Re-cap:

The is the nearest I canget to Q/As about , Safe-Isolation.

Q) To verify or prove a successful-electrical-isolationyou would use a ? Voltage-indicator
Voltage-indicator
Voltage-proving-unit
Set of GS-38 test-leads
Small-padlock.

Q) To securean electrical-isolation you should use a ? padlock .
Voltage-indicator
Voltage-proving-unit
Set of GS-38 test-leads
padlock .

Q) Where a test-instrument or voltage-indicator is used to prove a supply-dead , thesame-device must be tested to show that it still-works using a ? Voltage-proving-unit
Voltage-indicator
Voltage-proving-unit
Set of GS-38 test-leads
Small-padlock.

Q) To give adequate-protection to theperson carrying-out a safe-isolation-procedure , thetest-instrument must incorporate a ? Set of GS-38 test-leads
Voltage-indicator
Voltage-proving-unit
Set of GS-38 test-leads
padlock.

Q) When connecting single-phase-loads to a three-phase-supply , we must take care to distribute the single-phase-loads equallyacross the three-phases so that each phase carries approximately the same-currents , this is called ? Balancing of theload .

Re-cap: Socket-outlets. 2392-10

Additional - 30mA RCD protection is required for socket-outlets .
Ifused by Ordinary-persons .
And intended for general-use

Regulations - 411.3.1. 415.1.1.

Additional protection for socket-outlets . RCD / Circuit-breaker .

Additional-protection by 30mA RCD is required in ( Addition ) to ( Overcurrent-protection ) for allsocket-outlets to be used by Ordinary-persons and intended for general-use .

For this reason . Additional protection
Is provided in case ( Basic-protection ) or ( Fault-protection-fails ) or if the User of the installation is careless - 415.1.1.

By definition . Ordinary-person : A person who is neither a skilled-person nor an instructed-person .


 
Q) Continuity of protective-conductors .

Recap -Written exams . 2394

What is you reason for this .
The object of the test is to ensure that every-circuit-protective-conductor is correctly-connected and has avery-low-résistance .

Q) Insulation-résistance - ( IR )

What is you reason for this .
The object of the test is the verify the quality of theinsulation and that the insulation-résistance has a high-value . MΩ

The test is made at the consumer-unit with the supply-disconnected using an insulation-résistance-tester which supplies a voltage of 500V . ( BS-EN-61557-6 )

Q) Part - 6 of the IET - Regulations deals with ?
Protection for safety
Selection and erection of equipment
Special-installations
Inspection & testing .

Q) the electricity-supply to adomestic-consumer is usually protected at the incoming-service-position by a ?
Meter
Double-pole-switch
100A circuit-breaker
100A HBC - fuse . ( BS-88-3 - C )

Q) What action is necessary toproduce a secure-electrical-isolation ? The isolated-supply must be locked-off or secured with a padlock
Isolate the supply and observe that thevoltage-indicator-reads-zero
Find connect a test-device such as a voltage-indicator to the supply
Larger-pieces of equipment may require-isolating at a local-isolator-switch
The isolated-supply must be locked-off or secured with a padlock

 
My- point .

The form of protection-provided by the Insulation of Live-parts would be .
Protection against “ direct-contact

p.23 . Basic-protection: Protection against electric-shock under fault-free-conditions .
Note : for low-voltage installations , systems andequipment . basic-protection generally-corresponds to protection against “ Direct-contact “ that is “ Contact of persons or livestock with Live-parts

Whywas the name left in BS-7671:2008 “ Direct-contact
Direct-contact“ Deleted by BS-7671:2008: ( see Basic-protection)

It was left in the BS-7671:2008:2011: for a better understanding of the meaning of the : WordDirect-contact

Calculationof earth-fault-loop-impedance : ( Zs )
Themost commonly used protective-measure against ( “ Direct-contactBasic-protection) is that of automatic-disconnection of the supply , using the overcurrent-protective-device

Which also provides protection against overload & / or short-circuit-currents for the circuits-concerned .

Residual-current-devices ( RCD ) or combined-devices ( RCBOs ) RCD / Circuit-breaker . ( inExams use the full-name , Not MCB )

Whichever type of device is chosen , it is necessary for the designer to calculate the earth-loop-impedance ( Zs ) of every-circuit in the installation .
Tocheck that these impedances do not exceed the maximum specified in BS-7671:2008:2011: Tables, 41.4. 41.5 . Etc .

