Must thank my learned colleague tazz , guiding me on the right path . Part - 1 & Part - 6 , Thank mate

Using the building , for a dwelling , the design may result in either a system of smoke & heat alarms or a more complex system such as . a
BS-5839-1 Grade A which may be found in a large dwelling or a house in multiple occupation

The design of the system can ( Either ) meet the requirements of BS-5839-1 ; BS-5839-6 or for a new or materially altered dwelling . Approved Document B .

Smoke alarms own RCBOs
Re-wired a shop , with two flats above the shop premises . The flat(s) have each 1 Heat , 1 Ionisation , 1 Optical
5 detectors . Heat , Ionisation , Optical . large shop .

Fire & Safety Services . was working of ( BS-5839 part 6 )
Fire Inspector . was doing his rounds in the shop . happy about the (( Detectors to BS-5839-6 )) as he said this is the , Minimum protection ( LD3 )

Fire Inspector . ask for two remote sounder from the shop to the flats upstairs ( individual )

haven't done this before , the old brain was on overdrive here . Fire Inspector looked through the flats and said no fire doors , normal doors ,

BS-5839-6 recommends achieving a sound level of 75 dB(A) at the bedhead. It also recommends more than 85 dB(A) at the doorway of each bedroom where doors exceed 20 dB ..." unless there is a sounder in the bedroom ". As domestic smoke alarms usually generate 85 dB(A), neither of these levels can be achieved in most situations and a bedroom alarm or sounder is justified. Also, research has shown that young children can sleep through loud alarms while elderly people and others with hearing impairments may also not respond.

after a talk with him Fire Inspector . he gave me some options .
• Yes you can use 3 core & E . depends on the circumstance . Part - 6 .
from my point of view . I have used ( FP - 200 ) after leaving the shop , 50/60 metres . on the grounds off identification .

from the Shop : if this was 3 - core & E . after the flats have been Isolated , to the layman would he know that there is a live cable in the attic ??
That's why I used this system ( FP - 200 ) and not 3 - core & E . grounds of Safety .

Now am a bit wiser about 75 dB(A) at the bedhead . The doors , The doors .
Yes . fire Inspector said install the remote sounder in the hall next to the bedroom door . ( No fire door ) I have decided to install the remote sounder in the bedroom . end of .

PS , I never got any paperwork with this . I have asked the fire Inspector for information on this matter Part - 6 . remote sounder 2013

► (( In the drawing , am only making you aware of the ( dB ) the doors . the doors )) ◄ something to work off .

In my case Part - 6 : ( LD3 ) BS-EN-14604:2005 , Ei141RC Ionisation , Ei144RC Heat , Ei146RC Optical & Aico EI167RC Remote Sounder
Remote Sounder. Mains powered. Interconnects with 2100, 160RC and 140 series alarms

Fire Inspector , was happy about the safety aspect of Electrical Safety . He backed me up on this .

PS the landlord was doing handstands
 
Which one of the following is not part of the requirements for fault protection : A) 411.3. 411.3.1. 411.3.1.1.

- Protective earthing .
- Protective equipotential bonding
- Automatic disconnection
- Protection by insulation of live parts

Protection against electric shock : Chapter 41.
410.3.3. The following protective measures generally are permitted :

(i) Automatic disconnection of supply ( Section 411 )
Note : In electrical installations the most commonly used protective measure is automatic disconnection of supply .

Section 411: Protective Measure : automatic disconnection of supply
 
Extracts : 2008:

Certificate of Design , Installation and Commissioning of a Fire Detection and Alarm system of Grade B , C , D , E , F in a dwelling

□ Details of the Client .
This section of the certificate needs no explanation require only that the client be indentified .

□ Details of the fire detection and alarm system .
This requires the address at which the system is installed to be stated . together with extent of the installed system and the identification of the status of the system in terms of " New or a Modification "

Commissioning
Additionally , the model and serial number of an instrument used for testing the ( sound level ) must be recorded in the space provided . An instrument complying with BS-EN-61672 , class 2 , with a slow response and " A " weighting is suitable for measuring the sound level .

it should be noted , however , that sound pressure tests may be unnecessary . The requirements of 85 dB(A) at the bedroom door , with the door open , will be deemed to have been met if a smoke alarm complying with BS-5466 is located within 3 m of the doorway .

In order to get accurate and repeatable measurements, it is essential that a sound level meter meets the relevant standards. Most measurement regulations will state the standards that should be met by the equipment.

Sound Level Meter Standards
To satisfy most regulations, new meters should meet the standard IEC 61672 (or the British Standard equivalent BS-EN-61672) to either Class 1 or Class 2. There are other standards for the Calibrator, for noise dose meters, personal sound exposure meters, octave band filters and so on. Here is a summary of the most important standards.

Standard : IEC 61672
Relates To : Sound Level Meters
Electro acoustics - Sound level meters
This is the most recent sound level meter standard and the one that modern measurement regulations will require.
Grades in order of accuracy: Class 1, Class 2

Standard : IEC 60651
Relates To : Sound Level Meters
Specification for Sound Level Meters
This standard has been superseded by IEC 61672. Older meters meeting this standard can still be used for many applications. Originally this standard was called IEC 651, but was renamed IEC 60651.
Grades in order of accuracy: Type 1, Type 2

Standard : IEC 60804
Relates To : Sound Level Meters
Integrating-Averaging Sound Level Meters
This standard has been superseded by IEC 61672. It was originally called IEC 804 but was renamed IEC 60804. It extends IEC 60651 and describes the performance of Integrating sound level meters.
 
2013 / 14
BS-5839 Parts 6 .

Detection & Alarm Systems .

Power supplies
1 ) The power supply for fire alarm system should be taken from the dwelling's mains electricity supply . The mains supply to the smoke alarm(s) should comprise :

a) a single independent circuit at the dwelling's main distribution board ( consumer unit ) :
or
b) a single regularly used local lighting circuit . ( This has the advantage that loss of supply will be rectified to restore the lighting )

Most installations in dwellings , carried out in accordance with the 17th Edition of the IET Wiring Regulations , will have a 30mA RCD ( residual current device ) or RCBO ( residual breaker with overcurrent protection ) protecting all circuits . in this circumstance it is arguably preferable for the supply for the fire alarm systems to be taken from a regularly used lighting circuit as operation of the RCD or RCBO will soon be known , ( for other than Grade d systems , BS-5839-6 recommends avoiding the use of RCDs on fire system circuits . This will usually require clipping cables direct to the surface or enclosing in steel conduit or the like )

The Approved Document requires a means of isolation for the smoke alarms so that they can be isolated with the dwellings lights on . This does not usually necessitate separate isolation facilities as most smoke alarms can be removed from their mounting plate ; this satisfies the recommendation for means for isolation .
 
Smoke alarms for landlords & agents

The Building Regulations (1991) state that all properties built since June 1992 must be fitted with mains operated interlinked smoke detectors/alarms with at least one detector per floor level. .. ( Regarding rented properties of any age )

2013 : Scope of Part P ( BR )

Part P applies to electrical installations in buildings or parts of buildings comprising :
i) dwelling houses and flats;
ii) dwelling and business premises that have a common metered supply - for example shops and public houses with a flat above with a common meter ;
 
Carbon monoxide fire detectors ( Clauses 10.1.4 & 10.2 )

Carbon monoxide fire detectors can be immune to certain environmental influences that can cause false alarms in other detectors such as dust , steam and cigarette smoke , whilst responding to most types of fire appreciably faster than most heat detectors .

