Useful-Junk: 2001 / 2004 .

Means of earthing in Older-Installation(s)

Older-Installation(s)are sometimes found to employ the water-service-pipe as the sole means ofearthing .
Older-Installation(s)may use a Gas , Water orother-metal-service-pipe as a means of earthing . This is Not-permitted .

Ithas never been permitted to use a , Gas-pipe as a means of earthing and , since 1966 , it has not beenpermitted to use any other-service-pipe either .

Necessary-equipotential-bonding-connections, MUST , be made to the Gas-installation-pipe , Water and other metal-service-pipe(s)

542-02-04 : p113
The metalwork of a Gas , Water or other-serviceshall , NOT be used as aprotective-earth-electrode , this requirement does not preclude the bondingof such metalwork as required byRegulation - 413-02 .

 
Labelling of the Earthing-Conductor :

it make life easer for any Inspectors inthe near-future .

the earthing-conductor , the conductor connectingthe installation to the ( Means ) of earthing , Mustbe easily-identifiable .
earthing-conductor(s) are not always labelled where requiredmaking it easily possible to mistakenly-disconnect the wrong-conductor.

a Equipotential-bonding-conductor , mayunintentionally be disconnected when intending to disconnect theearthing-conductor .

Earthing-conductor: [ Protective-conductor ]
Water-service-pipe: [ Main-protective-bonding-conductor ]
Gas-installation-pipe: [ Main-protective-bonding-conductor ]
Distribution-board 1 :
Distribution-board 2 :

MET- Safety-electrical-connection Do NotRemove .
 
Blast from the Past :

Earthing-Clamps , Not to be used on Cables , Where did it come from . What Edition ??

BS-7671:2001 .

Earthing-Clamps , Not to be used on Cables .
Earthing-Clamps, must not to be used on Paper-insulated / Lead-sheathed orSteel-wire-armoured ( SWA ) cables .

Under, No-circumstance should an earthing-clamp ( Complying with BS-951 or any other type ) be attached to the , Lead-sheath of any cable.
Inthe case of a supply-cable this practice is wrong for , Two-reasons

Thesupply-cable is the property of the , DNO .
Thesecuring of the clamp to the Lead-sheath is likely to damage theconductor-insulation of the supply-cable . and with the cold-flow of the lead ,the connection is liable to loosen over-time . BS-951 :

1999 States in Note-3 . ( second-sentence) to it’sscope that “ such-clamps are not intended for connection to the armour or sheath of a cable “ :icon_bs:

Inthe worst-cases , this practice may lead to increased-risk from the hazards of fire or electrical-shock .


 
2001 / 2011:

Blast from the Past : :icon_bs:

Earthing-Clamps , Not to be used on Cables :

Many installations are supplied by , Lead-sheathed-incoming-service-cables, and earthing-facilities are often provided , by DNO by means of a ( Wiped-soldered-joint on to the Lead-sheath ) with an attached-earth-tail to an earthing-block .

Wherean adequate earthing-facility has not been provided , electrical-contractorsare advised always to enquire of the cable-owner ( such as the DNO whether or not such a facility can be made available, it must never be assumed that , because a supply-cable has a , Lead or other metallic-sheathor armour , it is capable of providing an effective-connection to Earth . orthat it is adequate for carrying the ( PFC)

The compressive-forces-exerted by tighteninga clamp , onto most types of armoured ormetal-sheathed-cables ( sufficient toprovide a Low-résistance joint for fault or other-currents to flow ) are liable to cause damage to theconductor-insulation and bedding . such misuse of a clamp is a departure fromthe Regulation - 512-05-01 .

One solution open to the . installation-designer is to make the ,installation part of a , TT - system .

Regulation- 512-05-01
Every item of equipment shall be selected anderected so that it will neither cause harmful-effects to other equipment nor-impair the supply during-normal-service including-switching-operations .

Regulation- 512.1.5. p/114
Every item of equipment shall be selected anderected so that it will neither cause harmful-effects to other equipment nor-impair the supply during-normal-service including-switching-operations .
 
Re-cap .

Exposed-conductive-parts : :icon_bs:
Arenot simply conductive-parts that are ,Exposed or Accessible . such as metal-table . the definition of an Exposed-conductive-part is a conductive-part ofequipment which can betouched

Whichis not live-part but which may become live under fault-conditions .