The earth-loop-impedance thathas to be considered is that which comprises the impedance of the source , the Line-conductor up to the fault plus the protective-conductor from the fault to the source , Note : that when an RCD or RCBO is used to provide automatic-disconnection of the supply in a TN- system , the calculations of ( Zs ) is normally unnecessary-provided that continuity of the earth-loop hasbeen established .

Regulation: p.55 . look at 411.4.7. / 411.3.2.3. , the values specifiedin Table - 41.3 for the types and ratings of overcurrent-devices listed may be used instead of calculations . 2392-10. your off the hook here . RCBOs or Circuit-breakers .

Where a circuit-breaker is used tosatisfy the requirements of Regulation , Etc. Uo of 230Vand disconnection-time of 0.4s in accordance with Regulation - 411.3.2.2. or 5s in accordance with Regulation - 411.3.2.3. the values specified in Table - 41.3 for the types andratings of overcurrent-devices listed may be used instead of calculations .

Re-cap: 2392-10 . ( RCBOs ) RCD / Circuit-breaker / Overcurrent-protective-device.

You will not get this in your Exams . 2392-10, just an understanding . Yeah .
Theother , reason for calculating the earth-loop-impedances is to check that the circuit-protective-conductors areadequately-protected-thermally .
Thatthey comply with ,adiabatic-equation given inRegulation - 543.1.3. Etc .

BS-7671:1992: + Amd 1:1994 included a regulation that required account to be taken of the increase in temperature and résistance of conductors as a result of the fault-current .

However: this Regulation also allowed a simpler approach to be taken under-some-conditions , for thedevice listed in Appendix - 3 of BS-7671: 1994 , the requirement was deemed to be satisfied if the circuit-loop-impedance met the required when the conductor(s) are at there normal-operating-temperature .

Fuses to BS-88-3 - C . up to 100A . p.56. Old - BS-1361
Semi-enclosed-fuses to BS-3036 to 100A .p.56 .
Fuses to BS-88- part 2 .& Part -6 up to 100A . p.56 .
Type B . C , D , circuit-breakers , BS-EN-60898 , & RCBOS to BS-EN-61009-1 up to 125A . p.56

circuit-loop-impedance -1994 , ( Zs ) The word circuit-loop-impedance is not used 2011: Earth-fault-loop-impedance. all it does is define it a bit better . Yeah . use the full title in exams .


 
GN-3: p.39
The purpose of the insulation-résistance-test is to verify that the insulation ofconductors-provides adequate-insulation , is not damaged and thatlive-conductors or protective-conductors are ( Notshort-circuited )

Operation of two-wayand intermediate light-switch s -&-s

GN-3. p.40 / 41 .
Insulation-résistance-test of a whole-consumer-unit . ( Lamps removed for test ) Open-circuit

For circuits containing two-way-switching or two-way and intermediate-switching ,the switches must be operated oneat a time and the circuitssubjected to additional-insulation-résistance-test in these-configurations .

GN-3. p.41 .
Insulation-résistance-test of a final-circuit . ( Lamps removed for test )

Operation of two-wayand intermediate light-switch s -&-s

For circuits containing two-way-switching or two-way and intermediate-switching ,the switches must be operated oneat a time and the circuitssubjected to additional-insulation-résistance-test in these-configurations .

 
Spam.

Pitty you can't spell, a credit to you're company.

To confuse everyone, the post I was refering to has been deleted. NOT AL's posts.
 
Last edited by a moderator:
O.S.G.p96 .

Re-cap,

For an installation-operating at 400/ 230V , although an insulation-résistance-value of only 1MΩ complies with BS-7671 :

Where.

The insulation-résistance-measured is less than 2MΩ the possibility of a latent-defect-exists .

In these circumstances , each-circuit should then be tested separately .

2394 : Keep in mind written-exams . :gettree: :17:



 
O.S.G.p87 . 2392-10 , just starting out on Inspection & Testing . Inspection meaning - Visual is our first line of defence .

One of the most important Regulations in exams , 612.1.
If any test indicates a failure to comply , that test and any preceding-test , theresults of which may have been influenced by the fault-indicated , shall berepeated after the fault has been rectified .

O.S.G. 9.3. Testing .
Testing must include relevant-tests from the following-checklist

O.S.G. 9.3.1. Testing checklist . ◄

Insulation-reading:
Test-instrument , Readings with leads . Open-circuit - > 999MΩ .

Q) if there is no British-Standard then the insulation-résistance should not be less than 1MΩ .