Note : The 2013 version of BS-5839-6 advises :
e) Carbon monoxide fire detectors , or multi-sensor detectors incorporating a carbon monoxide sensor , should not be used within dwellings , unless :

i) the detectors are incorporated within a Grade A , B or C, system and there is a high likelihood that the system will be subject to periodic maintenance by a competent person at periods not exceeding 12 months ; or

ii) a fault warning is given to indicate the need to replace the electrochemical cell of the detector before it reaches the end of its anticipated life .

f) Subject to compliance with 10.2e ) above , carbon monoxide fire detectors may be installed within the circulation areas of a dwelling in conjunction with an equal number of optical smoke detectors .

g) Subject to compliance with 10.2e ) carbon monoxide fire detectors may be installed in any rooms within a dwelling , other than kitchens .

Note 5 : if , in any room of dwelling , a heat detector could provide adequate fire protection , a carbon monoxide detector may be used instead .
 
2013 .

Fire safety enforcing authority : The body responsible for enforcing the Fire Safety Order 2005 This is usually the fire & rescue authority .
Fire Safety Order : The Regulatory Reform ( Fire Safety ) order 2005 ( SI 2005 / 1541 , The Stationery Office Ltd )
Local authority : The local authority empowered to carry out the building control function and to enforce Building Regulations in their area by virtue of section 91(2) of the Building Act 1984 .
 
( BR ) 2013

Domestic installations

are within the compass of the Electricity at Work Regulations when persons are at work , i.e. employed to work in the premises , otherwise they are not . However , the same basic principles apply as are appropriate to places of work , in the maintenance of domestic installations would comprise .

a ) routine checks .
b) periodic inspection and , as necessary , testing .

in a user manual , a householder must be advised that as well as a professional periodic inspection and test at least every ten years , all defects must be repaired as they arise . if there are signs of wear , overheating , looseness , or difficulty in operating equipment then an electrician should be instructed to inspect the installation and maintain as necessary .
 
2013 : Fire detection & Alarm systems

Inspection , testing & certification
Inspection & testing

The fire alarm electrical installation must comply with Part P of the Building Regulations .
Test results may be included in the electrical installation certificate ( and schedules ) if carried out as part of the electrical installation ; otherwise a minor electrical installation certificate shall be completed ( for grade D systems ) In all cases after successful testing and commissioning , a fire system certificate for design , installation and commissioning must be completed and given to the person ordering the work .

2013 : ( BR ) Installation and commissioning certificate ( Grade D system )
The fire alarm installation is to be designed , installed and tested in accordance with BS-5839-6

Testing
The wiring of one fire alarm installation may be included in the Electrical Installation Certificate ( and schedules ) if carried out as part of the electrical installation ; otherwise a minor Electrical Installation Certificate shall be completed ( for Grade D systems ) In all cases after successful testing and commissioning , a fire system certificate for design , installation and commissioning must be completed and given to the person ordering the work .

Fire detection & Alarm systems
( BR )

Handover
Inspection , test and commissioning certificates ( and schedules ) manufacturer's instructions and necessary guidance are handed over to the person ordering the work .
 
( BR ) 2013

PME - supply ( TN-C-S system )
Based on 25mm[SUP]2[/SUP] tails and selection from Table 54.7. of BS-7671:

Notes :
1) An isolator is not always installed by the electricity distributor .. ( DNO )
2) Distribution will quote a ( Ze - 0.35Ω ) and a fault level of 16kA . A loop impedance of 0.35Ω equates to a fault level of , 230V ÷ 0.35Ω = 657A . 16kA is the worst-case short-circuit fault level and 0.35Ω the worst-case external earth-loop-impedance .
 
Kitchen is no longer identified in the Approved Document as being a special location .

( BR ) 2013
Location of accessories in kitchens .
General guidance can be provided as follows

i . Wiring accessories ( e.g. socket-outlets , switches ) should preferably be mounted on the building fabric and not on kitchen furniture .

Accessories and electrical equipment such as socket-outlets and under-cupboard lighting can be fixed to fitted kitchen units provided that they are securely fixed to rigid parts of the units that are not demountable or otherwise liable to be disturbed in normal service . Account should be made regarding accessibility for inspection , testing and maintenance , and provision of adequate protection against damage ( by impact or water for example )
for the accessories , equipment and associated wiring .

ii . Cooker control switches , extractor fan switches , etc should not be mounted so that it is necessary to lean or reach over gas or electric hobs for their operation .

iii . Socket-outlets should be installed a minimum of 450mm from the floor .

iv . Accessories should be installed a minimum of 300mm from the edge of kitchen sinks and draining boards to reduce the risk of being splashed .

v . Socket-outlets supplying washing machines and dishwashers , etc should be positioned so that water that may drip from plumbing or the equipment is unlikely to affect the socket-outlet or plug .

vi . To prevent damage to the plug and flexible cable on insertion and without the centre of a socket-outlet should be a minimum of 150mm above the work surface .

vii . Socket-outlets supplying appliances pushed under a work surface , e.g. dishwashers , tumble dryers and fridges , should be accessible when the appliance is pulled out .

viii . Appliances built into kitchen furniture ( integrated appliances ) should be connected to a socket-outlet or fused connection unit that is readily accessible when the appliance is in place and in normal use , or be supplied from a socket-outlet or other connecting device controlled by a readily accessible double-pole switch or switched fused connection unit .

ix . Light switches should be readily accessible .
x . Cooker hoods should be 650 to 700mm above the hob surface , subject to ( xi )
xi . Manufacturer's instructions should be followed .
 
( BR ) 2013

Extractor fans :
A suitable 230V extractor fan may be installed in zones 1 & 2 , and outside the zones . if an extractor fan is installed in zone 1 or 2 it must be protected against the ingress of moisture to at least IPX4 .

An extractor fan supplied from a lighting circuit for a bathroom without a window should have its own means of isolation . as otherwise replacement or maintenance of the fan would have to be carried out in the dark , An isolation switch for a fan with an overrun facility will need to be triple-pole ( switch-wire , Line and neutral ) and must be installed outside zones 0 , 1 , and 2 .
 
( BR ) 2013.
Switch wires in a new installation or an addition or alteration to an existing installation

Where a two-core cable with cores coloured brown and blue is used as switch-wires , both conductors being line-conductors , the blue-conductor must be marked brown or L at its terminations .

Intermediate and two-way switch wires in a new installation or an addition or alteration to an existing installation

Where a three-core cable with cores coloured brown , black and gray is used as switch-wires , all three-conductors being line-conductors , the black and gray-conductors must be marked brown or L at the terminations .
 
Cooker circuits in household or similar premises . ( BR 2013 )

Circuit specifications

A cooker circuit with cables in walls or partitions installed in earthed steel conduit or with an earthed metallic sheath does not require RCD protection unless the cooker control unit incorporates socket-outlet

The circuit should supply a control switch complying with BS-3676 or a cooker control unit complying with BS-41177.

The rating of the circuit is determined by the assessment of the current demand of the cooking appliance(s) and cooker control unit socket-outlet if any.
A 30 or 32A circuit is usually appropriate for household or similar cookers of rating up to 15kW.