Bydefinition : p/27 . will indicate thatequipment - Means
Electrical-equipment, and electrical-equipment is an item which generates , converts , transmits , distributes orutilises electrical-energy . Etc
So what is an , Exposed-conductive-part:

Be part of electrical-equipment .
Be able to be Touched
Whichis Not normally-live
Butwhich can become live underfault-conditions

Extraneous-conductive-parts :
Extraneous-conductive-part for it is simply any piece of Extraneous-conductive-material , an Extraneous-conductive-part is a conductive-part of the electrical-installation .

Theessence of an , Extraneous-conductive-part is that it is likely to ( Introduce ) earth-potential into a Building / Installation .
Extraneous-conductive-parts : be ( Exposed) Conductive and in generalcontact with the mass of Earth .

p/28. Extraneous-conductive-part.
a conductive-part ( Introduce ) a potential generally Earth-potential .
Not forming-part ofthe electrical-installation .

By definition : p/27

Electrical-equipment :
(abbr : Equipment ) Any item for such purposes as

Generation.
Conversion.
Transmission.
Distributionor utilisation of electrical-energy suchas

Machines’
Transformers
Apparatus
Measuring-instruments
Protective-devices
Wiring-systems
Accessories
Appliances and luminaires .

Electrical-installation :
(abbr : Installation ) An assembly of associated-electrical-equipment having co-ordinated characteristics to fulfil specific-purposes .


 
Whilstmeasuring the earth electrode resistance , the earth lead of an earth loopimpedance tester should be connected to ?
- The incoming-line .
- The main-earthing-terminal
- the neutral-conductor only
- The disconnected-earthing-conductor .

Wherea 100mA RCD is protecting a TT installation , when tested at ( ½ ) it should
- Operate within 200mS
- Not operate
- Operate within 300mS
- Operate within 40mS

The ( R[SUP]1[/SUP]+ R[SUP]2[/SUP] ) reading taken at sockets during a continuityof ring-final-conductors test should be approximately ?
r[SUP]1[/SUP]+ r/n / 4
r[SUP]1[/SUP] + r[SUP]2[/SUP] / 4
r[SUP]1[/SUP] + r[SUP]2[/SUP] / 2
R[SUP]1[/SUP] + R[SUP]2 [/SUP]/ 4

Whichof the following test instrument would be most likely to give a reading of 2.5kA ?
Low-résistance-ohmmeter
RCD-tester
Insulation-résistance-tester
Prospective-fault-current-tester.

Theaccuracy of digital test instrument as recommended by Guidance-Note 3 is ?
0.04
0.05
0.02
0.1

Ifthe C.S.A. of a protective-conductor increases , thiswill lead to ?
- A decrease in résistance .
- An increase in résistance .
- An increased ( Zs ) reading
- An reduction in operating-current .

Accordingto GS-38 , test-leads should be . ?
Individually-coloured
Colouredbrown and blue .
Non-flexible
Insulatedto 230V

ATT - installation is protected by a 300mA - RCD . the maximum value ofearth-electrode-résistance is given byGN-3 as . ?
500Ω
1660Ω
100Ω
160Ω

Accordingto GN-3 is the correct-sequence of the following-dead-tests . 1 - Continuity ofthe ring-final-conductors . 2 - Polarity . 3 - Insulation-résistance . 4Continuity of CPC .
2. 3 . 4 . 1 .
4. 1 . 2 . 3 .
1. 2 . 3 . 4 .
4 . 1 . 3 . 2.

When testing a ring-final-circuit , the résistancereadings of ( R[SUP]1[/SUP] + R[SUP]2[/SUP]) will be . ?
Approximately 1.87 x R[SUP]1[/SUP]+ Rn
Approximately 2 x R[SUP]1 [/SUP]readings
Approximately 1.67 x R[SUP]1[/SUP] & Rn readings .
Approximately 1.67 x R[SUP]1[/SUP] & R[SUP]2 [/SUP]readings .

Whichof the following should be carried out when conducting aninsulation-résistance-test . on a 2 -way lighting-circuit . ?

Ensurethat Edison-screw light bulbs are connected in the Line-conductor only .
Bridgeout the switches .
Ensurethat both switches are in the on-position .
Operate all switches duringthe test .