 
Leaning - Curve . Only. Old-Notes 2008 . :icon_bs:

From the information given determine ,

The value of the insulation-résistance-measured taken and the requirements of BS-7671: are satisfied . Your-Call . Yeah

1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4 + 1/R5

1/Rt = 1/6 + 1/3 + 1/4 + 1/12 + 1/6

Find the lowest-common-denominator i.e. - 12

= 2 + 4 + 3 + 1 + 2 - 12 .

1/Rt = 12 / 12

Therefore : Rt/1 = 12 / 12 = 1MΩ .

Re-cap . Reminder - Guidance-Note - 3 .

Although the requirements of BS-7671: appear to have been satisfied , GN-3 refers to the possibility of a [ Latent-Defect ] existing within the installation . the circuits’ should be tested individually and a minimum-insulation-résistance of 2M is recommended .

As the measurement taken for all of the circuits are above 2MΩ then no investigation would be required .




 
Leaning - Curve . Only. Old-Notes 2008 . :icon_bs:

From the information given determine ,

The value of the insulation-résistance-measured taken and the requirements of BS-7671: are satisfied .

1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4 + 1/R5 + 1/R6

1/Rt = 1/120 + 1/30 + 1/40 + 1/12 + 1/60 + 1/10

Find the lowest-common-denominator i.e. - 120

= 1 + 4 + 3 + 10 + 2 - 12 - + 12 - 120

1/Rt = 32 / 120

Therefore : Rt/1 = 120 / 32 = 3.75MΩ .


 
Electricians , Do I Mixor Match ??

SafeSection of Devices for Installation in Assemblies . August - 2011:

Awarning against the practice of installing devices ( E.g. RCBOs , Circuit-breakers ) of one-manufacturer into assemblies ( E.g. consumer-units . Distribution-boards ) of another-manufacturer . there is evidence that some installers aremixing-products , oftenwithout fully understanding the potential-safety-implications .

Assembliessuch as consumer-units , Distribution-boards and panelboards are tested with specific-devices installed , these devicesare more often than not from the same- manufacturer as the enclosure , testingand certification is undertaken to BS-EN-60439 . formerlyBS-5486 Although BS-5486 is now obsolete there are manyexisting-installations with assemblies complying with this standard and the issues of mixing-different-manufacturer’s devices equally apply , particularly where older-devices maybe difficult to source .

Inall cases , installing-devices other than those declared by the assembly-manufacturer invalidates any testing / certification andwarranty .

BS-7671:puts specific-responsibility on the installer . Regulation - 510.3 . requires that the installer takes into account the manufacturer’s-instructions . it is therefore theresponsibility of the installer who intends to , mix-different- manufacturer’s-devices/ components . in an assembly , to undertake appropriate-testingand ensure-conformity with BS-EN-60439 . if this is not done then there is aprobability that , in the event of death . injury . fire or other-damage , the installer would be accountable under , Health & Safety - legislation .

Althoughdevices may appear similar , the dimensions . technical-performance andterminations are not necessarily-compatible .

Distributor and Wholesalerresponsibilities :

A distributor and wholesaler also has aresponsibility under the , general-product-safety-regulations to act “ withdue care “
Distributorand wholesaler should be able to substantiate any advice related to ,interchangeably of devices in assemblies , if the installer acts on a distributor’s - advice and information , andin doing so produces anon-compliant-assembly , then both the distributor and installer may be liable forany-consequences .
 
Circuit-breakers to BS-EN-60898 &RCBOs to BS-EN-61009-1 in non-preferred-current-ratings

Circuit-breakersto BS-EN-60898
RCBOsto BS-EN-61009-1 are sometimes encountered that have a rated-current other than thepreferred-values [ 3A , 6A , 10A ] listed in Table - 41.3. of BS-7671:2008:2011:

Themaximum-value of ( Zs ) for such a device , at a nominal-voltageof [ Uo - 230V ] can be found from the right-hand-columnof Table - 41.3. of BS-7671:2011:
Table- 41.3 , right gives therelevant-information .

Type - B circuit-breaker . having arated-current ( In ) of 8A ( or the overcurrent-characteristic of an8A Type - B RCBO ) the maximum-value of ( Zs )
at 230Vis 46 / In , = 46 / 8 = 5.75Ω .

Maximum( Zs ) for circuit-breakers to BS-EN-60898 and the overcurrent-characteristic of RCBOs to BS-EN-61009-1for instantaneous-operation giving compliance with the , 0.4 & 5 seconds ,disconnection-times at nominal-voltage [Uo - 230V ]

Table- 41.3.