A circuit of rating exceeding ( 15A ) but not exceeding ( 50A ) may supply two or more cooking appliances where these are installed in one room . it is recommended that a control switch or cooker control unit should be installed and placed within two metres of the appliance , but not directly above it . Where two stationary cooking appliances are installed in one room , one switch may be used to control both appliances provided that neither appliance is more than two metres from the switch .

it is recommended that electric ovens are supplied by a separate circuit ; however , for lightly loaded circuits , ovens of rating ( 13A ) or less may be connected into a ring final circuit .

Precautions need to be taken to prevent the heat generated by a cooker , including the hob , creating a risk of fire , or of harmful thermal effects , to adjacent equipment or materials including furnishings , e.g. curtains .
 
Reg / P 278

BS-4177:1992 , Specification for Cooker vcontrol units . Table 53.4.

A cooker switch complying with BS-3676 or a cooker control unit complying with BS-4177 ( a cooker switch incorporating a socket-outlet ) is usually installed where a cooking appliance is to be connected other than by means of a plug and socket-outlet.

BS-3676 :
Switches for household and similar fixed electrcal installations .
Specification for general requirements . Now replaced by BS-EN-60669-1 , 2000 , but remains current , 2000 is dual nimbered BS-3676:2000
 
Traditional Junction boxes .. ( Acceptable for locations which are accessible )

As standard ( junction boxes ) have no cable clamps this means the box must be screwed-down and the cables fixed to prevent strain on the connections.
- cables fixed to prevent strain .. ( Cable Clips )
 
Wago - 2014:

Thank you for contacting us with your enquiry.

The most recent requirements of BS5733 for a maintenance free accessory extend to the terminals, the enclosure and most importantly the performance of the enclosure with the terminals. The Wago 773 and 222 range of connectors have undergone the testing required for the standard along with the ipcc-1 Wagobox enclosure. The junction box and terminals when used together and installed following the MF instructions meet the BS5733 MF requirement. The ( MF ) mark is therefore placed on the junction box not on the terminals. The MF BS 5733 markings are all on the underside of the lid and also include information about the parameters for the cable clamp strain relief in the enclosure, current ratings for the connectors and maximum aggregate current information for the accessory in a MF situation. This information is also provided in our instruction leaflet. Further information is available on the support page of our website.

At the time of our MF testing we undertook even more vigorous testing on areas such as vibration to future proof the junction box system in the event of any changes to the requirements. At this time we are not aware of anything in the new third amendment due next year which should affect your ability to use the Wagobox in its present form for MF applications.
 
( BR ) 2013:

Outcome (Observation & Recommendations)

The condition Report form in BS-7671: includes notes for guidance. Within Section ( K )
Observations . each observation is required to be allocated a classification code as follows :

C1 - danger present – Risk of injury . Immediate remedial action required .
C2 - Potentially dangerous – urgent remedial action required .
C3 - Improvement recommended .

The electrician carrying out the inspection & test is required to provide an overall assessment as to whether the installation is satisfactory or unsatisfactory .

C1 . Immediate remedial action required
• Broken equipment where live-parts are exposed
• Conductive parts live ( the result of a fault )
• Incorrect polarity

C2 . Potentially dangerous – urgent remedial action required
• No means of earthing at origin
• RCD installed for fault protection (e.g. in a TT installation) that does not operate when test button is pressed
• No circuit protective conductor in one or more lighting circuits with Class 1 light-fitting ( Class 1 light-fitting must be earthed )
• A borrowed neutral ( two-circuits using the same neutral )
• A socket-outlet with no earth-connection

C3 - Improvement recommended
• No 30mA RCD protection to socket-circuit
• No supplementary bonding in bathroom where it is required .
• No circuit-protective conductor in one or more lighting circuit with Class II light-fitting ( Class II light-fittings do not require to be earthed but may be changed to Class 1 )
• Use of water-pipe as a means of earthing
 
( BR ) 2013

A ring or radial socket-outlet final circuit , with spurs and permanently connected equipment , if any , may supply an unlimited number of socket-outlets and fused connection units

Socket-outlets for washing machines , tumble dryers and dishwashers should be located so as to provide reasonable sharing of the load in each leg of the ring .

Where two or more ring final circuits are installed , the socket-outlets and permanently connected equipment to be served are to be reasonably distributed among the circuits .

Spurs
A non-fused spur is wired in the same size ( cross-sectional area ) cable as the ring final circuit . A fused spur is connected to the circuit through a fused connection unit , the rating of the fuse in the unit not exceeding that of the cable forming the spur and , in any event , not exceeding 13A

Supplementary bonding in kitchens
There is no specific requirement in BS-7671 to provide ( Supplementary bonding in kitchens ) Water pipes , metal sinks or draining boards and metal furniture do not require ( Supplementary bonding )

- ( ESC )
Kitchen Safety , If appliances such as fridges, dishwashers and washing machines are fitted under worktops, getting to sockets may be difficult. Ideally, these appliances should be controlled by a switched fuse-connection unit mounted above the worktop where you can reach it easily.

- BS-7671:2011: Appendix 15 .
Fused connection unit ( FCU ) to BS-1363-4 … maximum fuse 13A

Junction box to BS-EN-60670-22
Junction boxes with screw terminals must be accessible for inspection , testing & maintenance or alternatively , use maintenance-free terminals / connections ( Regulation 526.3. )

R/P 285 : BS-EN-60670-22: 2006
Particular requirements for connecting boxes and enclosures .. 521.8.3. Appx 15 Fig 15A

Installations designed from 1st July 2008 must comply with this new set of Regulations.
There are regulations concerning the connection of conductors relating to lighting and power final circuits

This is further reinforced in Appendix 15 of the Wiring Regulations which states “ Junction boxes with screw terminals must be accessible for inspection, testing & maintenance or, alternatively, use maintenance-free terminals / connection (Regulation 526.3)

“ Junction boxes with screw terminals must be accessible for inspection ... ”
( Providing the enclosure is fixed and accessible traditional junction boxes are acceptable )

“ Maintenance free terminals provide a solution where accessibility is an issue ”

• Ancient colours
Installations with plain green sleeving on the earth wires will typically be approaching 40 years old and are likely to require replacement.

R/P 115 . 2011:
514.4.5. The single colour green shall not be used .

Identification of protective conductors
The first sentence of Regulation 514.4.2 is conclusive and leaves no room for doubt. It reads, ‘ The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor and this combination shall not be used for any other purpose ’.
 
Split-load . ( CCU ) Etc. .

Schedule of Test Results

RCD 1
Light up . .. BS-EN-60898-1
Sockets down .. BS-EN-60898-1
Cooker .. BS-EN-60898-1

RCD 2
Light down .. BS-EN-60898-1
Sockets up .. BS-EN-60898-1
Shower .. BS-EN-60898-1

Generic Schedule of Test Results
Circuit number , for three-phase installations it is preferred to use the designation ( L1 . L2 , L3 ) so for example , for the 5[SUP]th[/SUP] circuit , the designation ( 5L1 , 5L2 , 5L3 )
 
( BR )
Before the supply is connected .
Polarity ( by continuity methods )

With the supply connected and energized
Re-check of polarity , using an approved voltage indicator
 
Continuity of ring final circuit conductors .
Three step test is required to verify the continuity of the Line , Neutral , & Protective-conductors

Step 1 .
The line , neutral and protective-conductors are identified at the distribution board or consumer unit and the end-to-end résistance of each is measured separately .