It is often necessary to control a lampfrom more than one location , By utilising 2-way switches and strappers ( thecables in between the two operating switches )
Wecan effectively control the lamp from 2-different locations , such asthe top and bottom of stairs , known asthe “ conventionalmethod “

Whichcolumn would you record the results from the long-lead-test-method used todetermine continuity of the protective-conductors . ? Wander-lead-method .
Zs.
PFC.
R[SUP]2[/SUP].
(R[SUP]1[/SUP] + R[SUP]2[/SUP])

Which of the following tests would be carried out first ?
Earth-fault-loop-impedance
Insulation-résistance
Continuity of ring-final-conductors
Prospective-fault-current

 
The minimum-test-voltage that should be appliedwhen testing the insulation-résistance of a SELVcircuit is ?
500V d.c.
500V a.c.
250V d.c.
250V a.c.

An RCD when tested at 100% ( x1 times ) of its trip-rating should ?
Not-trip
Trip within 300mS
Trip within 40mS
Trip within 100mS

Some of the essential andoptional-information required on the , Electrical-Installation-certificate and Minor-Electrical-Installation-Work-certificate is ?
Number of rooms , type of lighting ,outdoor-supplies
Floor-area, separate building , number of floors
Means of earthing, main-protective-conductors andsupply-characteristics
Name of sub-contractor , invoice , contact-number

Before carrying out an Insulation-résistance test ?
Carry out verification of voltage-drop. ► ( Regulations - 612.14. p/194 . Note : Verification of voltage-drop is not normallyrequired during initial-verification )
Ensure supply is switched on
Contact local-authority-building-control
Safely-isolate and consider electronic-equipment andvoltage-sensitive-equipment

Prospective-fault-current-measurement ensures that ?
Cables can carry the required-load-current
The consumer-unit-main-switch can be operated during a fault
The overcurrent-protective-devices at that point in the installation can disconnect ( Overload / Overloaded - Overcurrent )
The main-fuse will operate in the event of afault .

Overcurrent-Protective-Devices :
Protection against overload , & short-circuits in electrical-equipment .
O.S.G.- p/23 Note . RCBOs - Overload , Short-circuit , Earth-fault . MCB/ RCBO ( Overload-protection - Fuses ) its inthe Questions

A Minor-electrical-certificate does not require details of ?
System-earthing-arrangements
Departures from BS-7671:
Method of fault-protection
Prospective-fault-current. ( PFC )

Once an Electrical-Installation-certificate has been completed theoriginal should be ?
Sent to the local-building-control
Retained by the electrical-contractor
Given to the person ordering the work
Given to the tenant of the building .

Test-Leads to GS-38 should have ?
1mm exposed-probe , non-fused and finger-barriers
2mm exposed-probe , non-fused-lead or current-limiting and finger-barriers
2mm exposed-probe , fused-lead or current-limiting and finger-barriers
1mm exposed-probe , fused- lead or current-limiting and finger-barriers

2mm exposed-probe ( for live-testing ) “ Fingers “ or Hands
4mm exposed-probe ( for dead-testing )

During the initial-inspection and testing sight would indicate a fault such as ?
Overheating
Equipment-overheating
Vibration of transformer-cover
Damaged-equipment .
 
Metallic supply-pipework can be used for anearth-electrode if ?
It is water-utility-pipework
It is other than water-utility-pipework
It is an unused-gas-pipe that is less than10-years old
It is other than utility-pipework providing-precautions have been taken . BS-7671:2011 . p/159 - 542.2.6.

If running in permitted-zones are used as protection against impact , whatextra-measure would be required if the installation was in a domestic-premises ?
Run cables with capping-fitted
All circuits protected with a30mA RCBO
Cables to have additional-protection by means of 30mA RCD BS-7671:2011:p/125 . 522.6.102
Cables to have additional-protection by means of 100mA RCD

When assessing-circuits for any need of continuity of service , the following-characteristic that does notneed to be considered is ?
Multiple-power-supplies
Selection of earthing-system
Lighting-protection ( BS-7671:2011. p/ 49 . 361.1
Number of circuits

When automatic-disconnection of supply is used as a measure of protection , additional-protectionby RCD shall be provided for ?
Mobile-equipment having a rating of greater than 32A
Socket-outlets in commercial and industrial-locations
Only for sockets-rated at 32A or less where it is reasonable to expect they may be used to supply-equipment for use outdoors
Socket-outlets-rated at 20A or less in a domestic-installation ( BS-7671:2011: p/54. 411.3 )

All circuits in a location containing a bath or shower shall have ?
A disconnection time of 0.4s
Be installed at a depth of at least 50mm
Be installed using earthed-conduit
Additional-protection by a 30mA RCD . ( BS-7671:2011: p/199 . 701.411.3.3.