Type- B - ( Zs ) Ohms for devices ofrated-current ( In ) 46/In .
Type- C - ( Zs ) Ohms for devices ofrated-current ( In ) 23/In.
Type- D - ( Zs ) Ohms for devices ofrated-current ( In ) 11.5/In.

Obsolete-Circuit-Breakers :
Maximum-valuesof ( Zs ) for circuit-breakers for which thisinformation is no longer given in BS-7671: can be obtained either from the edition of BS-7671: that was current when the deviceswere readily-available , or by reference to the manufacture’s - data .

Alternatively, for MCBs to BS-3871: Table - 2 , can be used to find the maximum-value of ( Zs ) at a nominal-voltage of [ Uo - 230V ]

For a Type- 2 circuit-breaker to BS-3871: having a rated-current ( In ) of 30A , the maximum-value of (Zs ) at 230V is [ 32.8 / In = 32.86/ 30 = 1.1Ω ]

Maximum( Zs ) for circuit-breakers toBS-3871: for instantaneous-operationgiving compliance with the , 0.4 & 5 seconds , disconnection-times at anominal-voltage of [ Uo - 230V ]

Type( Zs )
Type- 1 . Ohms - for device of rated-current- ( In ) 57.5/In
Type- 2 . Ohms - for device of rated-current- ( In ) 32.86/In
Type- 3 . Ohms - for device of rated-current- ( In ) 23/In
Type- 4 . Ohms - for device of rated-current- ( In ) 4.6/In

Type- B - ( Zs ) Ohms for devices of rated-current ( In ) 46/In .
Type- C - ( Zs ) Ohms for devices of rated-current ( In ) 23/In .
Type- D - ( Zs ) Ohms for devices of rated-current ( In ) 11.5/In .

Obsolete-fuses :
Maximum-valuesof ( Zs ) for fuses for which this information is no longer given in BS-7671: can be obtained either from the editionof BS-7671: that was current when the deviceswere readily-available , or by reference to the manufacture’s - data .

After 31 - December 2011 : one of these approaches is necessary forfuses to BS-88-2.2. : BS-88-6 : and BS-3871 : as data for them is notincluded in , BS-7671:2008:incorporating Amendment - 1 . 2011:

Overcurrent-protective-devices generally :
Forany type and rated-current of a fuse or overcurrent-circuit-breaker , includingall those mentioned above , the maximum-value of ( Zs ) can be found using the , formula given in Appendix - 3 of BS-7671: Where :- Zs = Uo /Ia .

Uo- is the nominal A.C. r/ms line-voltage to Earth - 230V.
Ia - is the current causing-operation of the protective-devicewithin the specified-time . such as 0.4 or 5 seconds . obtained fromthe manufactures - time / current-characteristics for the particular device-type and rating .

Supposed the manufactures - time / current-characteristic for a 400A - fuse , to BS-88-2.1. gives a value of ( Ia of 2840A ) for a disconnection-time of 5 - seconds . Using the above - formula , the maximum-value of ( Zs ) for the fuse , fordisconnection-time of 5 - seconds and anominal-voltage
( Uo ) of 230V , 230V ÷ 2840A = 0.08Ω

Measured- values of ( Zs ) taking account of conductor -temperature

It should not be forgotten that when comparing ameasured-valued of ( Zs ) with the maximum-value of ( Zs ) allowable for the device used for , fault-protection , account must betaken of the temperature and résistanceof the circuit-conductors . Appendix - 14 of BS-7671: refer .

Provethat the following table-provides instantaneous-disconnection for a BS-EN-60898 & BS-EN-61009-1 - Type B .32A Circuit--breaker using table 41.3. App - 3 .

Zs ≤ Uo /Ia . Table- 41B2

16[SUP]th[/SUP] Edition :
Type- B . 48/In
Type- C . 24/In
Type- D . 12/In

Zs ≤ 240/ 160 = 1.5

48/ 32 = 1.5Ω
240/ 48 = 5. In
32A x 5 = 160A

Mostmanufactures data-shows 3 - 5 x . In for instantaneous-disconnection .

Zs ≤ Uo /Ia .

17[SUP]th[/SUP]Edition : 2008: 2011 :
Type- B . 46/In
Type- C . 23/In
Type- D . 11.5/In

Zs ≤ Uo /Ia . Table - 41.3.