A finite reading confirms that there is no open circuit on the ring conductors under test .
The résistance values obtained should be the same ( within 0.05Ω ) Note if the conductors are all of the same size .

If the protective conductor has a reduced csa the résistance ( r2 ) of the protective conductor loop will be proportionally higher than that of the line and neutral loops e.g. 1.67 time for 2.5 / 1.5mm2 cable . ( 2.5 ÷ 1.5 = 1.67 )
 
(Dry meter) to (Card Meter)

This is another job, from the Fire & Safety Department & Local Council .. systems use at time ( LD3 )

(Watch Manager) 4/7/2014 .
Fire & Rescue Service . Fire Safety Department .

Day and time of a private landlord . Does greed come into play here ?
( Shop work ) with two individual flats above shop .

Landlord changed a , Dry meter to card-operated meter , just to make more money from the tenant ….. ( That’s when it when Pear Shape )

Fire Safety Officer , did a Safety check and found this problem . The card ran out , with no power in the Building . ( LD3 ) Alarms running of Battery only . no mains to Building . 14 hours on Battery only . The owner of the shop had complained to the land lord about loss of power to shop premises .

On one occasion the landlord when away for the weekend Fri / Monday . Emergency credit was only one pound .

Taken from Extracts from letter :
Electricians a better understanding . from your point of view

□ The electrical power supply that is feeding the fire alarm system in all the above premises is by a ( Card Meter ) and that a recent electrical power failure in the shop/s resulted in the alarm being powered by the ( battery alone for an unspecified time ) This is insufficient and is totally unacceptable to have the fire alarm on a card-operated meter or similar set up .

BS-5839 part 6 grades fire detection and alarm systems for premises according to the (Complexity of the system) for the purpose of specifying fire detection and alarm systems and the associated engineering design parameters there are ( Six Grades) ◄◄

Grades A to D are the most relevant to yourself and are all described below with regards there power supplies .

Please find below the excerpts for the relevant power supplies to BS-5839 part 6 fire alarm system. Depending on size layout , fire separation and number of rooms etc. , dictates what grade and level of fire alarm is acceptable for that premises .

15.2 : Recommendation’s for power supplies for Grade A system . ←
The following recommendations are applicable .
a) Power supplies for a Grade A systems should comply with the recommendations of Clause 25 of BS-5839-1:2002 . with the exception of 25.4e )

b) The circuit serving the fire detection and fire alarm system should be such that it is not isolated within the dwelling, except in event of deliberate isolation of the supply by the occupier ( e.g. by use of an isolating device complying with the recommendations of 25.2a ) of BS-5839-1:2002. Or in the event of fault conditions . I is not. For example , [[ It is not . acceptable for the main supply to be connected via a card-operated meter or similar ]]

c) The standby supply should be capable of automatically maintaining the system in normal operation ( whilst giving an audible and visual indication of mains failure ) for a period of 72h , after which sufficient capacity should remain to supply the maximum alarm load ( see 3.22 ) for at least 15 mim . However , if a dwelling is never left unattended ( e.g. a mansion in which staff are always present and can arrange for rectification of a supply failure ) the period of normal operation sustained by the standby supply may be reduced from 72 h to 24h .

Note 1 : it is not recommended that the standby period be reduced in dwellings on the grounds that an automatically started emergency generator is present .
Note 2 : T provide a battery that will operate a Grade A system for 72h in the event of mains failure will normally necessitate relatively larger batteries , which might need to be housed in a separate supply unit . Any external cabling between the power supply unit and the CIE needs to be duplicated for compliance with BS-5839-1 and needs to be fire-resisting .

15.3: Recommendation’s for power supplies for Grade B system . ←
The following recommendations are applicable .
a) The normal supply for a Grade B system should be derived from the public electricity supply , transformed or modified as necessary . The mains power should be supplied from an independent circuit at the dwelling’s main distribution board . No other electrical equipment should be connected to this circuit .

b) The mains supply to the fire detection and fire alarm system should be supplied, via an isolating protective device ( such as a circuit-breaker ) form the load ( dead ) side of the main isolating device for dwelling . The isolating protective device should be labelled “ Fire Alarm : Do Not Isolate

c) The circuit serving the fire detection and fire alarm system should be such that it is not isolated within the dwelling , except in the case of deliberate isolation of the supply by the occupier ( e.g. by use of an isolating device complying with the recommendations of 25.2a ) of BS-5839-1:2002. Or in the event of fault conditions , it is not , for example , [[ It is not . acceptable for the main supply to be connected via a card-operated meter or similar ]]

d) The circuit serving the fire detection and fire alarm system should preferably not be protected by any residual current device ( RCD ) if RCD protection is required for reasons of electrical safety ( e.g. in an installation forming part of a TT system ) either of the following conditions should be satisfied :

i) The RCD . should serve only the circuit supplying the fire detection and fire alarm system.
ii) The RCD protection of the fire detection and fire alarm system circuit should operate independently of any RCD protection for circuit supplying socket-outlets or portable equipment .

Note : for example , 15.3d ii ) would be satisfied if , say , a time delayed 100mA RCD . served the entire electrical installation in 15.5 Recommendation’s for power supplies for Grade D system . ←

e) The mains supply should be backed up by a standby supply , comprising a secondary battery with an automatic charger , that is capable of automatically maintaining the system in normal operation ( whilst giving an audible and visual indication of mains failure ) for a period of 72h , after which sufficient .

capacity should remain to support the maximum alarm load ( see 3.22 ) for 15 min .

f) The normal and standby supplies should each be capable of supplying the maximum alarm load irrespective of the condition of the other supply .

g) Batteries used in Grade B systems should be of a type that have an expected life of at least four-years under the conditions of use likely to be experienced in the system . Automotive lead-acid batteries ( i.e. the type normally used for starting service in cars ) are not suitable for fire alarm services and should not be used .

h) The battery charger for the standby supply should be compatible with the batteries used . and should be capable of re-charging a battery from its final voltage ( see 3.10 ) to a capacity sufficient to comply with the recommendations of 15.2e ) within a charging period of 24h
 
15.4 Recommendation’s for power supplies for Grade C system . ←
The following recommendations are applicable .

Power supplies for Grade C systems should comply with the recommendations of 15.3. except that : , [[ It is not . acceptable for the main supply to be connected via a card-operated meter or similar ]]

a) the working of the label described in 15.3b ) may be amended to indicate the nature of any other system with which the fire detection and fire alarm system is integrated ( e.g. to read “ Fire / Intruder Alarm : Do Not Isolate

b) The standby supply should be capable of automatically maintaining the system in normal operation for a period of 72h ( whilst giving the fault warning recommended in 17.4 ) after which sufficient capacity should remain to support the maximum alarm load ( see 3.22 ) for four minutes or to maintain fault warnings of the form and duration recommended in 17.4. whichever load is the greater .