The installation reference for multicore-cables clipped-direct is ?
30
C ( BS-7671:2011. p/318 . number - 20
A
13

Automatic-disconnection of supply is used as a method of protectionfor ?
Indirect-contact
Basic-protection
Fault-protection ( BS-7671:2011: definitions )
Direct-contact
 
How things change - 1991 / 2011 : 15[SUP]th[/SUP]/ 16[SUP]th[/SUP] - 17[SUP]th[/SUP] edition 2011:

Sixteen Edition 1991:

ThisEdition was issued on 10 may 1991 . it isintended to supersede the fifteen-edition , fifteen-edition will bechanged to the sixteen-edition to take effect from 31-december 1992.

130-09: Additions and Alterationsto an Installation : 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
130-09-01. No addition or alteration , temporaryor permanent , shall be made to an existing-installation , unless it has been ascertainedthat the rating and the condition of any existing-equipment , including that ofthe supplier , which will have to carry any additional-load is adequate for the altered-circumstances andthe earthing-arrangement is also adequate .

132.16 : Additions and Alterationsto an Installation : 17[SUP]th[/SUP] - edition
Noaddition or alteration , temporary or permanent , shall be made to anexisting-installation , unless it has been ascertained that the rating and thecondition of any existing-equipment , including that of the distributor , will be adequate for thealtered-circumstances , furthermore , the earthing and bonding-arrangements ,if necessary for the protective-measure applied for the safety of the additions and alteration , shall be adequate .

Comparing things form the past - EditionsWhat’s in a Wording “


 
Comparing things from the past - Editions

15[SUP]th[/SUP]/ 16[SUP]th[/SUP] . 1991 / 1992 .
Earthed-equipotential-zone:
A zone within which , exposed-conductive-partsand , extraneous-conductive-parts are maintained at substantially the sane-potential by-bonding , such that , underfault-conditions , the differences in potential between-simultaneously-accessible , exposed and extraneous-conductive-parts will not cause electric-shock .

Earthing: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
The act of connecting the , exposed-conductive-partsof an installation to themain-earthing-terminal of an installation .

Earthing: 2011 :
Connection of the exposed-conductive-parts of an installation to the main-earthing-terminalof that installation .

Equipotential-bonding: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
Electrical-connection-maintaining various , exposed-conductive-parts and extraneous-conductive-parts atsubstantially the same-potential .

Equipotential-bonding: 2011:
Electrical-connection-maintaining various , exposed-conductive-parts and extraneous-conductive-parts atsubstantially the same-potential . ( see also Protective-equipotential-bonding )

Exposed-conductive-part: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
A conductive-part of equipment which can be touched and whichis not a live-part but which may become live under fault-conditions .

Exposed-conductive-part: 2011:
Conductive-part of equipment which can be touched and whichis not a normally live , but which can become live under fault-conditions .

Extraneous-conductive-part: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
A conductive-part liable to introduce a potential , generallyearth-potential , and not forming-part of the electrical-installation .

Extraneous-conductive-part: 2011:
A conductive-part liable to introduce a potential , generally Earth-potential, and not forming-part of the electrical-installation .

Prospective-fault-current: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
The value of overcurrent at a given-point ina circuit resulting from a fault of negligible-impedance betweenlive-conductors having a difference ofpotential undernormal-operating-conditions , or between a live-conductor and an , exposed-conductive-part.

Prospective-fault-current: 2011: ( Ipf )
The valueof overcurrent at a given-point in a circuit resulting from a fault ofnegligible-impedance between live-conductors having a difference of potential under normal-operating-conditions , or between a live-conductor and an ,exposed-conductive-part .

Earth-fault-current: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
A fault-currentwhich flows to Earth .

Earth-fault-current: 2011:
A current resulting from a fault of negligible-impedancebetween a line-conductor and an , exposed-conductive-part or a protective-conductor .

