15[SUP]th[/SUP]/ 16[SUP]th[/SUP] . 1991 / 92
713-02: Continuity of protective-conductors .
713-02-01: Every protective-conductor shall betested to verify that it is electrically-soundand correctly connected .
713-03: Continuity ofring-final-circuit-conductors
713-03-01: A test shall be made to verify the continuity of each-conductor includingthe protective-conductor . of every-ring-final-circuit .
713-04: Insulation-résistance .
713-04-01: The insulation-résistance between live-conductors shall be measured , before the installation is connectedto the supply .
713-04-02: Particular attention shall be given to the presence of electronic-devicesconnected in the installation and , where necessary , such devices shall be isolatedso that they are not damaged by the test-voltage and thereafter tested inaccordance with regulation - 713-04-06 .
713-04-03: The insulation-résistance measured with the d.c.test-voltages indicated in table - 71A shall be considered satisfactory if the , main-switchboard , and eachdistribution-circuit tested separately with all it’s final-circuits connectedbut with current-using-equipment disconnected , has an insulation-résistancenot less than the appropriate value given in Table - 71A
BS-7671:2008:2011:
612.2.: Continuity of conductors .
612.2.1.: Continuity of protective-conductors , including main & supplementary-equipotential-bonding.
A continuity test shall be made , it isrecommended that the test be carried out with a supply having a no-load voltagebetween 4V and 24V d.c. or a.c. Etc
612.2.2.: Continuity ofring-final-circuit-conductors
A test shall be made to verify the continuityof each-conductor including the protective-conductor . ofevery-ring-final-circuit .
612.3: Insulation-résistance
612.3.1: The insulation-résistance shall bemeasured , between live-conductors and between live-conductors and the protective-conductors connected to theearthing-arrangement , where appropriate during this measurement , line andneutral-conductors may be connected-together .
612.3.2: The insulation-résistance measured with the test-voltages indicated in Table- 61 , shall be considered satisfactoryif the main-switchboard and eachdistribution circuit tested separately , with all its final-circuits connectedbut with current-using-equipmentdisconnected , has an insulation-résistance not less than the appropriate-valuegiven in Table 61 .
711: Initial-Verification : 15[SUP]th[/SUP]/ 16[SUP]th[/SUP] . 1991 / 92
Every installation shall . during erectionand/or on completion before being put into service be inspected and tested toverify , so far as is reasonably-practicable , that the requirements ofregulations have been met .
The method of test shall be such that nodanger to persons , livestock or property or damage to equipment can occur evenif the circuit tested is defective .
BS-7671:2008:2011:
610.1.: Every installation shall . during erection and oncompletion before being put into service be inspected and tested to verify , sofar as is reasonably-practicable , that the requirements of regulations havebeen met .
Precautions shall be taken to avoid , danger topersons , and livestock , and to avoid damage to property andinstalled-equipment , during inspection and testing .
Past to Present . 15[SUP]th[/SUP] / 16[SUP]th[/SUP] . 1991 / 92 . BS-7671:208:2011: We have came a long way since then . “ Not in WAGES but Regulations “ Yeah
314: Installation Circuit Arrangement
314-01-01: Every installation shall be dived intocircuits as necessary to :
i) avoid danger in the event of a fault . and
ii) Facilitate safe operation . inspection . testing. and maintenance .
Look in 314.2. Now - 314-01-02A separate circuit shall be provided foreach-part of the installation which needs to be separately controlled forcompliance with the regulations orotherwise to prevent danger . so that such circuits remain energised in theevent of failure of any other circuit of the installation , and due accountshall be taken of the consequences of the operation of anysingle-protective-device .
Look in 314.3. - 314-01-03: The number of final-circuits required , and the number of points suppliedby any final-circuit , shall be such as to facilitate compliance with therequirements of chapter 43 for overcurrent-protection , chapter 46 forisolation and switching and chapter 52 as regards current-carrying-capacities of conductors .
Look in 314.4. - 314-01-04 : Where an installation comprises more than one-final-circuit , each final circuit shallbe connected to a separate-way in the distribution-board , the wiring of eachfinal-circuit shall be electrically separate from that of every other final-circuit , so as to prevent theindirect-energising of a final-circuit intended to be isolated . RCDs have a field-day now .