Not : for intruder alarm systems , BS-EN-50131-1:1997 recommends a standby capacity of less than 72 h .Modifications to an intruder alarm systems are . therefore , likely to be necessary it is to incorporate a fire detection and alarm facility complying with the recommendations of this standard for a Grade C system . if a system is incapable of complying with the recommendations of this clause . it might be appropriate to regard it as a Grade E system , or to consider the possibility of a variation ( see 3.35 ) in respect of standby power supply duration , subject to agreement of the relevant interested parties ( e.g. the authority responsible for enforcing any relevant fire safety legislation ) for example , a variation might be considered in the case of an intruder alarm system with a facility for transmission of a mains failure condition to an alarm receiving centre .

15.5. Recommendation’s for power supplies for Grade D system . ←
The following recommendations are applicable .

a) The normal supply for smoke alarms and any heat alarms in Grade D system should be derived from the public electricity supply to the dwelling . The mains supply to the some alarms and heat alarms should take the form of either :

i) an independent circuit at the dwelling’s main distribution board , in which case no other electrical equipment should be connected to this circuit ( other than dedicated monitoring device installed to indicate failure of the mains supply to the smoke alarms and any heat alarms ) ; or

ii) a separately electrically protected . regularly used local lighting circuit .

b) if smoke alarms and any heat alarms are of a type that can be interconnected by wiring , all smoke alarms and heat alarms should be connected on a single final circuit .

Note : This recommendation does not apply if the form of interconnection is not capable of conducting current e.g. if the means of interconnection comprises radio communication rather than wiring .

c) The capacity of the standby supply should be sufficient to power the smoke alarm(s) and any heat alarms in the quiescent mode for at least 72h , whilst giving an audible or visual warning of power supply failure after which there should remain sufficient capacity to provide a fire warning for a further four minutes , in the absence of a fire , a fault warning for at least 24h .

Plus : Remote sounder have to be added to upstairs flats. 85 dB
 
15.5. Recommendation’s for power supplies for Grade D system . ←
c) The standby supply for smoke alarms and heat alarms may take the form of a primary battery , a secondary battery or a capacitor
 
Guide to Fire Detection & Alarm systems . 2013.

Grade D System:

Cables : Standard in accordance with BS-7671:
Standby supply : Required either primary battery or more usually secondary battery or capacitor .

Supply : An independent circuit not supplying other equipment or regularly used lighting-circuit should be used ( Clause 15.5 ) The isolator of an independent circuit should be labelled “ Smoke Alarms Do Not Isolate

When a regularly used lighting-circuit supplies the smoke alarms there should be a means of isolating the fire alarms whilst maintaining the lighting labelled “ Smoke Alarms Do Not Isolate “ unless the smoke alarms can be removed from their mounting-plates .

Interconnection : Required with standard cables per BS-7671 colour-coded .

Note : Interconnected smoke alarms etc. . must be connected to the same circuit .

House in multiple occupation with smoke & heat-alarms in common parts : smoke & heat alarms in common parts and smoke & heat alarms in dwellings with pre-payment-meters should be supplied from a permanent landlord’s supply . Then permanent notices should be displayed adjacent to any consumer unit etc. in the dwelling , which states “ Caution . Smoke Alarms Are Not Connected To This Circuit . Isolation / Switching Off At This Point , Or Having No Credit On The Meter , Does Not Isolate The Electrical Supply To The Smoke Alarm
 
All there is to known ( radio linked systems )

( BR ) 2013: 4.4.3 Note : Smoke alarms may be interconnected using radio links , provided that this does not reduce the lifetime or duration of any standby power supply to below 72 hours .

4.4.9. Radio links
Mains - powered smoke alarms may be interconnected by radio links. Provided the lifetime or duration of the standby supply is not reduced to below 72 hours. If these conditions are met the smoke alarms may be connected to different circuits ( as there is no need to isolate all the alarms to work on one )

7.11. Radio Linked System … ( BS-5839-1 Clause 27 )
The Standard recognises that radio linked systems cannot comply with all the requirements for hard-wired systems and that there are advantages & disadvantages in both systems. it is likely that the demand for radio-linked systems will grow , particularly because of the relative ease of installation in existing buildings .

Systems cannot be completely designed from drawings ; it is necessary to test on site . Booster aerials may be required on completion .
Radio links can be used for almost all elements of the system including detectors , manual call points , and sounders . Their advantage and disadvantages are summarised
Advantage and Disadvantages of radio linked systems

Advantages : Reduced hard wiring … Comments : Particularly easy to install in existing buildings
Flexible … Easy to change locations and add elements ( sounders , call points etc. )

Disadvantages :
Interference
Variable signal strength … Comments : Needs to test on site before and after installation
Low-frequency electromagnetic radiation … Comments : Some customers may have concerns
Reliance on batteries … Comments : Cost of periodic battery replacement
 
The Electrical Installation 2013 . Fire Detection & Alarm System's

The requirements for the electrical installation in terms of cable types and segregation as well as the main and standby supplies depend upon the system grade

Which summarises the requirements

Electrical supply and wiring requirements of BS-5839-6 dwellings ... ( Clause 15 & 16 )

Grade A : Power supply ( Clause 15 )
A mains supply final circuit's to all parts of the fire alarm system dedicated solely to the fire alarm system , Switches and protective device to be labelled " Fire Alarm : Do Not Switch Off .

Grade A : Standby supply
The standby supply should be capable of automatically maintaining the system in normal operation ( whilst giving an audible and visual indication of mains failure ) for a period of 72 h , after which sufficient capacity should remain to supply the maximum alarm load for at least 15 minutes , Secondary battery to have an automatic charger .

Wiring ( Clause 16 ) Cables and cable support systems ( fixings , conduit , trunking ) used for all parts of the critical signal paths and for the final circuit providing low-voltage mains supply to the system should be fire-resisting , This can be achieved by ensuring either that cables are fire resisting or that cable and cable support systems ( fixings , conduit , trunking ) are fire-resisting . ( * ) ◄

Cable segregation
Fire alarm cables to be segregated from cables of other services by , for example :
1 ) Not installing in the same conduit or trunking unless " strong " compartments are used .
2 ) Use of separate sheathed multicore cables .
3 ) Physical separation . Fire cables to be identified by colour .

Grade B : Power supply ( Clause 15 ) As for A ,
Standby supply , As for A
Wiring ( Clause 16 ) As for A - No special requirements
Cable segregation - No special requirements

Grade C : Power supply ( Clause 15 ) As A but may also supply an integral intruder alarm . The isolating protective device should be labelled " Fire / Intruder Alarm : " Do Not Switch Off "

Standby supply
As for A , the standby supply should be capable of automatically maintaining the system in normal operation for a period of 72 h , ( whilst giving the fault warnings ) but after which sufficient capacity should remain to support the maximum alarm load for 4 min .

Wiring ( Clause 16 ) - No special requirements
Cable segregation - No special requirements

Grade D : Power supply ( Clause 15 )
An independent circuit at the dwelling's main distribution board , in which case no other electrical equipment should be connected to this circuit ( other than a dedicated monitoring device installed to indicate failure of the mains supply to the smoke alarms and any heat alarms ) or a separately electrically protected , regularly used local lighting circuit .