Zs ≤ 230/ 160 = 1.4375 . Round-up to 1.44Ω
46 / 32 = 1.44Ω
230 / 46 = 5. In

Type- B : > 3/In . ≤ 5.0 / In
Type- C : > 5/In . ≤ 10.0 / In
Type- D : > 10/In . ≤ 20.0 / In


If Armoured-Cable is harshly-treated the Amour-wires canbecome-displaced , twisted or stretched , leading to bulges in the sheath-material
Cablesare uniform and circular in cross-section when manufactured , but mishandlingcan result in bulges an kinks which cancause difficulties in pulling into ducts, termination at glands , as well as being unsightly , such problems can be causedby incorrect-pulling from the drum . the introduction of loop and kinks ,pulling round too tight a bend .

 
Q) a 6A BS-EN-60898 circuit-breaker is used to protect a circuitwith a , maximum-earth-fault-loop-impedance ( Zs ) of 3.83Ω would be type ? Table - 41.3 . p56
B. ……… above 3/In up to including 5/In
C . ……… above 5/In up toincluding 10/In
D. ……… above 10/In up to including 20/In

Youcan’t predicted what level yourcircuit-breaker will trip on , will trip instantly between three and five timesits rated-current [ 3In x 6A = 18A : 5In x 6 = 30A ]
Type- B current for time , 0.1sec to 5 seconds . Fig - 3A4 , p.301 . BS-EN-60898 & BS-EN-61009-1

Calculating- Earth-fault-loop-impedance . Zs = Uo /Ia .
5 times magnetic-settings - 5 x 6A = 30A : Zs ≤ 230V ÷ 30A = 7.67Ω . re-cap Table 41.3 6A = 7.67Ω .

 
Thisone always trips up . Q/As -&-s . 2392 . 2394

Q). When testing a 100mA RCD themaximum-test-current applied via the test-instrument will be ? ( G )
3 x In
5 x In
I x In
 
RCDscannot detect . Short-circuits or Overloads . due to their design .

Tosummarise the RCD tests . 30mA -Testing .

IΔn / 2. No-tripin 2 seconds . 30mA ÷ 2 = 15.
 
Because it’s Not in the 17[SUP]th[/SUP]- Edition : 2008: or 2011: Doesn’t not mean it did not Exist . “ Pastto Present “ :icon_bs:

Earthing& Bonding - 2[SUP]nd[/SUP] Edition
Incorporatingthe requirements of BS-7671:2001:
IncludingAmendment , No - 2 .

Looped-main-equipotential-bonding . 2006.

Main-equipotential-bonding-conductor(s) should , ideally, Not be looped from service to service . ( METto Water - Gas )

Solution:
Wherea common-bonding-conductor-loops In and Out,to connect to an ,extraneous-conductive-part . The protective-conductor should beleft-unbroken at the connection .

Thisis so that the ( Continuity ) to other-items connected to thebonding-conductor will not be detached , for example . as a result of work beingcarried out to pipework , refer , Regulation - 528-02-04.

Wherea wiring-system is to be installed in proximity to a non-electrical-service, it shall be so arranged that anyforeseeable-operation carried out on either-service will not cause-damage tothe other .

528.3.3. : 17[SUP]th[/SUP] - Edition .
Wherean electrical-service is to be installed in proximity to a non-electrical-services , it shall be so arranged that anyforeseeable-operation carried out on either-service will not cause-damage tothe electrical-service or the converse . Etc .

Apermanent-label bearing the Words “ Safety Electrical Connection - Do Not Remove “ isrequired in a visible-position at or near the point of connection ofevery-main-bonding-conductor to an , Extraneous-conductive-part , and at themain-earthing-terminal where this isseparate from the main-switchgear - Regulation - 514-13-01.

514-13: 2002 / 2004 : Warning-notices: earthing and bonding-connections .
514-13-01 . A permanent-label to BS-951 , with the words “ SafetyElectrical Connection - Do Not Remove “ shall be permanently-fixed in avisible-position at or near : Etc .

514-13: Warning-notices :earthing and bonding-connections .
514-13.1: A durable-label to BS-951 , with the words “ SafetyElectrical Connection - Do Not Remove “ shallbe permanently-fixed in a visible-position at or near : Etc .

Regulation- 528-02-04 :
Wherea wiring-system is to be installed in proximity to a , non-electrical-serviceit shall be so arranged that any , foreseeable-operation carried out on eitherservice will not cause-damage to the other.

 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
376
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top