Earth-fault-loop-impedance: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
The impedance of theearth-fault-current-loop starting andending at the point of earth-fault , this impedance is denoted by the symbol; ( Zs )

Earth-fault-loop-impedance: 2011:
The impedance of theearth-fault-current-loop starting andending at the point of earth-fault , this impedance is denoted by the symbol; ( Zs )

Gas-installation-pipe: 15[SUP]th[/SUP] / 16[SUP]th[/SUP]
Any-pipe, not being a service-pipe ( other thanany-part of a service-pipe comprised in a primary-meter-installation ) or apipe comprised in a gas-appliance , for conveying gas for a particularconsumer and including any associated-valve or other-gas-fitting.

Gas-installation-pipe: 2011:
Any-pipe, not being a service-pipe ( other thanany-part of a service-pipe comprised in a primary-meter-installation ) or apipe comprised in a gas-appliance , for conveying gas for a particularconsumer and including any associated-valve or other-gas-fitting.

Has thing changed much .



 
Certification and Reporting : 15[SUP]th[/SUP] / 16[SUP]th[/SUP]

743: Alterations and Additions .
743-01-01. The requirements of section 742 for the issue of a Completion and Inspection-Certificate shall apply toall the work of the alterations or additions , Any defects oromissions-revealed in that work shall be made good before a Completion-Report is issued .

The Contractor or other person responsible for the new-work , ora person authorised to act on his behalf , shall report in writing , to theperson-ordering the work any defects found in related-parts of theexisting-installation .

633: Alterations and Additions . 2011:
633.1: The requirements of Section 631 and632 for the issue of an , Electrical-Installation-Certificate or a Minor-Electrical-Installation-Works-Certificate shall apply to all the work of the ,additions or a alterations .

633.2: The contractor or other-person responsible for new-work or a personauthorised to act on his behalf , shall record on the , Electrical-Installation-Certificate or the Minor-Electrical-Installation-Works-certificate, any defects found , so far is reasonably-practicable , in theexisting-installation .


 
15[SUP]th[/SUP]/ 16[SUP]th[/SUP] . 1991 / 92
713-02: Continuity of protective-conductors .
713-02-01: Every protective-conductor shall betested to verify that it is electrically-soundand correctly connected .

713-03: Continuity ofring-final-circuit-conductors
713-03-01: A test shall be made to verify the continuity of each-conductor includingthe protective-conductor . of every-ring-final-circuit .

713-04: Insulation-résistance .
713-04-01: The insulation-résistance between live-conductors shall be measured , before the installation is connectedto the supply .

713-04-02: Particular attention shall be given to the presence of electronic-devicesconnected in the installation and , where necessary , such devices shall be isolatedso that they are not damaged by the test-voltage and thereafter tested inaccordance with regulation - 713-04-06 .

713-04-03: The insulation-résistance measured with the d.c.test-voltages indicated in table - 71A shall be considered satisfactory if the , main-switchboard , and eachdistribution-circuit tested separately with all it’s final-circuits connectedbut with current-using-equipment disconnected , has an insulation-résistancenot less than the appropriate value given in Table - 71A

BS-7671:2008:2011:
612.2.: Continuity of conductors .
612.2.1.: Continuity of protective-conductors , including main & supplementary-equipotential-bonding.
A continuity test shall be made , it isrecommended that the test be carried out with a supply having a no-load voltagebetween 4V and 24V d.c. or a.c. Etc

612.2.2.: Continuity ofring-final-circuit-conductors
A test shall be made to verify the continuityof each-conductor including the protective-conductor . ofevery-ring-final-circuit .

612.3: Insulation-résistance
612.3.1: The insulation-résistance shall bemeasured , between live-conductors and between live-conductors and the protective-conductors connected to theearthing-arrangement , where appropriate during this measurement , line andneutral-conductors may be connected-together .

612.3.2: The insulation-résistance measured with the test-voltages indicated in Table- 61 , shall be considered satisfactoryif the main-switchboard and eachdistribution circuit tested separately , with all its final-circuits connectedbut with current-using-equipmentdisconnected , has an insulation-résistance not less than the appropriate-valuegiven in Table 61 .

711: Initial-Verification : 15[SUP]th[/SUP]/ 16[SUP]th[/SUP] . 1991 / 92
Every installation shall . during erectionand/or on completion before being put into service be inspected and tested toverify , so far as is reasonably-practicable , that the requirements ofregulations have been met .

The method of test shall be such that nodanger to persons , livestock or property or damage to equipment can occur evenif the circuit tested is defective .

BS-7671:2008:2011:
610.1.: Every installation shall . during erection and oncompletion before being put into service be inspected and tested to verify , sofar as is reasonably-practicable , that the requirements of regulations havebeen met .