Standby supply : As for C
Wiring ( Clause 16 ) - No special requirements
Cable segregation - No special requirements

Grade E : Power supply ( Clause 15 )
The mains supply to smoke alarm(s) and any heat alarms in a Grade E system should comprise a single independent circuit at the dwelling's distribution board . No other electrical equipment should be connected to this circuit ( other than a dedicated monitoring device installed to indicate failure of the mains supply to the smoke alarms and heat alarms )

Standby supply , None
Wiring ( Clause 16 ) - No special requirements
Cable segregation - No special requirements

Grade F : Power supply ( Clause 15 )
The batteries of smoke alarms and any heat alarms in Grade F systems should be capable of supplying the quiescent load of the smoke alarm or heat alarm , together with the additional load resulting from routine weekly testing , for at least one year before the battery fault warning is given , At the point at which the battery fault warning commences , the battery(ies) should have sufficient capacity to give afire alarm signal for at least 4 min or , in the absence of a fire , a battery fault warning for at least 30 days .

Power supply ( Clause 15 ) None .
Wiring ( Clause 16 ) - Not applicable
Cable segregation - Not applicable

( * ) Comprise either
1) Mineral insulated copper sheathed cables , with an overall polymeric covering , conforming to BS-EN-60702-1 with terminations conforming to BS-EN-60702-2
2) Cables that conform to BS-7629 specification for 300/500V fire resistant electric cables having low-emission of smoke and corrosive gases when affected by fire .
3) Cables that conform to BS-7846 Electrical cables - 600/1000V armoured fire-resistant cables having thermosetting insulation and low emission of smoke and corrosive gases when affected by fire .
4) Cables rated at 300/500V ( or greater ) that provide the same degree of safety to that afforded by compliance with BS-7629 .
 
Aico Ei1529RC , has its points .


Fire Alarm Control Switch .
230V Remote Locate, Silence & Test Control Switch - Ei1529RC


• The Test switch allows the user to test the Alarms easily, without having to access the Alarms on the ceiling. **
• Easy installation with 3 core cable: live, neutral and interconnect/control


All the units that can interconnect with the EI1529RC.


Ei141RC ..Ionisation Alarm ..Hard wire interconnection
Ei144RC.. Heat Alarm.. Hard wire interconnection
Ei146RC ..Optical Alarm ..Hard wire interconnection


• The Remote Control should be wall mounted at standard light switch level ( 1.2m from floor level ) to allow easy access. **


Siting : - Ei1529RC .. 2010.
Position the Remote Control in a location that will allow it to be easily accessed. In the majority of installations this will be in a hallway, possibly next to the master bedroom. It should be installed at the standard light switch height ( 1.2m from floor level ).
If a metal back-box is used it must have a minimum depth of 35mm. Up to four Ei1529RC System Remote Controls can be used in a system


Note: The Ei1529RC Remote Control can be wired from any location within the system. **
Fire alarms sensor remote switch.jpg
The Test switch allows the user to test the Alarms easily, without having to access the Alarms on the ceiling. ◄◄◄


Wiring in some Ionisation Alarms, Heat Alarm, Optical Alarm, Hard wire interconnection. ( LD3 )
► Disabled person by using the Ei1529RC Siting it (1.2m from floor level) to allow easy access


Ei1529RC Can be used in shops with High Ceilings, without having to access the Alarms on the ceiling ( Fire & Safety Officer asked for LD3 )


- The locate option silences all the alarms except the initial activating alarm allowing easy identification of the source of the fire
- The test option will activate all the alarms
- The hush option will temporarily silence any false alarm
- Auto-reset within 10 minutes for locate and hush
 
Appendix 12 of BS-7671:2008:
Appendix 12 of BS-7671:2011: Moved Appendix 4 sec 6.4 P421

Taken from Extracts
Verification of voltage drop : 2008:

Verification of voltage drop is now covered in BS-7671, with the introduction of BS-7671:2008
Regulation 612.14 refers .

Note : Verification of voltage drop is not normally required during the initial verification of either a new installation or an alteration or addition to an existing installation. This is because the designer of the electrical work should have sized the circuit conductors so that the voltage drop requirements of Section 525 of BS-7671:2008 are met , having regard to the circuit lengths and design currents .

However , in the case of periodic inspection and testing of an existing installation, the inspector may judge it necessary to verify the voltage drop for a particular circuit ( or circuits ) if he or she has doubts that the voltage drop requirements of section 525 are met for the circuit . This may be case, for example , where there is evidence that a circuit has been extended or that additional load has been connected or it .

a detailed explanation of the voltage drop requirements of Section 525 is beyond the scoop of this book . However , as given in Regulation 525.3 the requirements of Section 525 are deemed to be met if the voltage drop between the origin of the installation ( usually the supply terminals ) and a socket-outlet or the terminals of fixed current using equipment does not exceed that stated in Appendix 12 of BS-7671 For a low voltage installation supplied directly from a public low voltage distribution system , Appendix 12 gives maximum voltage drop of ( 3% ) for lighting circuits and ( 5% ) for other circuits , Greater voltage drop than given in Appendix 12 may be accepted for a motor during starting periods and for other equipment with high inrush currents . Also as before , a higher voltage drop may be accepted for a motor during starting conditions and for other equipment with high in rush currents , provided it is verified that it is acceptable for the equipment ( Regulation 525.4 ) refers

Regulation 612.14 lists the following two ways to verify the voltage drop for a circuit.
• Evaluate the voltage drop by measuring the circuit impedance
• Evaluate the voltage drop using calculations

Evaluation of voltage drop by measuring circuit impedance ( worked example )
Suppose that it is desired to verify that the voltage drop does not exceed ( 5% ) in an existing single-phase 230V 50Hz radial circuit supplying a 20A heating load connected at the end of the circuit . The circuit is supplied directly from distribution board at the origin of the installation . The line and neutral conductors of the circuit have thermoplastic ( pvc ) insulation and their résistance ( R[SUP]1[/SUP] + R[SUP]n[/SUP] ) is 0.3Ω when measured at ambient temperature ? 20°C

As the circuit rating does not exceed ( 100A ) and the supply frequency is 50 Hz . ( R[SUP]1[/SUP] + R[SUP]n[/SUP] ) may be taken to be the circuit impedance ( that is , inductive reactance maybe ignored )

To evaluate the voltage drop , the measured value of ( R[SUP]1[/SUP] + R[SUP]n[/SUP] ) should be increased on the basis of the increase in conductor temperature due to load current , and then multiple by the design current of the circuit ( Ib ) In the absence of better information , a correction factor of ( 1.2 ) should be used to increase the conductor résistance in this case . This assumes an increase in conductor temperature from ( 20°C ) ambient to ( 70°C ) , the maximum permitted operating temperature for thermoplastic insulated conductors .

The voltage drop ( Vd ) for the single phase circuit in this example is (\) therefore given by :
( Vd ) = measured value of ( R[SUP]1[/SUP] + R[SUP]n[/SUP] ) x 1.2 x Ib
therefore (\) Vd = 0.3Ω x 1.2 x 20A = 7.2V

A voltage drop of ( 7.2V ) is equivalent to ( 3.13% ) given by 100% x 7.2V ÷ 230V . it has therefore been verified that , in the case of this example , the voltage drop in the circuit does not exceed ( 5% )

Evaluation of voltage drop using calculations ( Worked example )
The calculation method mention in Regulation 612.14 , as an example , is to use diagrams or graphs showing maximum cable length versus load current for different conductor sizes with different percentage voltage drops for specific nominal voltages, conductor temperatures and wiring systems .

