . 100% of current demand of largest-point . which in our case - ( 100% is 32A )
40% of currentdemand of every-other-circuit .
(5) - Water-heater. (( Instantaneous-type * )) including-electric-shower-heaters . sometimesknown as - power-circuits . 100% . fl.of largest appliance
2394: plain-english - when you are designing an Installation it always means that . diversity must be taken into account . %
This is a Scenario Only . “ Please-read carefully “ You do Not use this Method ◄◄
To comply with . Regulation - 553.1.7. an adequate number of suitably-positioned socket-outlets areneeded for . mobile-equipment . without allowing for diversity a circuit having - ( ?? ) sixteen 13A socket-outlets. would have a potential-load of approximately - ( 208A ) This is unrealistically-large & exceededthe rated-current-capacity of the supply-providing . ( Your 100A )
To bring it back into line : 2394: So the load on the . socket-outlets-circuit(s) of a (Your Dwelling / Installation ) does NOT- depend on the numberof socket-outlets ( BUT ) on the particular-items of current-using-equipment . connected to them . twenty - 13A socket-outlets . simultaneously in use. ( diversity not all use at the sametime ) Conventional- 13A final-circuit(s)
Usefuljunk . BS-EN-61009-1 .
RCBOs- this devices are functionally-dependent on the . Line-voltage for thepurposes of detection & evaluation of leakage-current . & of interruption of the supply .
The product-standard for these . voltage-dependent-device therefore requires them to trip .automatically if the supply to the [ Electronic-circuit-fails ] otherwise this would prevent their operation in the . event of an Earth-fault . This
is particularly-important in the case of a . loss of Neutral. which would otherwise leave a potential of . 230V at the Load .
facts : This automatic “ Fail-safe “ trip feature is . afforded by the connection of the “ Devices “ Thin-white or cream-lead . to the[ Earthing-arrangement of the Installation ] the lead is often-referred to as . “ Functional-earth-lead “
but ) its sole-purpose is to . provide a [ Second-reference-point ] for thesupply to the - Electronic-amplifier .
as soon as the supply . Neutral is lost . the RCD is forced to Trip . it isfor this reason . that the lead should . Not be Cut-off or .Left-unconnected .
2394: Trust-me . I’ve seen some daft thing in mydays .
[ Caution ] RCBOs
Inorder to prevent-damage to the [ Electronic-components ] & to avoid erroneous-test-results . Manufactures of [ Electronic-components-RCDs ] recommend that such devices . are disconnected whilst - ( IR ) Insulation-résistance-tests . are carried OUT . ◄◄
Finally Put to REST . At . [ 2/ IΔn]
However. !! . this explanation may be of help.
Familiar-currents of . - 0.5 x IΔn . - 1 x IΔn . - 5 x IΔn . as applicable . should be all that are needed when testingRCDs in the vast-majority of installations. as is the case under the . 16[SUP]th[/SUP] Edition .
[ 2/ IΔn ] test would be needed . only in .exceptional-circumstances . but evenwhere this is the case . it does not . necessarily meanthat an RCD - test-instrument having . a [ 2/ IΔn ] test-setting is required .
Therumour seems to have originated from . Note-2 . of table - 41.1 of the 17[SUP]th[/SUP]Edition . which gives . maximum-permitted-disconnection-times. for final-circuits rated at . up to [32A ] The note states that .
“ Where compliance with this . Regulation is provided by an RCD . the disconnection-time in accordance with Table - 41.1 . relate to . prospective-residual-fault-currents . significantly-higher than the rated-operating-current . of the RCD - Typically - [ 2/ IΔn ] However - Note - 2 DOES not MEAN that a [ 2/ IΔn ] testis required .
Seeif you’d remembered - Part- 6 . of BS-EN-61557
2394 : The basic-requirement of the 17[SUP]th[/SUP] Edition - 2011: [ for Testing RCDs ] with atest-instrument . which must comply with . - BS-EN-61557-6 is thatit must be . Verified that therelevant-requirements of Chapter-41 are met - Regulations - 612.8.1. & 612.10 refer .
Theserequirements ( Depend-on ) whichType-of-electric-shock-protection . the RCD is being used to provide ??? .