Precautions shall be taken to avoid , danger topersons , and livestock , and to avoid damage to property andinstalled-equipment , during inspection and testing .

Past to Present . 15[SUP]th[/SUP] / 16[SUP]th[/SUP] . 1991 / 92 . BS-7671:208:2011: We have came a long way since then . “ Not in WAGES but Regulations “ Yeah

314: Installation Circuit Arrangement
314-01-01: Every installation shall be dived intocircuits as necessary to :

i) avoid danger in the event of a fault . and
ii) Facilitate safe operation . inspection . testing. and maintenance .

Look in 314.2. Now - 314-01-02A separate circuit shall be provided foreach-part of the installation which needs to be separately controlled forcompliance with the regulations orotherwise to prevent danger . so that such circuits remain energised in theevent of failure of any other circuit of the installation , and due accountshall be taken of the consequences of the operation of anysingle-protective-device .

Look in 314.3. - 314-01-03: The number of final-circuits required , and the number of points suppliedby any final-circuit , shall be such as to facilitate compliance with therequirements of chapter 43 for overcurrent-protection , chapter 46 forisolation and switching and chapter 52 as regards current-carrying-capacities of conductors .

Look in 314.4. - 314-01-04 : Where an installation comprises more than one-final-circuit , each final circuit shallbe connected to a separate-way in the distribution-board , the wiring of eachfinal-circuit shall be electrically separate from that of every other final-circuit , so as to prevent theindirect-energising of a final-circuit intended to be isolated . RCDs have a field-day now .

 
For Our Younger Members .

Fig 2.1. p/ 37 .
Example of Earthing-Arrangementsand Protective-conductors . Chapter 54 .

Firstly: Protective-conductors - 1 , 2 , 3 , 4 .
1) Circuit-protective-conductor
2) Main-protective-bonding-conductor ….. ( Equ-ipotenti-al-bonding) Equal-potential
3) Earthing-conductor
4) Supplementary-protective-bonding-conductor ( where required )

B) Main-earthing-terminal - ( MET )
M) Exposed-conductive-part ….. Conductive-part of equipment whichcan be .
C) Extraneous-conductive-part ….. Conductive-part liable to introduce a potential
P) Metallic-water-pipe . ( extraneous-conductive-parts )
T) Earth-electrode ( TT and IT systems )
E) Other means of earthing ( TN systems )

B) Main-earthing-terminal - ( MET )
1) Circuit-protective-conductor - going to Exposed-conductive-parts ( M )

2) Main-protective-bonding-conductor .
B) Main-earthing-terminal - ( MET ) 2 - Main-protective-bonding-conductor. main-metallic-water-pipe ….. ( making me. Extraneous-conductive-parts)

3) Earthing-conductor . ( B ) Main-earthing-terminal - ( MET ) E) Other means of earthing ( TN systems ) T) Earth-electrode ( TT and IT systems )

4) Supplementary-protective-bonding-conductor (where required ) can be ?? ( M ) Exposed-conductive-part to Exposed-conductive-part or
Exposed-conductive-part (C ) Extraneous-conductive-parts . Structural-steelwork .

Protective-conductor ( PE )
Aconductor used for some measures of protection against electric-shock andintended for connecting together any ofthe following-parts . p/32
i) Exposed-conductive-part(s)
ii) Extraneous-conductive-part(s)
iii) Earthing-conductor .
iv) Earth-electrode(s) ….. ( s ) making me , one or more Rods . Etc
v) The earthed-point of the source . or an artificial-neutral .

i) Exposed-conductive-part(s) p/27
Exposed-conductive-part. Conductive-part of equipment which can be
- Touched and which is not normally-live. But
- Which can become live under-fault-conditions.

ii) Extraneous-conductive-part(s) p/28
Extraneous-conductive-part. a conductive-part liable to introduce a potential.generally earth-potential . and
Not forming part of the electrical-installation .

iii) Earthing-conductor. p/27
Earthing-conductor. A protective-conductor connecting the, main-earthing-terminal of an installation to an earth-electrode or toother means of earthing . Etc .
 
Whenchecking Polarity withtest-probes the voltage-indication on a single-phase socket-outlet should be
L- N 230V , L - E 230V , N - E 230V .
L- N 230V , L - E 0V , N - E 230V .
L- N 0V , L - E 230V , N - E 0V .
L - N 230V , L - E 230V , N - E 0V.