In the absent of such diagrams or charts , the voltage drop for a circuit may be calculated by using the tabulated values of voltage drop given in Appendix 4 of BS-7671: in accordance with the instructions given in item 6 of that appendix , To do this , it will be necessary to ascertaining the type and size of cable by inspection , and to estimate the length of run for the circuit .
 
Maximum earth fault loop impedance values for overcurrent protective devices in common use , ( for Fault Protection )
Extracts :

Why do you need to test , Earth-fault-loop-impedance !! .... Under Earth fault conditions RCD will trip out before 0.04s .

Under earth-fault-conditions , a circuit which relies on the protective measures ( ADS ) for fault protection is generally required to be disconnected under fault conditions within the maximum time permitted by BS-7671: for that type of circuit or location .

Tables 41.2 , 41.3 , 41.4 of BS-7671: give the maximum permitted values of ( Zs ) for different types of overcurrent protective devices and different maximum permitted disconnection times .

A indicated above , it is generally necessary to adjust the values obtained by the test before comparing them with the maximum permitted values given in BS-7671: This is because the values referred to in BS-7671: are based on the conductors having been heated up by the passage of load current , which increases their résistance , whilst test results are usually obtained when the conductor temperature is somewhat lower . Detailed advice on correction factors is given on IET Guidance Notes 3 & 6 .

Alternatively , as a rule of thumb , the measured value of ( Zs ) should not exceed ( 0.8 times ) the relevant value given in BS-7671: such as in Tables 41.2 and 41.4.

limiting values of measured earth fault loop impedance when measured at ambient temperatures up to ( 20°C ) These limiting measured values are based on ( 80% ) of the values given in BS-7671: for ( 0.4 second & 5 second disconnection ), as appropriate .

Note : that the value to be recorded in the schedule of test results is the measured value .
if the protective device is not of a type whose maximum permitted ( Zs ) value is given in BS-7671: then , as a rule of thumb , the measured value should not exceed ( 0.8 times ) the value given by the formula on the first page of Appendix 3 of BS-7671:

2008: 243
2011: 295
 
Working like a Trojan , don't have much spare time . Hi Karl

Re-cap

O.S.G. reminds us - The use of RCBOs will minimize inconvenience in the event of a fault and is applicable to ALL systems
RCBO - type of protective-device
Overload .
Short-circuit .
Earth-fault .

O.S.G. P/70 Choice of protective-device .
The selection of protective device ( Depends upon )
i) prospective fault current
ii) circuit-load characteristics
iii) cable current-carrying-capacity
iv) disconnection time limit

O.S.G. P/80 There is no general requirements to ensure electrical continuity across the metallic frame of an item of furniture unless the frame has been designed to be used as a protective-conductor . 543.2.1. , 543.2.6.
 
Why we do certain tests .
The regulation's tells us " Initial Verification "

Why do we need to test the continuity of protective conductor's
612.2.1. Continuity of protective conductors including main protective bonding conductor's
17th Edition - Supplementary protective bonding conductor's (where required )

it is essential to ensure that all circuit-protective-conductor's & main protective bonding conductor's are continuous .
otherwise , an exposed-conductive-part , an extraneous-conductive-part or the earth-terminal of a point or accessory could be left without an effective connection to Earth , giving no ( Fault-protection ) in the event of an earth-fault .

Fault-protection : Comprises
411.3.1.1. • Protective-earthing .
411.3.1.2. • Protective-equipotential-bonding .
411.3.2. • Automatic-disconnection in case of a fault . ADS

Fault protection is provided by limiting the magnitude and duration of voltages , that may appear under earth-fault-conditions between simultaneously accessible exposed-conductive-parts of equipment and between them and extraneous-conductive-parts or earth .

Whilst the primary purpose of testing for protective conductor continuity is to ensure that such continuity exists , the result ( R[SUP]1 [/SUP]+ R[SUP]2[/SUP] ) test can be used to determine the earth fault loop impedance at the point or accessory at which the test is applied.

The wander lead method . ( R[SUP]2[/SUP] )
This method is used principally for testing ( Protective-conductor's ) that are connected to the main earthing terminal , main equipotential bonding conductors , circuit protective conductors & so on .

612.2.2. Continuity of ring final circuit conductor's .. ( Continuity , a complete circuit ) Loop
Measure between two points in a circuit with MFT tester

612.2.2. A test shall be made to verify the continuity of each conductor , including the protective conductor , of every ring final circuit .
The cables of a ring final circuit start at the outgoing terminals of a ( CCU ) or ( DB )
Connect to all the points in the ring , and return to the same outgoing terminals , The line & neutral conductors must from a complete unbroken loop without interconnections as must the circuit protective conductors .

Single cable's - same size of conductor's ... Conduit or Trunking .

T&E Circuit-protective-conductor 1.5mm[SUP]2[/SUP] - ( 1.67 times )
Line / Neutral 2.5mm[SUP]2[/SUP] ÷ 1.5mm[SUP]2[/SUP] = 1.67

" Dead Test "
T&E Note :- the readings obtained as : ( Little r )
End to end résistance of the line conductor = ( r[SUP]1[/SUP] )
End to end résistance of the neutral conductor = ( r[SUP] N[/SUP] )
End to end résistance of the circuit-protective-conductor = ( r[SUP]2 [/SUP] )

The line and neutral conductors should have equal résistances , if the circuit-protective-conductor has a smaller cross-sectional area than the line and neutral , its résistance should be higher .

In the case of a ring circuit having 2.5mm[SUP]2[/SUP] Live conductor's ( L / N ) and a 1.5mm[SUP]2[/SUP] circuit-protective-conductor , the résistance of the Cpc should be about ( 1.67 times ) that of the line or neutral conductor.

? readings T&E Line & neutral = 0.20Ω
? readings T&E Line & circuit-protective-conductor = 0.27Ω

Socket-outlet-circuit
The length represents the total ring cable loop length and does not include any Spurs .
As a rule of thumb for rings , unfused spur lengths should not exceed ( 1/8 the cable length ) from the spur to the furthest point of the ring .

402 Generic Schedule of Test Results . * Where there are no spurs connected to a ring final circuit this value is also the ( R[SUP]1 [/SUP]+ R[SUP]2[/SUP] ) of the circuit .
 
on behalf of Amberleaf
Learning curve
: what is Parallel-paths
MFTMEGG.JPGMegger 1552 . ... MFT

TN-S converted to TN-C-S (PME)

1) - Live test

Switch the tester over to (PFC) prospective fault current .
(Green setting)

(PFC) Test between line & neutral ..( short-circuit-fault) reading 1.86kA ... just making a point, so example readings (kA)
(PFC) Test between line & earth ..(earth-fault) reading 1.84kA & Parallel-paths

► (kA) (Green PFC) Loop .. reading *.** kA

The(PSCC) of a circuit is the largest Prospective Fault Current (PFC) in a single-phase-system, this would be the larger of the earth loop (PFC) and the Neutral loop (PFC)

612.11. Prospective fault current .. Ipƒ

prospective short-circuit-current .. (PSCC) .. short-circuit .
&
prospective earth-fault-current shall be measured ..(PEFC) .. earth-fault

measured at the origin or at other relevant points in the installation

R/P 31, Origin of an installation. The position at which electrical energy is delivered to an electrical installation .