Provide “ What “ We have . two-methods .
i). RCD - is being used to provide [ Fault-protection ]
ii). RCD - is being used to provide [ Addition-protection ]
i) . for an RCD - being used for [ Fault-protection ] it ( Must - be - verified ) bytest that the . device would operate within the .relevant-maximum-disconnection-time permitted by the 17[SUP]th[/SUP]Edition - 2011: if an . Earth-fault-occurred. in the circuit-protected by the device .
2394: the maximum-disconnection-time permittedby - 17[SUP]th[/SUP] Edition - for A.C. circuits of nominal-voltage ( Uo -230V to earth ) are . 0.2s . 0.4s . 1s . & 5s .
inour-case here . 2394 : [ 0.4s being the most common in TN- systems . and 0.2s in TT- systems ]
Table- 3A - Time / current performance -criteria for RCDs to BS-EN-61008-1 & BS-EN-61009-1 . p.295 .
givesthe . Maximum-tripping-times for most-commonly-used-types of RCD . atresidual-current of . [ 1 x IΔn. and 5 x IΔn ] asspecified in the relevant British-Standards . 2011:
Table- 3A - it can readily be appreciated from the Table . thatwhen [ Verifying] the operation of the RCDs . listed inthis table within disconnection-times of [ 0.2s- 0.4s . 1s or 5s ] either a - 1 -IΔn test or a 5 x IΔn ] test is always suitable .
1/IΔn test is suitable for . verifying theoperation of . [ Keep in mind here . am starting with . BS- ] ONLY .
BS-4293 - or BS-7288 .Non-delay RCD . within a disconnection-time of . [ 0.2s ]
Any- Non-delay RCD .referred to in the Table - 3A . within a disconnection-time of [ 0.4s ] or 1s or 5s .
5 / IΔn . testis suitable for verifying the operation of - Any-delay-type RCD .referred to table - 3A . within a disconnection-time of 1s or 5s .
BS-EN-61008-1: or BS-EN-61009-1: non-delay RCD . within adisconnection-time of [ 0.2s ]
Not for - 2394 :
Experienced-electricians. [ 2/ IΔn ] test would be . necessary [ Only ] in . exceptional-circumstances of . [ 1/IΔn ] may legitimately not be enough to trip an RCD .within the maximum-disconnection-time permitted by BS-7671: such as where a BS-EN- 61008-1 RCD isused in a circuit where adisconnection-time not exceeding [ 0.2s is required ] but the test -instrument will perform a [ 5 / IΔn ] test for the particular rating of RCD-concerned . some RCD test-instruments will only perform a [ 5 / IΔn ] test for RCDs of rated-residual-operating-current [ IΔn ] 30mA or less .
Wherethis is the case . sufficient-test-current to trip the RCD within the required-time may be obtained by setting the test-instrument to suit an RCD of ahigher-rated-residual-operating-current . than the RCD being-tested .
Example- if a 100mA - BS-EN-61008-1 .non-delay RCD was being tested to . verify operation within [ 0.2s ] thetest-instrument could be set to test - 300mA RCD at a current of . 1 / IΔn . this would be [ Equivalent ] to testing the 100mA - RCD . at three-times its rated-residual-operating-current [ 3 / IΔn ] as can be deduced from the Table - 3A . a test-current of [ 3 / IΔn ] would be suitable to [ Verify - operation ] of the device within [ 0.2s ] as this current-exceeds [ 2 / IΔn] the current that BS-EN-61008-1 requires to cause operation within a maximum of [ 0.15s ]
ii ) . 2394 : back to basic. An RCD used for . [ Addition-protection ] musthave a rated-residual-operating-current [ IΔn ] not exceeding - 30mA & an operating-time not exceeding [ 40mS ] at a residual-current of [ 5 x IΔn] Regulation - 415.1.1. refer .
Test-procedure was used in the 16[SUP]th[/SUP] Edition . now- 17[SUP]th[/SUP]Edition . for RCDs used for this purpose is . therefore still applicable - [ 0.5non-trip . Test followed by 1x . x 5 .
2394: just a reminder . 0.5 - ½ . x IΔn . Test should also be carried out . to check for .unwanted-tripping .
2394:Initial-verification . ( T ) -&-s
134.2.1. During erection & on completion ofan installation . or an addition or alteration to an installation . & before it is put into service . appropriate . inspection & testing shall be carried out by .competent-persons to verify that the requirements of this . Standard have been met .