Some of the essential and optional-information required on the ,Electrical-Installation-Certificate and ,Minor-Electrical-Installation-work-Certificate is
Number of rooms . type of lighting ,outdoor-supplies
Floor-area, separate-building , number of floors
Mean of earthing . main-protective-conductors and supply-characteristics
Name of sub-contractor , invoice , contact-number

Electrical-Installation-Certificaterequired for replacing a light-fitting would be .
A Minor-Work-Electrical-Installation-Certificate
A Minor-Work-Electrical-Installation-Certificate and aschedule of test-results
A Minor-Work-Electrical-Installation-Certificate and aschedule of Inspections and a schedule of test-results
No Certificate required

Before carrying out anInsulation-résistance-test
Carry out verification of voltage-drop
Ensure supply is switched on
Contact local-authority-building-control
Safely-isolate and consider electronic-components andvoltage-sensitive-equipment
 
Part-P does Not apply to ?
Lifts
Land associated with a building
Share amenities in blocks of flats
Greenhouses

In which of the following would you find therequirements for the building-design , construction and management for building-regulations ?
Schedule 1
Schedule 2
Approved-document A
Approved-document B

Who is ultimately responsible forcompliance with the building-regulations .
The-building-control-officer
The-architect
The-person doing the building-work
Responsibility is shared between the local-authority and the part-governing-body

Which of the following is not a requirement of Part-E .
Parts of the same-building
Adjoining-buildings
External-sources
Excessive-reverberation from common-areas

Linked to L1 for energy-conservation ,which of the following is the best way of control on a heating-system .
Thermostatically-controlled-valves
A time-clock and thermostatically-controlled-valves
A time-clock only
Night-storage-heaters

Which approved-document is related to the installation of smoke and fire-alarms .
B
L
A
M

On a notifiable-electrical-installation , the person ordering the work isissued with a building-regulation-certificate and relative-certificate , whatpaper-work do you send to the governing-body
The building-regulations-certificate
The power-regulations-certificate
The BS-7671:2008:2011 certificate
A formal-letter confirming that you have completedthe work

According to Document A , horizontal-chases should beno deeper than what depth of wall-thickness
One-third
One-half
One-sixth
One-quarter

You are installing a new-circuit for recessed-light-fittings that penetrate the ceiling , what ,Approved-document(s) need to be referredto .
Document B
Document E
Document P
All of the above

Where do the building-regulations apply ?
England , Ireland and Scotland
England , Wales and Scotland
Across the whole of the United-Kingdom
England and Wales .

If you were fitting a consumer-unit ,what document would you primarily-refer to
L1
F
M
A

Thebuilding-regulations are made under which Act .
The domestic-installer-act 2003
The Health & Safety at Work Act 1974
The Electricity at Work-Act 1989
The Building-Act 1984

Approved-documentA , requires notches in joists to be no-greater than 0.125 times the ?
Width
Depth
Length
Span

Whichof the following is not a requirement of part - E ?
Parts of the same building
Adjoining-buildings
External-sources
Excessive-reverberationfrom common-areas

Linked to L1 , for energy-conservation , whichof the following is the best way of control on a heating-system ?
Thermostatically-control-valves
A time-clock & thermostatically-controlled-valves
A time-clock-only
Night-storage-heaters

Which of these is outside the scope of Part - P ?
Installing-new-circuits in a dwelling
Installing a power-supply for a garden-fountain
Rewiring a shower-circuit in a dwelling
Rewiring a church

On a notifiable-electrical-installation , the person ordering the work is issued with abuilding-regulation-certificate and relative-certificate , what paperwork doyou send to the governing-body ?
The building-regulations-certificate
Thepower-regulations-certificate
The BS-7671: certificate
A formal-letter-confirming that you havecompleted the work

Building-work is defined in regulation - 3 , of thebuilding-regulations and includes ?
Caravans
Tents
Football-pitches
The erection or extension of a building

The Building-Regulations - 2000 ( As Amended ) Are made under the , Building-Act 1984 , are ?
A statutory-instrument-number - 2531
Applicable to a majority of building-work
Split into sections related “ Approved-documents “
All of the above .

You are installing a new-circuit for Recessed-light-fittings , that penetratethe ceiling , what , Approved-document(s) need to be referred to ?
Document- B
Document- E
Document- P
All of the above

 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
376
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top