The requirements are that the (PSCC) & (PEFC) are to be measured .. (also at the other relevant points in the installation)
A relevant point is a point where a protective device, required to operate under fault-conditions, has been installed, etc.

To prove that in the event of a fault the protective device can handle the fault current (at the point of installation) without danger.

Parallel-paths, what is Parallel-paths

Learning curve : All circuit-protective-conductors & main-protective-bonding-conductors are connected through the (MET) via earthing-conductor down to the substation ↓↓↓↓

At origin . Measurement of (PEFC) earth-fault-current .. with Parallel-paths in place . 1.84kA worst case scenario .

At origin . Measurement of (PEFC) earth-fault-current .. with Parallel-paths removed . 1.66kA .. small reading . Just earthing conductor connected

R/P 26 . Earth-fault-current . A current resulting from a fault of negligible impedance between a line-conductor and an exposed-conductive-part or a protective-conductor

R/P 34 . Short-circuit-current . An overcurrent resulting from a fault of negligible impedance between live-conductors having a difference in potential under normal operating conditions .

The highest reading measured is the "worst case scenario" and is the one that will be entered onto the schedule of tests
Domestic, circuit-breakers can safely break 6kA( 6000A) in the event of a fault BS-EN-60898
 
GN-3 2008: 3.10.3. (c) Polarity
Tests should be made to verify that : 1) the polarity is correct at the meter and distribution board .

BS-7671: P/402 , Schedule of Test Results .. Top left-hand corner . Correct supply polarity confirmed [ ]

O.S.G. P/99 . it is important to confirm that :
After connection of the supply , correct polarity must be confirmed using a voltage indicator or a test lamp ( in either case with leads complying with the recommendations of HSE Guidance Note GS-38 . refer to

GN-3 : P/47
Polarity testing
The polarity of all circuits must be Verified before connection to the supply . refer
Alternatively polarity can be verified by visual checking core-colours at terminations , Thus:
Verifying the installer's connections . Whatever method is used , polarity checks are required at all points on a circuit .

Note : The continuity test and ring-continuity test may confirm polarity

R/P 192 . Polarity . A test of polarity shall be made and it shall be verified that :
i) every single-pole control and protective device is connected in the line conductor only
iii) wiring has been correctly connected to socket-outlets and similar accessories

O.S.G. Correct polarity must be confirmed using a voltage indicator or a test lamp

Correct incoming polarity

T5-1000 Electrical Tester

Safe isolation procedure .. 100A Isolator
Lock off , padlock

Main switch is in the OFF position
1) firstly testing for voltage between the incoming line & neutral-conductor ....... right sided little window will indicate ( Orange ) 230V
This shows a voltage present as highlighted but does not tell you which one of these terminals is ( line ) it could be either one .

2) Test between line & earth " line " incoming terminal appears to be " line " on the incoming polarity check
....... right sided little window will indicate ( Orange ) .. 230V

3) final check on the incoming polarity , test between neutral & earth , no ( 0 ) voltage present , This proves that neutral & earth are at the same voltage , if the incoming supply was ( back to front ) you would get a voltage indication here . ( neutral & earth ) reversal of polarity .. 230V

• it proves that the line incomer terminal is in fact ( Line ) correct polarity

Lock off , padlock .. still in place , 100A isolation switch :
Checking safe isolation !! checking that the main-switch is really isolated .
Check the operation of the voltage tester ( T5-1000 Electrical Tester ) is the outgoing side of the main-switch still be live .
Checking the line out-going terminal of the dead side ( bottom side of ) the isolator to earth , you should get No Readings . " Dead "

recap - you have proved , the incoming supply has been connected properly with correct incoming polarity
 
Speed up your Laptop or PC

if your Windows computer has become slow and unresponsive , then unneeded files and programs could be clogging it up . A simple hard-drive clean-up can boost its performance and make for speedier surfing . Here how :

Left-hand , One click on mouse
1 . Click the " Start " button ( bottom left-hand corner on your screen ) Choose " All Programs " from the menu that appears .

2 . Click on " Accessories folder " and choose " System tools folder " from the menu . Click on " Disk Cleanup "

3 . Select the drive you want to clean up , and click " OK " (C:) !!!
4 . Click " Clean Up Systems Files " for more categories of files to delete .

5 . Choose what you want to remove .
For example . temporary set-up files . recycle bin files and files left over from old software updates . Click " OK " and then click " Delete Files "
 
Inspected first & tested secondly
Initial verification , New installation is not allowed to fail . Fails are only relevant to periodic reporting .
 
On rant mode .

Method 2 : or " Wander lead test "
relevant column on the test schedule Continuity ( Ω ) R[SUP]2 [/SUP]column 14 .

When will I used the Method 2 :
Confirm that you have a protective-conductor in place ( R[SUP]2[/SUP] ) Water , Gas pipes copper .

The main-protective-bonding-conductor , Equipotential Bonding .
Parallel path's must be eliminated for this test , measuring this cable alone . main-protective-bonding-conductor .. ( A to B )

Evaluation of Test Results

Candidates were asked to determine whether a stated value for the measured resistance of a given main protective bonding conductor was acceptable. Candidates were therefore expected to use given information to determine the expected value of resistance and compare

given main protective bonding conductor was acceptable. Candidates were therefore expected to use given information to determine the expected value of resistance and compare this with the stated measured value. Some candidates carried out the correct calculation but failed to identify the units applicable to their answer and so losing marks.

A large number of candidates incorrectly stated that the maximum value for the resistance of a main protective bonding conductor was 0.05 Ω. This value is applicable where access to the bonding connection is not possible and a test is made between two extraneous conductive parts (GN-3 Page 35). This value is not the maximum permitted resistance of the main protective bonding conductor.

GN-3 - 2008: ( R[SUP]2[/SUP] )
To confirm the continuity of a bonding conductor , the leads from the instrument are connected to each end of the conductor and a reading is taken .One end of the bonding conductor and any intermediate connections with services may need to be disconnected to avoid parallel paths

This method can also be used to confirm a bonding connection between extraneous-conductive-parts where it is not possible to see a bonding connection e.g. where bonding clamps have been " built in " The test would be done by connecting the leads of the instrument between any two-points such as metallic pipes between which a bonding connection was required and looking for a low ( minimal deflection ) reading of the order of 0.05Ω or less

GN-3 - 2011: ( R[SUP]2[/SUP] ) P/35
Testing bonding conductors & Earthing conductors
To confirm the continuity of these protective conductors , Test method 2 may be used

This method can be used to confirm a bonding-connection between extraneous-conductive-parts where it is not possible to see a bonding connection e.g.
where bonding clamps have been " built in " The test would be done by connecting the leads of the instrument between any two-points such as metallic pipes and looking for a low reading of the order of 0.05Ω ( it should be noted that not all low-résistance ohmmeters can read this low )
 
Chief Examiners’ report – December 2012

Testing

Another common incorrect answer given by candidates was that the continuity of main-protective-bonding-conductors could be carried out using either the ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) method or, worryingly, an earth fault loop impedance tester.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Re-take - Useful Information for 2394 :
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
1K

Advert

Thread statistics

Created
amberleaf,
Last reply from
Richard Burns,
Replies
1,197
Views
27,877

Advert

Back
Top