Appropriate-certification. shall be issued in accordance with . Section - 631 & 632 - Initial-verification.
632.4. ( T ) -&-s
Defects or Omissions revealed during . inspection &testing of the installation work covered by the . Certificate shall be made good before the Certificate is issued .
GN-3. just an Example .
Inspection& Testing . explains that . among other things . the purpose of periodic-inspection & testing is to provide .so far as is reasonably-practicable . for the identification of installation - defects & non-compliance withthe requirements of the Regulations -BS-7671: whichmay give rise to danger .
Useful-junk.
Statutory-requirements. “ Socket-outlets “
Exceptin Scotland . There are no-statutory-requirements in the United-Kingdom regarding the “ Minimum-number “ of socket-outlets to be provided in a dwelling .
Exceptin Scotland - 1990 - Part Q .
O.S.G.- P.178 . Table - H7 . Gives - recommendations on the . [ Minimum-provision ] Twin-socket-outlets to be provided in homes .
O.S.G.- A2 . Small-business-premise ..
Worked-example . Connected-loads . Diversity-factors . Calculation of Maximum-demand
Description- High-frequency discharge-lighting .
Number-ofpoints-served - 12 .
Connected-load. per-point . - 64 VA .
Total-connected-load of all points . 768 VA ÷ 230V = 3.34A .
Allowance for diversity - from Table - A2 - Type of premises !! . Small-business-premise . Etc . Lighting - 90% of the connected-lighting-load .
Resulting-contribution to maximum-installation-demand . - 3.00A
Worked-example . Connected-loads . Diversity-factors . Calculation of Maximum-demand
Description- Instantaneous-water-heater .
Number-ofpoints-served - 1 .
Connected-load. per-point . - 2.5 kW .
Total-connected-load of all points . 2500W ÷ 230V = 10.87A .
Allowance for diversity - from Table - A2 - Type of premises !! . Small-business-premise . Etc . 100% - Fl . of largest plus 100% -Fl . of 2[SUP]nd[/SUP] largest - appliance plus 25% Fl . of remaining -appliances .
Resulting-contribution to maximum-installation-demand . - 10.87A
100%- Fl . Number-of points-served - 1 . 2.5kW . 2.500W ÷ 230V= 10.87A
100%- Fl . Number-of points-served - 2 . 2.5kW . 2.500W ÷ 230V= 10.87A
(FL ) denotes full-load .
Whatis Overload-current .
Interms of the definitions given in .Part - 2 .
- Overload-current is . An overcurrent-occurring in a circuit which is . electrical-sound “
And.
Overcurrent - which is mentioned in the definition of overload-current . is . “ Acurrent exceeding the rated-value . forconductors the rated-value is the . Current-Carrying-Capacity “
Itshould be noted - that the term “ Overcurrent “ includes both . Overload-current and Fault-current.
Circuit-breakers - BS-EN-60898 . some facts .
Where- BS-EN-60898 . circuit-breaker is to provide . Overload-current-protection .the requirements - Regulation - 433.1.1. condition (iii) are to be complied with . the current ( I [SUP]2 [/SUP]) causing the effective-operation of the protective-device . is not to exceed ( 1.45 - times ) the lowest current-carrying-capacities ( Iz ) of any of the conductors of the circuit .
BS-EN-60898- circuit-breakers have aconventional-tripping-time ( I[SUP] t [/SUP] ) which is equal to ( 1.45 / In ) . This means that the current ( I [SUP]2 [/SUP]) causing the effective-operation of the circuit-breaker is . ( 1.45 - times ) the nominal-current or current-setting ( In ) of the BS-EN-60898 . The term “ conventional-tripping-current “ meansthe same term “ current ensuring effective-operation ofthe protective-device “ whichis used in . Regulation - 433.1.1.
Therefore. where nominal-current or current-setting of a BS-EN-60898. circuit-breaker is selected such that - Regulation - 433.1.1. condition ( ii ) is met . then condition ( iii ) of the Regulation . will also be met . This is confirmed by Regulation - 433.1.100 .
Short-circuit-capacity:
A circuit-breakerconforming to BS-EN-60898 . which hastwo-defined . short-circuit-breaking-capacities ( Ultimate & Service )
Miniature-circuit-breaker- conforming to . BS-3871 . Part - 1. has only one . short-circuit-capacity . designated as its. “ Category of duty “ thisis marked on the device .
2394: If in doubt the O.S.G. will simplify , p.151.
Fundamentally. Two-types of form are recognisedby. BS-7671 .
- Certificate are issued for . New-installation-work . Q) . whatwould I be . - ( EIC ) Electrical-installation-certificate .
-Reports are issued for . inspections of Existing-installations . Q) . whatwould I be . -( EICR ) Electrical-installation-condition-certificate.
G2- Certification : Watch your . Wording . in Exams
Two-types of certificate for . ( New-work ◄ ) . are recognised by. BS-7671 .
Q). what would I be . ( New-work ◄ ) - ( EIC) Electrical-installation-certificate.
Q). what would I be . ( New-work ◄ ) - ( MEIWC ) Minor-electrical-installation-work-certificate .
(EIC ) Electrical-installation-certificate. is “ Safety-certificate “ :aureola:
2394: learning-curve . what is Testing & Inspection . all about .
( Private-landlords) I’ve waited 5-years before anything was done .
Soyou can see I think there money crabbing **** .
That’swhy I’ll fight all the way . on this . matter .
The landlord . sent round . a ( Plummer ) to check my Electrics . AM - PART-P . Qualified . I politely told him to get the hell out the House . :6:
I issuedan Certificate . with major-faults on it 3/half years ago . (Dusty-bin got it )
I’ll kill two-birds’ with one stone here .
Firstly: 27/9/12 . N***** - Inspector . because it is an Exiting-installation .he used an . Domestic-electrical-installation-condition-report .
Time on site . 3/half hours . because of . ( LIM ) limitations ◄ . this will --- up on your Exams Etc .
12- faults . 8 - CI . 4 - C2 . Unsatisfactory . oneor more issues of safety have been identified .
O.S.G. - p. 152 . will simplify .
Unsatisfactory . oneor more issues of safety have been identified .
Where an unsatisfactory . result has been recorded . C1 and / orC2 - observations will have beenincluded indentifying the reason(s) for the result . Once the report has been issued by the ( Inspector ) the ( Onus is then placedon the Client to Act ) in responseto the ( Observation - recorded)
C1 - Danger-present . Risk of injury . Immediate remedial-action required .
C2 - Potential-dangerous- Urgent . remedial-action required .
C1 - Where danger currently-exists . & an immediate-issue of safety is apparent .
C2 - Not immediately-dangerous but a . dangerous-condition could occur due to a fault .
p.153. G3.3 - Dangerous-situation . ( learning-curve )
The Inspector is advised to exercise-judgement to secure the area & inform the ( Client . **** ) immediately . followed up inwriting . Once permission has been obtained . the danger should be removed .
Exercise-Judgement whichthe Inspector . did . - Hecould shut down the problems . without . turning of 4 - circuit-breakers . ( I only have 6 - way )
Judgment- day tomorrow . ( Will make eye contact )
2394: It’s all in the books . ( Addition or Alteration ) ◄► ( Existing-circuit ) Not a New-circuit . “ it’s all in the Wording “
(MEIWC ) Minor-electrical-installation-work-certificate. Regulations. GN-3 .
O.S.G.p.151. simplified .
The Minor-electrical-installation-work-certificate. is intended to be issued where more significant-installation-work. is undertaken .
- Adding lights to a . lighting-circuit .
- Adding socket-outlets to a ring-final-circuit.
- Rerouting an ( Existing-circuit)
-Replacing an ( Existing-shower ) with alarger-power-rating of unit . PS. You have to check the size of cable . is it . 6.0mm[SUP]2 [/SUP] / 10.00mm[SUP]2 [/SUP]
-Replacing circuit-breaker(s) with . RCBOs where there is a difference of . Overcurrent-type . ( replacing - characteristics type C or B )
in each case . the characteristics. of the circuit are likely to have been altered . whether it’s the . ( addition ) ofextra-load or changes to the original . earth-fault-loop-impedance.
Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
thanks for the confirmation this is what i thought.
i cant think of what use this device is .
i have seen David Saverys Arc Fault Detection Device...
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...